@batalto A couple of questions
- what is your heat distribution system? Radiators, under floor
- Do you have a buffer tank or system separator?
- What other control systems do you have for the heating?
- Where did you get the figure of 30w/m2
- How big is your heat pump?
- What is the build of your house, do you have stud walls of brick internally?
Anything else you may think is necessary
The EPC means nothing, it is a document full of assumptions and short on facts. (I am a qualified DEA and can produce them)
Director at Heacol Consultants ltd
In short,
- Radiators - although the upstairs ones basically never come on as it never gets cold up there
- Buffer tank 20l and 210l unvented cylinder for hot water
- Thermostat (nest)
- 30w/2 comes from a room by room survey of the house based on insulation, windows type, window size etc
- 12kw heat pump
- Lower floor of the house is brick with cavity and double glazed. Upper floor is structurally insulated panels with triple glazing and outside solid wall insulation
- Loft is 370mm of insulation
- Insulation between first and second floors
- Insulation between the walls
- Whole downstairs was built to 2015 building regs upstairs to 2020 building regs
- All pipes fully lagged
Oh, 260m2 house
@batalto, Ideally, as your house has a relatively low thermal mass, it should be controlled with an internal thermostat connected to the heat pump controller, the best thing to do is to move the controller to a common area, usually the hall, at the farthest point from the front door is best, but anywhere in the heated envelope is acceptable except close to a radiator. Then re-program the programmer to work as an internal temperature sensor. If this cannot be moved, as a compromise, set the weather compensation to be 25 Deg C at 15 external and 45 deg C at -3 external. (you may have to play with this to find the right settings for your house. Set the heating on/ off setting to 18 with a 5 degree offset. (I know it is difficult with this controller as there are 5 wires, you can however cut the wire and extend it with a flex, just make sure you do not mix the wires up, it will not break it, but it will not work)
Disconnect the Hive and remove the TRV actuators off all the radiators except in the bedrooms.
You will find that the heat pump will run nearly all the time below 18 deg C but at a very low level resulting in the best performance, you will also find that it does not frost up as much when it gets cold, and you will have a much more even temperature in your house.
If you want even better performance, remove the second pump the other side of the buffer tank (this costs you £100.00/year to run), remove the return pipes and connect them together, the pump inside the unit is man enough to run the whole system and if most radiators are open, it is very unlikely you will have a low flow error.
Director at Heacol Consultants ltd
Hi Heacol,
It sounds like your description of a system using weather compensation, along with internal temperature measurement, is basically continuous process control utilising a PID controller algorithm.
Do all manufacturers systems have this capability? What level of accuracy can be achieved?
Personally I have a PID controller which varies the radiator water temperature to maintain the indoor temperature within +or- 0.2C of the setpoint.
Hi Batalto,
Having just watched the video accessed by the link you posted, I can now see why people's ASHP systems are not working at their optimum settings, if this is how they are being commissioned.
The controller on our heating system varies the water temperature from 25C up to about 42.5C, when the outside temperature has fallen to -10C. If the outside air temperature was to fall even lower, it would simply raise the water temperature to supply the additional heat loss. In Spring and Autumn the radiators often feel cool to the touch, but are still providing sufficient heat energy to maintain the indoor temperature at the desired 21C.
Dependent upon the heat loss and the size of your heat emitters, you would probably get much better efficiency by setting the minimum water temperature at 25C, when the outside air temperature rises to 16C, and set the maximum water temperature at 45C or 50C, when the outside air temperature falls to -10C. Provided that your ASHP is capable of operating over that temperature range, then you should be able to optimise the operation of your system.
@derek-m, you are correct, it is a great shame that the industry, most manufacturers and merchants are training people to install and commission heat pumps in a way that leads to poor performance and high running costs. However, you must remember that their aim is to shift a box.
Director at Heacol Consultants ltd
@batalto, If you do not get rid of the Nest, do not bother to do anything, nothing will make a differance.
Director at Heacol Consultants ltd
Hi Heacol,
With the method of control that you are suggesting, how is the central heating water pump controlled?
Rather than move the Midea controller, I presume an external temperature sensor could be connected to the controller, the sensor being located at a suitable place to measure the average temperature. In that way the controller could replace the Nest to provide better control.
@heacol I don't really see why. Surely the Nest is just an on off control, just like the heat pump controller temperature sensor? The heat pump will still adjust the flow temperature based on weather compensation separately to the Nest so why does it matter? All the Nest does is call for heat until it gets to 21 and then holds it by keeping the pump running? If weather compensation lowers the flow temperature wouldn't the Nest just keep calling it? Or am I missing something between the Nest temperature sensor and the heat pump controller sensor?
- 21 Forums
- 1,972 Topics
- 42.8 K Posts
- 27 Online
- 2,303 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
If you haven’t voted on this poll yet, please take a mo...
By Mars , 8 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
I should add that my system has two circulating pumps: ...
By JohnR , 9 hours ago
-
RE: Transforming a Derbyshire Property into an Energy-Efficient Haven
I feel that this is a good campaign for me to embark an...
By Mars , 9 hours ago
-
RE: Replacing knackered oil boiler with ASHP - Perthshire
On the basis that 1l oil = 10kWh and 1cu m wood = 2500k...
By JamesPa , 10 hours ago
-
RE: Battery storage to run Heat Pump.
@jeff The government are quite happy for the network ...
By Lucia , 10 hours ago
-
RE: Grant ASHP not reaching target temperatures
We may have similar and could share experiences: I ha...
By Hillswick , 10 hours ago
-
@sandman1600 Yes, you have the idea of what you need to...
By bontwoody , 11 hours ago
-
RE: Setback savings - fact or fiction?
OK, so I'm just thinking out loud here: You loose ene...
By BobTSkutter , 11 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist The OE guidelines mention that their con...
By Toodles , 13 hours ago
-
RE: Adjusting 6kW Daikin's Weather Compensation Curve
@jamespa I'm grateful for your advice.
By Ubert767 , 14 hours ago
-
@heatgeek thanks! I contacted them too.
By Eliuccio , 14 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
Thanks. I've seen the video several times at the beginn...
By cliffhanger , 17 hours ago
-
RE: Say hello and introduce yourself
@carrownisky where are you based? Would you like me con...
By Mars , 19 hours ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@transparent Good morning, the installer sorted our m...
By Cathyem1 , 20 hours ago
-
@roodo welcome to the forums and I’m really sorry to he...
By Mars , 21 hours ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
Don’t rip out a IVT! Amazing heat pump! Unless your com...
By greenlight , 23 hours ago
-
RE: Sunamp Thermino Heat Battery
Wow, I knew they were pricey, but didn’t expect it to b...
By Mars , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
@matthew_w good luck with the quotation and proposal pr...
By Mars , 1 day ago
-
RE: Should I make my radiators smaller?
Mine are also upstairs because I upgraded them before I...
By JamesPa , 1 day ago
Latest Topics
-
Adjusting 6kW Daikin's Weather Compensation Curve
By Ubert767 16 hours ago
-
Replacing knackered oil boiler with ASHP - Perthshire
By DowallyDrifter 18 hours ago
-
Should I make my radiators smaller?
By Scalextrix 2 days ago
-
Daikin Heat Pump Cycling Frequency?
By Ubert767 2 days ago
-
Battery storage to run Heat Pump.
By Broadsman 3 days ago