Legionella cycle: Heat Pump or Immersion Heater?
Hi,
I've had my Grant ASHP for about 6 months now, and am slowly adjusting the set-up to hopefully more reasonable values.
Initially, DHW was set to temp of 55°C to run at 05:00, 11:00, and 15:00 (each for 1 hour), with a separate immersion heater element also running for an hour each Monday at 01:00 (for legionella sterilisation I assumed).
I've gradually reduced this until now I have it running from 15:00 to 16:00 only, set to 45°C, with the legionella cycle now running at 16:00 on Monday, directly after the ASHP has finished heating the water to 45°C.
My thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
Grant Aerona 3 10kW
Posted by: @mikeflMy thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
When I was looking at legionella cycles a while back, I found a lot of variation in opinion regarding how often to run the cycle. Regs say one thing, others point out that the bottom of traditional cylinders rarely if ever reaches the required temperature. The actual temperature and duration required to kill the bacteria though was pretty much consistent.
If you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyIf you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
For what its worth Vaillant R290 heat pumps (I discovered a few weeks ago) are designed to do the legionella cycle in the heat pump only, and appear (unlike many other HPs) not even to be capable of controlling the immersion. So thats the decision Vaillant made once they got to the point of having a FT high enough.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a Grant ASHP and have the HW output from it set at 60degC for 75 minutes daily. This will charge my 250litre pre-plumb Grant cylinder to 55degC usually within 1hr, and it maintains this temperature for many hours if no hot water is drawn off. It's more thorough at heating the cylinder than the built in 3kW immersion. If I use the immersion the built in immersion thermostat starts to cycle on and off but the tank content thermostat never reaches above 54degC. The immersion stat is set to it's highest setting, supposedly 65degC.
Also, the tank contents cool much more quickly with no hot water drawn off compared to when I heat using the ASHP. That to me proves that the immersion heating is not very thorough. I have more faith in the ASHP providing better Legionella protection daily to 55degC than the 3kW immersion weekly to 54degC! The ASHP heating coil is lower down than the immersion element and a much larger surface area.
The ASHP will give a CoP of 2-2.5 in heating, so is much more energy efficient than the immersion. I have solar PV+battery and a diverter. Initially I thought using the diverter would be most cost effective, but charging the battery using solar, and then using it to power the ASHP is more economical. I'm using less than half kWh than direct immersion, and can export more surplus PV that way at 15p/kWh. 'Every little helps!' 😀
-
HOT TIP - DHW Cylinder Thermostat
2 years ago
-
Why run a disinfectant cycle ?
4 years ago
- 26 Forums
- 2,283 Topics
- 51.1 K Posts
- 322 Online
- 5,944 Members
Join Us!
Podcast Picks
Latest Posts
-
@editor another great episode, but same as @phil-bell I...
By Grantmethestrength , 5 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I have the same unit and controller and it has been a j...
By Grantmethestrength , 6 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@agentgeorge this is a pic of the bleed valve that’s sn...
By AdamK , 8 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@nickhorne Unfortunately not. We take the "normal" IOG ...
By HCas , 9 hours ago
-
RE: Mixture of copper and plastic CH pipework. Will it be ok, or need changing?
In principle yes. Some heat pumps (I think including D...
By JamesPa , 10 hours ago
-
RE: New Fogstar 15.5kWh upright solution
For the common benefit, a quick update on this. Fogs...
By Batpred , 10 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Some of the circuits in my home are not protected by RC...
By Batpred , 10 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@editor I had to deal with E.ON Next while proces...
By TechnoGeek , 11 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Aqara sells some inexpensive hubs (usb dongle size) tha...
By Batpred , 12 hours ago
-
RE: Extend the colder range of the weather compensation curve?
@thebinman In answer to this and personal...
By TechnoGeek , 12 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
And here is what the Homely plots say for the last few ...
By Toodles , 14 hours ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey I’m always watching 👀My Clivet cont...
By Mars , 19 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard That's probably fine, provided as you say...
By GrahamF , 20 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
16Kw AIROSD Manufacturer: Foshan Model: QBKFXFC-...
By Polar bear , 21 hours ago
-
Just a suggestion but upload your images to an AI agent...
By RadWhisperer , 22 hours ago
-
RE: Daikin Wireless Thermostat
The switch from WDC to LWT i.e. pure WC is fairly strai...
By RadWhisperer , 22 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Thank you for your continuous research, and posts. As y...
By ectoplasmosis , 1 day ago
-
RE: Trying to understand my Nibe F1245
@barry-sharp, is this something you could help with?
By Mars , 1 day ago
-
I signed up for this, I think it will be a good one. Al...
By ASHP-BOBBA , 1 day ago