HOT TIP - DHW Cylinder Thermostat
Whilst running some tests on the disinfection cycle of my Daikin Mono 16kw I observed that the temperature of the booster heater was only getting up to 59.9C and not reaching the 60c mark. I had set it to reach 60C for 5 mins to satisfy the legionella cycle but it had been running for 30 mins and could not get pass that magic 60c number.
I had a read through the cylinder book and it said "make sure the thermostat is FULLY insterted", so i unscrewed the thermostat gland and found that i could push in the probe another 2-3 inches. Immediately the reported temperature of the DHW went to 62.9C! So just by pushing in the probe right to the end of the pocket the 60c was satisfied and the disinfection cycle completed for the first time ever!
By my calculations that will save 0.5kw of additional heating every time the DHW is run, so that will be a saving of over 180KW per year just by pushing in the probe where it should be.
This is because the water would be heating an extra 3c above the setpoints for my Eco and Confort settings.
see also
Correction, it should say saving of over 540KW per year just by pushing in the probe - as i have HW heat 3 x per day
-
Ecodan unable to hit legionella target temp - what's the consensus?
2 weeks ago
-
Warm weather and heat pumps.
8 months ago
-
Oversized Daikin 9kw
9 months ago
-
Daikin COP / energy used measurement from MMI
2 years ago
-
Why does my second unit sometimes start up unexpectedly on a Daikin split system?
2 years ago
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 323 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
RE: GSHP WOES! Midland based engineer recommendations?
@johnbroome perhaps, does it rise in pressure when heat...
By ASHP-BOBBA , 12 minutes ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
can you see here it not like a set of steps every 20 mi...
By ASHP-BOBBA , 14 minutes ago
-
So I hear the export MPAN that UKPN assigned should be ...
By Batpred , 2 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
From what I read, the Solis has a very long list of err...
By Batpred , 2 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Roughly this should cost you £250-£300 per peak month a...
By ASHP-BOBBA , 3 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa thank you again. I know using the offset to tr...
By MairiA , 4 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 6 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Frost Protect/Freeze Stat is an operation mode, where D...
By F1p , 7 hours ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 8 hours ago
-
RE: Sunsynk Whole House Backup Issue
@sheriff-fatman - could you please re-post that in the ...
By Transparent , 9 hours ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 11 hours ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 11 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
I should think so, I thought that pretty much universal...
By JamesPa , 12 hours ago
-
RE: Setback savings - fact or fiction?
I'm also inclined to look into how a defrost is actuall...
By cathodeRay , 12 hours ago
-
MLCP (Multi-Layer Composite Pipe) for ASHP
@editor nope. The info you reported was sufficient for ...
By iotum , 22 hours ago
-
RE: Experience - New Build / Complete New Heating System
@vincro I would be surprised if it is much above 5 to 6...
By ASHP-BOBBA , 23 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Yes bang on and maybe I can illustrate that by way of e...
By iotum , 1 day ago
-