L9 error with Mitsubishi ecodan heat pump
Hi everyone,
Two years ago, I purchased a 14kW Ecodan air-to-water heat pump with R32 refrigerant.
Recently, I decided to install a Wi-Fi remote to monitor the temperature in my living room and control the heating more efficiently. However, after enabling the remote, I encountered an issue where the system displays an L9 error after a few hours, and the heat pump shuts down.
Based on my research, this error seems to indicate a flow issue. I have already taken the following steps to resolve it:
- Cleaned the water filter: I ensured there was no debris or blockages in the system.
- Checked the water pressure: It is approximately 1.6 bars when the system is off, which seems to be within the acceptable range.
- Increased the pump speed: I set the pump speed to level 5 to rule out insufficient flow as the cause.
Unfortunately, none of these actions resolved the issue.
During my observations, I noticed something unusual: the circulatory pump does not start even when the room temperature is below the set temperature. The pump only starts if I manually trigger it through the heat pump settings. Once it starts, it operates normally, which suggests the pump itself is not faulty.
Additionally, I activated the feature to display the ambient temperature reading, and the values seem accurate. This makes it even more puzzling why the circulatory pump fails to start automatically.
At this point, I am left without heating and am unsure how to proceed.
Does anyone have any insights into the cause of the L9 error or potential solutions to this issue?
Thank you in advance for your help!
Welcome to the forums and sorry to hear of your issues. So, your heating comes on, as displayed on your control panel, but your circulation pump doesn’t start automatically. Is that correct?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
As you state L9 is flow rate error, if you go to the service menu when the heat pump is running and then go into running information and put in code 540 it will tell you the flow rate in L/min. This has to be above 5L/min for the error not to show and a 14kw Ecodan should be running at 25L/min to transfer all the heat it can produce.
Hi @gary ,I tried to put code 540 to get the flow reading and the machine is giving me a flow of zero. It seems logical because the pump doesn't start. Do you have any clue why that is the case?
So many questions.
but if you’re having to manually activate the circulator it sounds like it’s not set up properly.
your language setting is set to French. Is that ok for you?
With the Mitsubishi system your circulator pump is the only pump that moves any water. There is no internal circulation pump inside the heat pump itself. In normal operation the circulator starts first before any heating takes place and this is fully automated when set up properly.
If you can give a full description of everything you’ve got installed including emitters and house size you will get the best advice on this forum.
my initial questions
Do you have the Mitsubishi pre plumbed cylinder? If not you probably can’t control circulator speed via the ftc controller. You will need to change speed on the circulator itself (push button)
What filter did you clean? There’s a metal deposits filter and there should also be a wire gauze strainer somewhere?
Who designed /installed it all? They may advise on how it’s set up.
I hope this helps so that this group can help you further…
@michel54, we had a similar issue recently that triggered an error (we don’t have an Ecodan), which turned out to be caused by a seized circulation pump. Since it couldn’t circulate water, it resulted in a flow error.
However, in your case, it sounds like the pump is working and circulating water when switched on manually. When you run it manually, are you still experiencing flow errors?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @michel54Recently, I decided to install a Wi-Fi remote to monitor the temperature in my living room and control the heating more efficiently
Did you use the Mitsubishi PAR-WT50R and if so after connecting the cable to the FTC, did you also set the appropriate dip switch in the FTC to on - I think it is SW1-8?
Hi everyone thank you for your answers.
This is a picture of my setup,
I have done all the plumbing myself. This is the diagram that i followed :
My flat is around 100 square meters and it is normal if it is in french because I live near Paris.
I used the PAR-WT60R-E with the associated PAR-WR61R-E, and i didn't forgot to put the switch SW1-8 on the on position.
I'm unable to tell you if by enable the pump manually I still get the flow error because by doing so just the pump starts and there is no heating.
Finally the filter that I cleaned looks like that and i was pretty cleaned. Like i didn't saw any suspicious things
@michel54, I reached out to our contact at Mitsubishi UK, and they’ve suggested getting in touch with Mitsubishi France, as they’ll have their own support systems in place, and before any fault-finding work can begin on the circulation pump outputs, there will likely need to be clarification regarding the wiring and the dip switch settings, specifically SW1-8 and SW2-1.
