Legionella cycle: Heat Pump or Immersion Heater?
Hi,
I've had my Grant ASHP for about 6 months now, and am slowly adjusting the set-up to hopefully more reasonable values.
Initially, DHW was set to temp of 55°C to run at 05:00, 11:00, and 15:00 (each for 1 hour), with a separate immersion heater element also running for an hour each Monday at 01:00 (for legionella sterilisation I assumed).
I've gradually reduced this until now I have it running from 15:00 to 16:00 only, set to 45°C, with the legionella cycle now running at 16:00 on Monday, directly after the ASHP has finished heating the water to 45°C.
My thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
Grant Aerona 3 10kW
Posted by: @mikeflMy thinking now is that the immersion heater element runs at COP of 1 (at best); and the HP runs at COP of 1 (at the very worst) so it actually makes more sense for the HP to do all of the legionella work i.e. on Mondays set the DHW to 60°C (the maximum it will permit) for 1 hour at 15:00, and no longer use the immersion heater at all.
Does this seem reasonable? I also think that 60°C is possibly too high, and something like 58°C would be fine. At the moment the HW is at about 58°C by 17:00 on Monday, and stays above 55°C until almost midnight. That seems more than adequate to kill legionella (over 55°C for 7 hours).
When I was looking at legionella cycles a while back, I found a lot of variation in opinion regarding how often to run the cycle. Regs say one thing, others point out that the bottom of traditional cylinders rarely if ever reaches the required temperature. The actual temperature and duration required to kill the bacteria though was pretty much consistent.
If you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyIf you can reach the required temperature using your heat pump then yes it makes a lot more sense to use it rather than the immersion coil. The only exception I can think of to this is if you have solar panels and a diverter, which essentially will do it for free (or a loss of export)
For what its worth Vaillant R290 heat pumps (I discovered a few weeks ago) are designed to do the legionella cycle in the heat pump only, and appear (unlike many other HPs) not even to be capable of controlling the immersion. So thats the decision Vaillant made once they got to the point of having a FT high enough.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a Grant ASHP and have the HW output from it set at 60degC for 75 minutes daily. This will charge my 250litre pre-plumb Grant cylinder to 55degC usually within 1hr, and it maintains this temperature for many hours if no hot water is drawn off. It's more thorough at heating the cylinder than the built in 3kW immersion. If I use the immersion the built in immersion thermostat starts to cycle on and off but the tank content thermostat never reaches above 54degC. The immersion stat is set to it's highest setting, supposedly 65degC.
Also, the tank contents cool much more quickly with no hot water drawn off compared to when I heat using the ASHP. That to me proves that the immersion heating is not very thorough. I have more faith in the ASHP providing better Legionella protection daily to 55degC than the 3kW immersion weekly to 54degC! The ASHP heating coil is lower down than the immersion element and a much larger surface area.
The ASHP will give a CoP of 2-2.5 in heating, so is much more energy efficient than the immersion. I have solar PV+battery and a diverter. Initially I thought using the diverter would be most cost effective, but charging the battery using solar, and then using it to power the ASHP is more economical. I'm using less than half kWh than direct immersion, and can export more surplus PV that way at 15p/kWh. 'Every little helps!' 😀
-
Ecodan unable to hit legionella target temp - what's the consensus?
2 weeks ago
-
HOT TIP - DHW Cylinder Thermostat
3 years ago
-
Why run a disinfectant cycle ?
4 years ago
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 362 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
Can you tell me if you have an FTC6 or FTC7 If you h...
By ASHP-BOBBA , 2 minutes ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Roughly this should cost you £250-£300 per peak month a...
By ASHP-BOBBA , 52 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa thank you again. I know using the offset to tr...
By MairiA , 2 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Here's that section of the Installation Manual: &nb...
By Transparent , 4 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 4 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Frost Protect/Freeze Stat is an operation mode, where D...
By F1p , 5 hours ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 6 hours ago
-
RE: Sunsynk Whole House Backup Issue
@sheriff-fatman - could you please re-post that in the ...
By Transparent , 7 hours ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 9 hours ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 9 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
I should think so, I thought that pretty much universal...
By JamesPa , 10 hours ago
-
RE: Setback savings - fact or fiction?
I'm also inclined to look into how a defrost is actuall...
By cathodeRay , 10 hours ago
-
MLCP (Multi-Layer Composite Pipe) for ASHP
@editor nope. The info you reported was sufficient for ...
By iotum , 20 hours ago
-
RE: Experience - New Build / Complete New Heating System
@vincro I would be surprised if it is much above 5 to 6...
By ASHP-BOBBA , 21 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Yes bang on and maybe I can illustrate that by way of e...
By iotum , 24 hours ago
-
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
A big thank you to @jamespa for all his efforts online ...
By trebor12345 , 1 day ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor It is indeed for servicing. My current service ...
By Morgan , 1 day ago