Icy cold weather, w...
 
Notifications
Clear all

Icy cold weather, weather compensation and consumption

34 Posts
16 Users
18 Reactions
5,424 Views
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 3384
Topic starter  

Thought I’d share this as a point of comparison. Two winters ago, our heat pump had been set to run the heating at a 45C set point. When we hit 0C for 24 hours, we did 120kW in electricity consumption. Admittedly, it was a happier time when we were paying 11p per kWh.

This winter it’s all weather compensation for us. Here’s our consumption over 24 hours with temperatures dropping to -2C and rising to 3C. Cold. While the 82 kWh is still high, that’s our full electricity consumption for the day including cooking (and I home brewed which uses power for a few hours). Our ASHP is an 18kW unit.

The house is warm, 21C in most areas. 

IMG 0241

Feel free to share your consumption data.

Pre-order: The Ultimate Guide to Heat Pumps

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
Quote
MikeFl
(@mikefl)
Reputable Member Member
Joined: 2 years ago
Posts: 123
 

This will be my first winter with my HP, and it currently seems to be struggling ... it's been trying for 3 hours to hit the target LWT for 0°C (46.5) but the interference of the defrost cycles keeps pushing it down. 3 days ago we didn't get above zero all day, and couldn't get about 20°C without additional heaters. My estimated COP is hovering just below 2.

Consumption peaked around 45kWh. These temperatures are more like January than November though!

Screenshot from 2023 11 28 09 50 00

(red line is LWT; orange line is OAT, averaging 0)

Grant Aerona 3 10kW


   
👍
1
ReplyQuote
(@iancalderbank)
Noble Member Contributor
Joined: 3 years ago
Posts: 643
 

mine for the 29th, max 3C day then -2 at night. 41kwh of electricity for 110kwh of heating. short-term COP is nearly 3 when it stable running in heating mode but the frequent defrosts bring it down 10% ish.

image

@mikefl if your system is struggling to reach target LWT with the frequent defrosts, that could make it worthwhile looking at your overall system to see if you can run with a lower WT? 

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
👍
2
ReplyQuote
MikeFl
(@mikefl)
Reputable Member Member
Joined: 2 years ago
Posts: 123
 

@iancalderbank Yes, that's something I'll be looking at. But I'm trying to hold off changing any WC parameters until I've sorted out the flow rates / balancing / commissioning, etc. (i.e. the stuff the installers should have done before leaving). Right now, I want to be confident the monitoring I've added is stable and accurate, so I can actually see the impact of any changes I make. And my strategy is "change one thing a week and see what happens", which is slow, but hopefully fruitful.

Grant Aerona 3 10kW


   
ReplyQuote
Morgan
(@morgan)
Noble Member Member
Joined: 4 years ago
Posts: 622
 

OUCH! 😲 

Yesterday.

Screenshot (44)
Screenshot (45)
Screenshot (46)

 

 

Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.

2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.


   
👍
1
ReplyQuote
 Gary
(@gary)
Prominent Member Member
Joined: 3 years ago
Posts: 350
 

@morgan I beat that by 2kwh

 

image

   
👍
1
ReplyQuote



Morgan
(@morgan)
Noble Member Member
Joined: 4 years ago
Posts: 622
 

Posted by: @gary

@morgan I beat that by 2kwh

 

-- Attachment is not available --

@gary I somehow doubt you are seeking awards and congratulations. 🤣 

Dreading today's readings given the temps overnight here.

 

Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.

2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.


   
ReplyQuote
(@kenneth)
Active Member Member
Joined: 2 years ago
Posts: 6
 

I recently installed a 5kw Mitsubishi ecodan to heat a small barn conversion- ground floor 35m2 with ufh. 1st floor ufh under engineered floor. 

I’ve been reducing the flow temp and find that at current temperatures (-1 to -4) that a flow temp of 26c keeps the room comfortable at 20c
A couple of questions 
  1.  is that flow temp too low for the heat pump to operate properly?
  2. Is the delta t of around 2c too low?        
    IMG 6897
    IMG 6896

     


   
ReplyQuote
 Gary
(@gary)
Prominent Member Member
Joined: 3 years ago
Posts: 350
 

@kenneth Ecodans don’t modulate down well I have ufh and it won’t run below 32C without cycling on and off which is what you are seeing.  The delta T is low as the flow temp is close to the actual temp of the room so the ufh can’t transfer the heat hence only a 2C difference between flow and return.  Delta T isn’t an issue, a lot of cycling is bad for the compressor.  You could turn up the flow temp and let it get the room to temperature quicker then let the thermostat turn it off and on as required.  You would get less cycling and shorter run times the energy consumption msg not be much different


   
ReplyQuote
(@kenneth)
Active Member Member
Joined: 2 years ago
Posts: 6
 

@gary Thanks for the advice. I will increase the flow temp and see what happens. If it gets noisy at higher temps I might revert back - neighbours haven’t complained about the noise but when it’s working hard it seems quite loud. From my point of view I’m relieved it’s working well heating this house. Lots of insulation in the floor ,walls. And roof have paid off. Minus 4.5 now outside but still 21c in here.😊
kenneth


   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 501
 

30th November was a bit cold we operated a setback to 16C and still got a TOPUP in the middle of the night

5A59519F 64DC 464C BA64 B62EEE96E831

Room temp is black line. Green is Outside temp.

608B9094 871C 4335 81A3 45F02A76D5FD

Flow temps for us typically around 40c with an all radiator system.

CE6AA3CB CD47 4AF2 B094 0617FBECB6B2

17th C house, 180sqM area, 21kw Rads (DT50), 8.5Kwh Ecodan, operating in Auto Adapt

7FDBE9EE A823 4567 AA48 97C5ECD223A7

typical defrost and recovery back to 40C

 


   
👍
1
ReplyQuote
Dunlorn
(@dunlorn)
Estimable Member Member
Joined: 3 years ago
Posts: 79
 

-10°C here overnight and still currently. House is just about at 18°C, so comfortable, but we've pulled 41kWh so far today. 😱

The one noteworthy thing, apart from eye-watering consumption, is that defrost frequency has been only around every 80-90 mins which has allowed the LWT to reach set point. Presumably this is a function of humidity - at around 0°-2°C with damp air or snow falling the defrost frequency can be every 30-40 mins so the LWT never really builds to its target. 

2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.


   
👍
1
ReplyQuote



Page 1 / 3
Share:

Join Us!

Latest Posts

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
ShieldPRO