Have you contacted Mitsubishi support in France?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
hi Michel. The L9 fault is specific to a problem with the flow rate registered by your flow meter.
If the flow rate drops below the usual minimum (which is 5 litres per minute) then the L9 error is reported and your heat pump will be shut down.
I also said in an earlier message you may have more than one filter fitted and both may need to be cleaned out.
you have since sent a picture of your equipment schematic.
I can see you have a Mitsubishi Hidrobox which is a pre-plumbed cylinder and pre assembled system. You will have a Y-strainer built in to this box located at the back. This is where all the limescale, rust flakes and radiator scum will collect and if you haven’t emptied it in the past 2 years you will probably have a problem with it being choked up and stopping the flow of your heating system.
please let me know if you can locate this component and if it can be isolated or sealed and then the filter chamber opened.
IMPORTANT - did you put rust inhibitor chemical in the water when you filled up the heating system? I ask just to be 100% sure.
I attached a picture of how it looks on your assembled hydro box. Make sure you shut the taps before you try to unscrew the filter nut…. That’s very important.
you will get a load of bits that look like this inside the mesh filter.
Or even bigger bits like this.
Michel, its important to reply so we can be sure you have been helped. Thanks in advance.
And Merry Christmas….
Hi @sunandair,
Over the last few days, I decided to contact a professional to take a look at my heating installation to see if they could resolve the issue.
They ended up cleaning the same filter you had mentioned earlier (I wasn’t aware it existed), and it was indeed full of rust!
Previously, I had a mix of aluminum and iron heaters in my system. After noticing that the iron ones were rusting, I replaced them with aluminum ones and cleaned the filter I sent earlier, thinking it was the only one.
Now, my heating system has been running the entire night without any errors, so I believe the problem is resolved. However, I wanted to wait a bit longer before posting to confirm it’s fully fixed.
Additionally, my system had :
, but it seems it didn’t prevent rust as expected. I’m quite disappointed in its effectiveness.
Thank you all for your help, and Merry Christmas!
-
Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
1 month ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
2 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
2 months ago
-
Ecodan consuming 100kwh per day in new build!!!
2 months ago
-
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
2 months ago
- 22 Forums
- 2,082 Topics
- 45.7 K Posts
- 49 Online
- 3,370 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: DHW SET UP with Samsung gen 5
So I go to Daily and 1 slot enter time and on choice an...
By Alfapat , 51 minutes ago
-
@bart Best of luck moving forward, I look forward to he...
By ASHP-BOBBA , 13 hours ago
-
RE: Renewables & Heat Pumps in the News
By Morgan , 13 hours ago
-
RE: Ecodan EMP2 kit - is it any good?
Please note: heat meter accuracy at 95+% is as long as ...
By ASHP-BOBBA , 1 day ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
@jamespa I love going on the tools, I did it yesterday,...
By ASHP-BOBBA , 1 day ago
-
RE: Flow Rate & Low Loss Headers
Houses with reasonably low loss aren't going to require...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
If it's running on WC then at night it's quite likely t...
By JamesPa , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@majordennisbloodnok That’s OK as long as the ‘Terminol...
By Toodles , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron All features were in place for the last several ...
By AF1 , 2 days ago
-
RE: To relocate or add extra PV panels..advice required
The situation you are currently experiencing is represe...
By apollogrid , 3 days ago
-
RE: I don't need any heating in the summer. How do I turn my Samsung heat pump off?
SmartThings indeed allows remote control over the heat ...
By HCas , 3 days ago
-
RE: Remaining hot water/hot water flow meter
@lakey Hi, I had a quick read through and wanted to see...
By ASHP-BOBBA , 3 days ago
-
RE: I worry I've messed my Samsung settings up somehow
@ecobaker I missed this, sorry So 3031 was set to...
By Joshua , 3 days ago
-
RE: Forum updates, announcements & issues
@old_scientist thank you, and thank you to @Morgan for ...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
I am a UK based product manager for an energy storage s...
By shawnlee , 4 days ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
That's great and in principle I wouldn't disagree, but ...
By JamesPa , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Mitsubishi 8.5 kW Ecodan Standalone (PUZ-WM85VAA)
By Nell , 4 days ago
-