Posted by: @jamespaPosted by: @derek-mI have now completed some further improvements to the modelling tool.
It is now possible to adjust the desired IAT setpoint and also the OAT value to one decimal place. This therefore provides the capability to ramp up and down the setpoint and more closely match variations in OAT.
Have fun in the 'Playroom'.
I downloaded your modelling tool but there are lots of '#value' in the playroom. Is there something I need to dial in to start it working?
Hi James,
Which cells contain '=value'?
About 50% of the play sheet. I'm guessing they all rely on or derive from one 'problem' cell.
I have an old version of Excel (2003) it could be that, although unlikely because it usually issues a warning if there are unsupported features. I will try to narrow down the root cause.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Had cop of 3.7 for yesterday/this morning, that seems lot better then what i had last winter, 3.04 last winter but that included dhw. Freezing at 5am this morning so running from 530-10-30 had used 27kwh, thats heavy, house now warm, prob too warm so switched off heating and will adjust curve down to 34 at- 5 and 26@20 try that tomorrow. That's a 12 degree difference to installer setting on cold side.
Posted by: @jamespaAbout 50% of the play sheet. I'm guessing they all rely on or derive from one 'problem' cell.
I have an old version of Excel (2003) it could be that, although unlikely because it usually issues a warning if there are unsupported features. I will try to narrow down the root cause.
Did you resolve the problem? If not, then please provide one cell location and I should be able to trace back to the cause.
I may be able to save the spreadsheet in a different format if that would help.
Unfortunately I didn't resolve it. #value cells include E1-AA1, D14, 16-18,20,23,24,31,32,36... but
opening it in Libre office calc seems to have fixed the problem. I will report back if I work out what the problem was!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaUnfortunately I didn't resolve it. #value cells include E1-AA1, D14, 16-18,20,23,24,31,32,36... but
opening it in Libre office calc seems to have fixed the problem. I will report back if I work out what the problem was!
Hi James,
As you will have noticed I carried out quite a number of modifications to create the present version, one of which was to simulate the heat pump stopping and starting. This uses the cells D1 to AA1 to set cells D14 through to AA18 to zero if the heat pump is deemed to have stopped.
The formula in cell D1 sets the cell value bases upon the values of cells D9 (Setpoint Temp.) and D11 (Actual IAT), such that if D11 > D9 + 0.1C the heat pump is switched off, cell D1 set to 0.
Try overwriting the formula in cell D1 with the actual value 1 or 0 and see what effect this may have. You could also try changing the value in cell E9, above and below that of cell E11, to see how that affects the formula in cell E1.
Has it just come out of a dhw cycle, which would be at a much higher ft (and thus may take a while to cool down)?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa No DHW cycle is 2-3pm, this was much later. Judging on my curve, @7.2deg, what should flow temp be? Maybe its ok. Using lot less KWH last few days which is good as i have been lowering flow temp since and slab is probably warmed up.
Have desired temperature on front screen but think that changes with the curve.Posted by: @kev-mThere might a minimum LWT setting that applies whatever the WC curve says. Maybe that is 30?
@newhouse87 well your WC line is 34 at -5 and 25 at 20, so at 7 you expect 25+9*(11/25) = 29. So 30 is just 1C out which is likely well within the hysteresis. Situation normal so far as I can see
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
 - 2,265 Topics
 - 50.6 K Posts
 - 661 Online
 - 5,924 Members
 
Join Us!
Podcast Picks
Latest Posts
- 
                        
                                Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 1 hour ago
 - 
                        
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Indoor air temperature ie room temperature Outdoor ai...
By JamesPa , 2 hours ago
 - 
                        
Thanks @bontwoody!It's worth noting that you did purcha...
By F1p , 2 hours ago
 - 
                        
                                RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 3 hours ago
 - 
                        
RE: Grant 13kW Aerona3 - issues getting zones to temp
@crimson I asked Eskimo about their correction facto...
By JamesPa , 3 hours ago
 - 
                        
                                RE: My DIY Heat Pump installation
@pollar-bear Top job, I installed my own too and even t...
By bontwoody , 4 hours ago
 - 
                        
RE: Help me keep the faith with my air source heat pump installation
There are two definitions of sufficient volume. The fi...
By JamesPa , 4 hours ago
 - 
                        
                                RE: Who has a V2G EV installation
Not sure how you got that information, @batpred. As of ...
By Majordennisbloodnok , 4 hours ago
 - 
                        
                                RE: Midea ASHP – how to set weather compensation
@pash44pump - I stopped using the Mide app ages ago, so...
By cathodeRay , 4 hours ago
 - 
                        
RE: UFH downstairs and radiators upstairs balancing question
@ashp-bobba Can I pick you brain about mine ...
By davidnolan22 , 5 hours ago
 - 
                        
                                RE: Electricity price predictions
One persons view In sync with the Nesta figures s...
By Jeff , 17 hours ago
 - 
                        
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 19 hours ago
 - 
                        
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 1 day ago
 - 
                        
                                RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 1 day ago
 - 
                        
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 2 days ago
 - 
                        
                                RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 2 days ago
 - 
                        
                                @old_scientist I dont monitor the tank temperature but ...
By bontwoody , 2 days ago
 - 
                        
                                RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 2 days ago
 




 