Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

HOT TIP - DHW Cylinder Thermostat

2 Posts
1 Users
3 Reactions
1,905 Views
(@saf1973)
Estimable Member Member
Joined: 4 years ago
Posts: 59
Topic starter  

Whilst running some tests on the disinfection cycle of my Daikin Mono 16kw I observed that the temperature of the booster heater was only getting up to 59.9C and not reaching the 60c mark.  I had set it to reach 60C for 5 mins to satisfy the legionella cycle but it had been running for 30 mins and could not get pass that magic 60c number.

I had a read through the cylinder book and it said "make sure the thermostat is FULLY insterted", so i unscrewed the thermostat gland and found that i could push in the probe another 2-3 inches.  Immediately the reported temperature of the DHW went to 62.9C!   So just by pushing in the probe right to the end of the pocket the 60c was satisfied and the disinfection cycle completed for the first time ever!

By my calculations that will save 0.5kw of additional heating every time the DHW is run, so that will be a saving of over 180KW per year just by pushing in the probe where it should be.

This is because the water would be heating an extra 3c above the setpoints for my Eco and Confort settings.

 

see also

https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/ashp-and-pv-diverter-working-together#post-20301

 



   
👍
2
Quote
(@saf1973)
Estimable Member Member
Joined: 4 years ago
Posts: 59
Topic starter  

Correction, it should say saving of over 540KW per year just by pushing in the probe - as i have HW heat 3 x per day



   
👍
1