Midea ASHP – how to set weather compensation
Good summary.
Some comments: they will probably dispute that the buffer tank is too small and, even if they replaced it with a larger one, unless its controlled properly it will still mix. What you can ask them to avoid this argument is
- how is the inevitable mixing (also called 'distortion') in the buffer accounted for in the design
- have they checked that it works as they have designed it ie the temperature drop across the buffer is what they designed for
then await a blank stare or some BS!
Yes I would ask about the control. They probably wont understand 'controlling the buffer', perhaps the simplest way to put it is 'does the call for heat from the UFH also connect to the ASHP as a call for heat, or does the ashp charge the buffer independently? A look at the wiring or some experiments with the thermostats could ferret this out.
Posted by: @pash44pump(1) I believe the presence of a large container of glycol suggests that there are no antifreeze valves. I assume this is an installer decision that might be sub-optimal but something I have to live with.
Yes and yes unless they are prepared to swap it out or a/f valves.
That said this may be a design fault, the UFH was designed presumably to work with water which is both less viscous and has a higher heat capacity. If the UFH is marginal (which it seems it is) then this could be contributing to the deficit. You could ask them how they have accounted, in the design, for the fact that water has been replaced by glycol in the UFH given the increased viscosity and reduced specific heat capacity of the latter. Again await a blank stare or some BS.
Posted by: @pash44pump(2) Are there any leaks? Yes there is a small amount of leakage from the pipework in the following photo. What actually are those valves? How big an issue is this? I would raise this with the installer as another thing that needs resolving.
I think its just a tee'd flow meter. Very useful!
Posted by: @pash44pumpYou won't be surprised to know that the worst performance in the house are bedroom 1 and its en-suite
Do you happen to know where the pipe run is, any possibility its poorly insulated.
Posted by: @pash44pumpSome posters have mentioned room thermostats as being negative but in a large house, how else do you control the temperature of zones that you don't want to be the same.
they are negative and should generally be set a couple of degrees above the target otherwise you may well not reach the target and the on/off switching contributes to system inefficiency.
In answer to 'how do you control', what you do is balance the loops, much like balancing radiators, so that when run 24*7 they emit the right amount of heat. There will be valves on the manifolds that allow you to do this.
I cant currently think of any other design faults but others may be able to comment and I would reserve your position until you have answers to the above, as those answers may reveal other faults.
Hope that helps
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Currently viewing this topic 2 users ( Tasos, cathodeRay ) and 2 guests.
Recently viewed by users: Tim441 30 minutes ago, JamesPa 15 seconds ago, Transparent 18 seconds ago, pash44pump 34 minutes ago.
- 26 Forums
- 2,152 Topics
- 47.2 K Posts
- 30 Online
- 5,671 Members
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
Good summary. Some comments: they will proba...
By JamesPa , 49 seconds ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 1 hour ago
-
RE: Octopus tariffs - a quick comparison
@scalextrix yes, battery is vital to maximise TOU tarif...
By Tim441 , 1 hour ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@howardp99 Yes, I get how the inverter rating is limiti...
By Old_Scientist , 1 hour ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 14 hours ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 16 hours ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 21 hours ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 21 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
🙁🙁🙁🙁🙁
By Lucia , 1 day ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 1 day ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@julianc Our solar PV has produced more this August tha...
By Toodles , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@transparent that is a very interesting suggestion, tha...
By GrahamF , 4 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Sorry to resurrect this thread, but it is sort of relev...
By cathodeRay , 4 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I missed your 22nd June post on this. I am sure it can ...
By cathodeRay , 4 days ago
-
Now posting on the right topic.... With general build...
By benson , 4 days ago