HOT TIP - DHW Cylinder Thermostat
Whilst running some tests on the disinfection cycle of my Daikin Mono 16kw I observed that the temperature of the booster heater was only getting up to 59.9C and not reaching the 60c mark. I had set it to reach 60C for 5 mins to satisfy the legionella cycle but it had been running for 30 mins and could not get pass that magic 60c number.
I had a read through the cylinder book and it said "make sure the thermostat is FULLY insterted", so i unscrewed the thermostat gland and found that i could push in the probe another 2-3 inches. Immediately the reported temperature of the DHW went to 62.9C! So just by pushing in the probe right to the end of the pocket the 60c was satisfied and the disinfection cycle completed for the first time ever!
By my calculations that will save 0.5kw of additional heating every time the DHW is run, so that will be a saving of over 180KW per year just by pushing in the probe where it should be.
This is because the water would be heating an extra 3c above the setpoints for my Eco and Confort settings.
see also
Correction, it should say saving of over 540KW per year just by pushing in the probe - as i have HW heat 3 x per day
-
Ecodan unable to hit legionella target temp - what's the consensus?
7 days ago
-
Warm weather and heat pumps.
8 months ago
-
Oversized Daikin 9kw
8 months ago
-
Daikin COP / energy used measurement from MMI
2 years ago
-
Why does my second unit sometimes start up unexpectedly on a Daikin split system?
2 years ago
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 155 Online
- 6,029 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@majordennisbloodnok — thanks, useful to know, I will l...
By cathodeRay , 14 minutes ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I found because I have very low heat loss I can set bac...
By RadWhisperer , 45 minutes ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 7 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 7 hours ago
-
I agree, I'm equally predisposed to a cold sunny winter...
By Old_Scientist , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj they will release smarter controls, its been m...
By swwils , 10 hours ago
-
RE: Speedcomfort radiator fans
Thats true, but having tried (and succeeded) in constru...
By JamesPa , 11 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash brilliant, thanks for the feedback
By energy9165 , 12 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair There I was, feeling grumpy, he said “Cheer u...
By Toodles , 14 hours ago
-
RE: Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
Depends on OAT. Mine cycles at OAT>10 and of course...
By JamesPa , 16 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent My conclusion is as you have noted, tha...
By Bash , 16 hours ago
-
That makes sense to me,although we don't know what the ...
By Transparent , 18 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
And to you too. Wishing you a very enjoyable festive s...
By Sheriff Fatman , 19 hours ago
-
RE: External pipework insulation
They do? But that isn't apparent from the photos we'r...
By Transparent , 21 hours ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 1 day ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 2 days ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 3 days ago