Legionella cycle: Heat Pump or Immersion Heater?
Hi,
I've had my Grant ASHP for about 6 months now, and am slowly adjusting the set-up to hopefully more reasonable values.
Initially, DHW was set to temp of 55°C to run at 05:00, 11:00, and 15:00 (each for 1 hour), with a separate immersion heater element also running for an hour each Monday at 01:00 (for legionella sterilisation I assumed).
I've gradually reduced this until now I have it running from 15:00 to 16:00 only, set to 45°C, with the legionella cycle now running at 16:00 on Monday, directly after the ASHP has finished heating the water to 45°C.
My thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
Grant Aerona 3 10kW
Posted by: @mikeflMy thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
When I was looking at legionella cycles a while back, I found a lot of variation in opinion regarding how often to run the cycle. Regs say one thing, others point out that the bottom of traditional cylinders rarely if ever reaches the required temperature. The actual temperature and duration required to kill the bacteria though was pretty much consistent.
If you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyIf you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
For what its worth Vaillant R290 heat pumps (I discovered a few weeks ago) are designed to do the legionella cycle in the heat pump only, and appear (unlike many other HPs) not even to be capable of controlling the immersion. So thats the decision Vaillant made once they got to the point of having a FT high enough.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a Grant ASHP and have the HW output from it set at 60degC for 75 minutes daily. This will charge my 250litre pre-plumb Grant cylinder to 55degC usually within 1hr, and it maintains this temperature for many hours if no hot water is drawn off. It's more thorough at heating the cylinder than the built in 3kW immersion. If I use the immersion the built in immersion thermostat starts to cycle on and off but the tank content thermostat never reaches above 54degC. The immersion stat is set to it's highest setting, supposedly 65degC.
Also, the tank contents cool much more quickly with no hot water drawn off compared to when I heat using the ASHP. That to me proves that the immersion heating is not very thorough. I have more faith in the ASHP providing better Legionella protection daily to 55degC than the 3kW immersion weekly to 54degC! The ASHP heating coil is lower down than the immersion element and a much larger surface area.
The ASHP will give a CoP of 2-2.5 in heating, so is much more energy efficient than the immersion. I have solar PV+battery and a diverter. Initially I thought using the diverter would be most cost effective, but charging the battery using solar, and then using it to power the ASHP is more economical. I'm using less than half kWh than direct immersion, and can export more surplus PV that way at 15p/kWh. 'Every little helps!' 😀
-
HOT TIP - DHW Cylinder Thermostat
2 years ago
-
Why run a disinfectant cycle ?
3 years ago
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 42 Online
- 3,351 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman Thank you for a very detailed review of...
By ASHP-BOBBA , 10 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 11 hours ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
I'm more than happy to try to help. Are you op...
By JamesPa , 14 hours ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 15 hours ago
-
RE: 5 Star Service from Havenwise
@sheriff-fatman Good post. I am also considering Hav...
By Morgan , 19 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 20 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet This is great assuming now the down stairs...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 2 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 2 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 3 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 3 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
I would switch it off and see if anyone noticed. We use...
By Anonymous 5011 , 3 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 4 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 4 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 5 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 6 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 6 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 6 days ago