Midea "ECO Mode" - an oxymoron
Does anyone have any docs on what the purpose of ECO Mode is on Midea heat pumps? One would assume it mean "economical" or perhaps "ecological", however as far as I can see, it is neither.
Consider the following:
With ECO Mode on, Weather Compensation is disabled, the flow temperature is set to 1°C above what the non-compensating flow temperature is, the energy consumed goes through the roof, and the heat output is not really any higher than it was with ECO Mode off!
ECO Mode is only of use when using the pre-programmed Weather Compensation curves as described from page 104 onwards in the detailed Midea data.
When ECO Mode is selected, it changes the controller from curve 4 to curve 6, which lowers the specified LWT.
If you are using curve 9, which can be adjusted by the user to match the home's heat loss, then switching to ECO Mode could actually increase the specified LWT.
- 26 Forums
- 2,122 Topics
- 46.6 K Posts
- 136 Online
- 4,529 Members
Podcast Picks
Latest Posts
-
RE: 300 Liter Tank - Do I have to heat it all?
There’s no second hand market for DHW tanks (I was told...
By Judith , 3 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 12 hours ago
-
You may well be right, @jamespa.
By Majordennisbloodnok , 16 hours ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 17 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 19 hours ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 21 hours ago
-
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@davidalgarve It should just be recovered by both servi...
By dgclimatecontrol , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 2 days ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 2 days ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 3 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 4 days ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 4 days ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 4 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 4 days ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 4 days ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 5 days ago