Hot water temperatures
Come early evening after 3 showers and quite a bit of washing up throughout the day my ecodan with a 170L tank shows a temperature of 16c.
As it seemed that the water coming out the kitchen tap was still too hot for the hands I put a gauge to it and it shows 50c.
My tank is set to heat to 60c at 3.30am.
How could this be happening??
Not necessarily a massive problem I know.
Any advice appreciated.
The hot water is taken from the top of the tank, to be replaced by cold water at the bottom of the tank with a minimising of disturbance. (I am presuming you have a Mitsubishi tank, though this should still hold true for different tanks to different degrees.) This keeps a decent stratification between the blocks of hot water and cold water, the boundary gradually rising up the tank. Your tank will probably have two thermistors measuring the temperatures at different heights. If I recall correctly it is the lower of the two that is displayed as the tank temperature so it can drop surprisingly low while there is still a lot of hot water remaining in the tank above its level.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Posted by: @westkentCome early evening after 3 showers and quite a bit of washing up throughout the day my ecodan with a 170L tank shows a temperature of 16c.
As it seemed that the water coming out the kitchen tap was still too hot for the hands I put a gauge to it and it shows 50c.
My tank is set to heat to 60c at 3.30am.
How could this be happening??
Not necessarily a massive problem I know.
Any advice appreciated.
Thats sounds like seriously good news, you have a tank that is well stratified! Rejoice!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks for the replies.
My mind is at rest although it would be great to have more of an idea when it about to run out of H/W.
Yes it is a Mitsubishi tank.
8.5 system.
No pipes around tank with pipe insulation so will look to sort that.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 80 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
By Grantmethestrength , 12 hours ago
-
@eliuccio good to hear you’re happy with the install. A...
By Mars , 21 hours ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 2 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 3 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 3 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 5 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago