High air source heat pump running costs – Vaillant AroTherm Plus
Hi everyone, I'm looking for some advice please and have seen that there are some very knowledgable people using this forum. One month ago we moved into a new build house which has underfloor heating throughout the ground floor and radiators upstairs. The property has a large number of floor to ceiling glazed windows, but a high B rated EPC. The primary heat source is a air source heat pump, and the running cost for the first month appears to be very high - especially since it has been so mild. I will try to include all the details here in the hope that someone can provide an insight into our setup and what might be done to optimise it.
EPC details
- 276 square meters
- B rated (86 score)
- All scores "very good", except:
- Hot water "good" from main system
- Airtightness "average" - air permiability 9.9m3/h.m2 as tested (the three and two should be superscript)
- Primary energy use for propert is 58 kilowatt hours per square meter (kwh/m2)
- Estimated yearly energy cost for the property = £1001 (presumably this is based on gas?)
- Space heating 14994 kWh per year
- Water heating 2425 KWh per year
Current electricity usage (last month)
- Day rate = 1761.1 kwh
- Night rate = 579.7 kwh
- Total = 2340.8 kwh
- Average daily usage during December = 70.93 kwh per day (today's usage is 112kwh!)
Installation details
- Airsource Heat Pump Model - Vaillant ecoTherm Plus VWL 105/6 or 125/6 (not sure which)
- uniSTOR HP
- Buffer cylinder VPS R 100/1 M (I think)
- Controller multiMATIC VRC 700/4
- Heat Pump control interface module VWZ AI
- Weather compensated system control VRC 700/6 - I am not sure whether this is optimally setup because the rep indicated it could have been done differently, with a full Vaillant system rather than the themostat setup used. It looks to have just one zone configured and DHW. The temp is set to 26.0 degrees and set back to 26.0 degrees. See image of the big number on the panel the temp is normally around 16 degrees whenever I've looked - is this the flow heat? The DWH is set to 50 degrees. The water always seems to be hot enough. Is it correct for the weather compensated system control to be in the insulated area of the garage?
- VWZ MWT 150
- Six heating zones, five downstairs and one for the whole of upstairs. They are controlled using Heatmiser Neo2 Thermostats.
- Thermostats have been set to 20-22 during the day and around 17 at night depending on the room. The upstairs stat rarely seems to reach temperature (note large glazed windows on all sides and high ceilings)
- There are manifolds for the zone heating in the garage (boxed in) and the understairs cupboard.
- The system is installed in a store room section at the rear of the garage which I assume is reletively well insulated for this purpose, but definately not as well insulated as the house itself.
- My neighbour has a very similar setup (two similar new build properties are sited next to each other) in a slightly different house design and has experienced similar high levels of consumption.
Other information:
- I noticed water pooling on the plaform built for the unit (after raining) - I will flag this to the installer, might this impact performance?
- I have noticed some draughts in the house that need addressing, but can't believe this is the root cause.
If anyone can offer any advice about how to maximise efficiency of our system I would be extremely grateful because this is currently costing well over £400 per month which is significantly higher than expected, and we're still on a fixed tariff and it's not been that cold yet! We are in contact with Vaillant and any information that might help inform discussions will help a lot.
Happy to provide further information as required. Many thanks in advance.
I'm sure @derek-m will help you with the technical details. However, although my house is smaller than yours at 160m2, its heat requirements are similar because it's older. My average in December is 25.5kWh/day to heat the whole house to 21C for 19 hours/day. As long as the design of the system is sound you should be able to improve on 70kWh/day.
If the EPC is correct, your heating requirements are c. 15000kWh/year. You should normally need 15% of that in December, say 2300kWh. Even at a COP of 2.3, that's 1000kWh/month consumed; a lot less than you're using.
A question; how much hot water do you use?
Hi @webcmg
I have been searching for a manual that details how to check and set the weather compensation curve, but have not been able to locate one.
Unless you have a manual that shows this information, then I would suggest that you ask your installer to demonstrate how the weather compensation has been set on your system, and how it can be adjusted if necessary.
I have a 5KW aroTHERM plus.
Manual:
My settings (desired temp 20.5 / setback 20.5) System on 24/7
Adaptive heating curve: OFF
Heating Curve 0.6 (Temp Mod)
Min Flow Temp 20 / Max Flow Temp 45
Domestic hot water 48C
Cylinder boost offset 8K
3 bedroom detached new build, my unit also pools water below it.
HTH
Posted by: @kev-mI'm sure @derek-m will help you with the technical details. However, although my house is smaller than yours at 160m2, its heat requirements are similar because it's older. My average in December is 25.5kWh/day to heat the whole house to 21C for 19 hours/day. As long as the design of the system is sound you should be able to improve on 70kWh/day.
