Midea ASHP – how to set weather compensation

145 Posts
14 Users
29 Reactions
27.9 K Views
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2780
 

Good summary.

 

Some comments: they will probably dispute that the buffer tank is too small and, even if they replaced it with a larger one, unless its controlled properly it will still mix.  What you can ask them to avoid this argument is

  • how is the inevitable mixing (also called 'distortion') in the buffer accounted for in the design
  • have they checked that it works as they have designed it ie the temperature drop across the buffer is what they designed for

then await a blank stare or some BS! 

Yes I would ask about the control.  They probably wont understand 'controlling the buffer', perhaps the  simplest way to put it is 'does the call for heat from the UFH also connect to the ASHP as a call for heat, or does the ashp charge the buffer independently?  A look at the wiring or some experiments with the thermostats could ferret this out.

Posted by: @pash44pump

(1) I believe the presence of a large container of glycol suggests that there are no antifreeze valves. I assume this is an installer decision that might be sub-optimal but something I have to live with.

Yes and yes unless they are prepared to swap it out or a/f valves. 

That said this may be a design fault, the UFH was designed presumably to work with water which is both less viscous and has a higher heat capacity.  If the UFH is marginal (which it seems it is) then this could be contributing to the deficit.  You could ask them how they have accounted, in the design, for the fact that water has been replaced by glycol in the UFH given the increased viscosity and reduced specific heat capacity of the latter.  Again await a blank stare or some BS.

Posted by: @pash44pump

(2) Are there any leaks? Yes there is a small amount of leakage from the pipework in the following photo. What actually are those valves? How big an issue is this? I would raise this with the installer as another thing that needs resolving.

I think its just a tee'd flow meter.  Very useful!

Posted by: @pash44pump

You won't be surprised to know that the worst performance in the house are bedroom 1 and its en-suite

Do you happen to know where the pipe run is, any possibility its poorly insulated.

Posted by: @pash44pump

Some posters have mentioned room thermostats as being negative but in a large house, how else do you control the temperature of zones that you don't want to be the same.

they are negative and should generally be set a couple of degrees above the target otherwise you may well not reach the target and the on/off switching contributes to system inefficiency.

In answer to 'how do you control', what you do is balance the loops, much like balancing radiators, so that when run 24*7 they emit the right amount of heat.  There will be valves on the manifolds that allow you to do this.

I cant currently think of any other design faults but others may be able to comment and I would reserve your position until you have answers to the above, as those answers may reveal other faults.

 

Hope that helps

 