Looking for some advice – no viable installer/system – I'm stuck
Posted by: @redguy17my annual gas ussage is 26786 KwH( heating and hot water)
bolier is over 15 years old ( estimates 87% efficent)
i work at home so heat is on all day every day usually to 19 degrees
20% of the house ( a bed room and ensuite) are currently heated with electricity.
Currently during October to February we use about 6 tonnes of wood as wood burner is on from 6 am till 6pm most days.
Wow, thats a lot of gas - you said 120 sq m is that the total floor area or just the ground floor footprint? For comparison my 200sq m detached was about 20kWh gas consumption/7kW loss.
6 tonnes of wood adds about another 24MWh making 50MWh consumed in total on heating plus hot water, even without the electric. If we assume 85% efficiency thats still 43MWh, which equates to somewhere between 14 and 20kW loss. Do you have a lot of long showers or keep the windows open a lot?
Posted by: @redguy17PS. my pipe work is already 28mm . heat loss was calculated as 9.8 and 10.9 respectively. a Vaillant aro therm plus
10/12 kw double fan unit has been suggested by both.
If the consumption figures are correct then 9.8/10.9 appears to be an underestimate for the loss. However lets run with it for now.
The Vaillant double fan is a bit of a monster size wise, but there are several single fan models doing up to 12kW. Mitsubishi for example do 11.2 in rather neat single fan format. Others do single fan also but sometimes wider. it might be worth contacting someone who does one or two of these?
I would be very concerned about your consumption though, unless there is an explanation buried in my questions above. It seems just too high which makes me wonder where the heat is going! Perhaps you can shed some more light by answering the questions above?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@james PA
My kids do like a bath and have two a day wife also has two showers a day so possible our hot wter usage is bumping up figures alot.
Just got this back from local guy.
Revised heat loss down to 8
Changinf 5 rads up to double units ( 1600 x 600)
and this heat pump
- 26 Forums
- 2,111 Topics
- 46.4 K Posts
- 26 Online
- 3,402 Members
Latest Posts
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 2 hours ago
-
@quakerquaker As I have mentioned before, I have a firs...
By Toodles , 3 hours ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 3 hours ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 3 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
When i was looking I encountered one installer who does...
By JamesPa , 4 hours ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 2 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
Hi all, thanks for your help. The installer has confirm...
By Rikiarn , 3 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
Just in case anyone is looking at Planet Atmo- we've ma...
By benson , 3 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 3 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 4 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 4 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 4 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 4 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 5 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 5 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 5 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 7 days ago