If the EPC is correct, your heating requirements are c. 15000kWh/year. You should normally need 15% of that in December, say 2300kWh. Even at a COP of 2.3, that's 1000kWh/month consumed; a lot less than you're using.
A question; how much hot water do you use?
Thanks for replying Kev. This is very reassuring. We don't use a great deal of hot water. There are two of us in the house and we normally have a reasonable length shower each day.
Posted by: @spdtdlI have a 5KW aroTHERM plus.
Manual:
My settings (desired temp 20.5 / setback 20.5) System on 24/7
Adaptive heating curve: OFF
Heating Curve 0.6 (Temp Mod)
Min Flow Temp 20 / Max Flow Temp 45Domestic hot water 48C
Cylinder boost offset 8K3 bedroom detached new build, my unit also pools water below it.
HTH
Thanks, what is the function of the set back temp and cylinder boost offset?
Posted by: @spdtdlI have a 5KW aroTHERM plus.
Manual:
My settings (desired temp 20.5 / setback 20.5) System on 24/7
Adaptive heating curve: OFF
Heating Curve 0.6 (Temp Mod)
Min Flow Temp 20 / Max Flow Temp 45Domestic hot water 48C
Cylinder boost offset 8K3 bedroom detached new build, my unit also pools water below it.
HTH
Also what's your target flow temp set to please? Also by 24/7 should I update this in the Time Programmes menu? Currently set to 06.00-22.00.
My heat curve was set to 1.1, now changed to 0.6
Just quick message of thanks to everyone for their help so far. Cheers, it's appreciated.
-
Mitsubishi EcoDan ASHP Settings not saving.
2 days ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 weeks ago
-
Heat Pump, DHW, UFH and Radiator Install
4 weeks ago
-
Installations in Flats
1 month ago
-
Heat Pump sizing - Further adventures of a boiler owner
1 month ago
- 21 Forums
- 1,747 Topics
- 37.4 K Posts
- 48 Online
- 2,036 Members
Join Us!
Latest Posts
-
RE: The UK’s Heating Nightmare: Why Many Systems Fail Homeowners
"within a few years" is a pretty long timeframe within ...
By Transparent , 20 minutes ago
-
RE: Samsung E911 intermittent issue
@netdonkey The model number for your Samsung indicates ...
By ASHP-BOBBA , 1 hour ago
-
RE: The good, the bad and the not that great – my heat pump installation
@dunlorn Good shout that buddy will give it a go at ...
By Burtis , 14 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@odd_lion I still have two copies of Bodge Buster left ...
By Mars , 23 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@bromide Thanks for the advice, doing it once but prope...
By ChandyKris , 24 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles 13.5kWh here, but no ASHP. 27kWh would be ampl...
By IanMK13 , 1 day ago
-
RE: What is a considered a decent weather curve?
Thanks Gary, I'll do that with the Drayton balancing ke...
By Crimson , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I've created a separate thread to discuss WC settings a...
By Crimson , 1 day ago
-
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Thanks I will try that and look at results
By A E Deans , 1 day ago
-
RE: New Samsung 12KW Heat Pump Help
No such luck yet - installers are saying their quoted 3...
By dinhp , 2 days ago
-
RE: Excessive performance/system issues with GSHP
@johnr Thanks - the Buffer tank is in the integral gara...
By didjerama_uk , 2 days ago
-
RE: Do thick walls make for warm houses?
@robl Thanks, thats interesting 🙂
By bontwoody , 2 days ago
-
RE: Mitsubishi EcoDan ASHP Settings not saving.
@fez96 Who’d of thought.? 👍
By Westkent , 2 days ago
-
RE: In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
A similar pattern happened again last night and into th...
By cathodeRay , 3 days ago
-
RE: Samsung HP secondary pump wiring
Thanks for the reply. I have asked a couple of days ago...
By Chris-in-Kemnay , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
Hi All We have 2 ASHPs, Solar/Battery system and soon...
By AlanB , 4 days ago
-
@westkent OK , Interesting , Im surprised that Airsourc...
By Alfapat , 4 days ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@potatoman I raised this with Secon, and here's what th...
By Mars , 4 days ago
-
RE: Smart meter installation – seamless or a potential nightmare?
@transparent, now hosted on our site as attached.
By Mars , 4 days ago
Latest Topics
-
Samsung E911 intermittent issue
By NetDonkey 15 hours ago
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 4 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 5 days ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 7 days ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 1 week ago
-
By R0y124 1 week ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 1 week ago