Posted by: @s_gatoratorHi @cathodeRay , aren't all of the cycles in your chart defrost cycles? The clue I'm seeing is in the OAT graph, which has a small spike just after the compressor stops, presumably due to your outside temperature sensor being near the external unit and it getting some heat from the warm air at the end of the defrost cycle when the fan restarts. I have the same think on ours.
Of the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
The OAT spikes are indeed down to the sensor being, in my (Midea) case, inside the main case, meaning it is really the AIT (air intake temperature) rather than the true OAT. In normal cycling, when running, the unit exhausts cooler air, which lowers the OAT/AIT, when it is off the OAT/AIT recovers a bit with a small spike visible. In defrost cycles, this spike is more marked as the unit, as you say, exhausts warmer air. We've had quite a lot of discussion about the problems of using AIT rather than OAT on other threads, because of course it is the OAT which is actually the IAT that the weather compensation curve uses. The OAT being actually the AIT also complicates assessments of heat loss, because the rest of the house is sitting in the true OAT rather than the AIT, and finally, the local slightly cooler air around the heat pump has at least some detrimental effect on performance. My heat pump by the way isn't in a so called cold well, but it is 1ft in front of a wall, and inevitably some of the air drawn in at the rear comes from the cooler air in front of the unit. Some heat pump brands do have true OAT sensors, placed away from the unit, but many don't.
If the temperatures are lower, as in Europe, the moisture freezes out of the air and it looks like frosting does not occur below -7C or above 5C (quick internet search). Otherwise, here, I agree, it's a problem.
This is indeed what one hears. One wonders whether there is a sort of tinkling of breaking ice as the moisture drops out of the air at -7 degrees. More seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayOf the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
Ah! OK, that's interesting, thanks @cathodeRay, I stand corrected. NIBE have a separate OAT sensor. I now know about Air Intake temperature sensors!
Another way I can see defrost cycles is the evaporator temperature, which goes positive.
Posted by: @cathoderayMore seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
That's a very good question. I wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
End 1980's terrace in Southern England
NIBE 12kW air source heat pump
2 solar water panels
1 x Ohme ePod
1 x VW ID Buzz
Posted by: @s_gatoratorI now know about Air Intake temperature sensors!
That is indeed what they are, though Midea calls readings from it the Outdoor ambient temperature. As ambient is in practice rather vague (does it mean immediate surroundings, or just surroundings? And surrounding what? The heat pump? The building?), and on top of that given ambient temperature is often used interchangeably with outside air temperature, there is a recipe for confusion. As a result, someone on this forum, maybe @jamespa, used the unambiguous term Air Intake Temperature to name the variable.
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
I echo this!
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
We need to be on the lookout for a person with a name that sounds vaguely Eastern European or Scandinavian.
@editor might know someone.
Save energy... recycle electrons!
@transparent I'm actually working on a podcast episode along these lines and will start looking for homeowners in the next couple of weeks with surnames ending in "wicz" and "ski" 🤣
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Great! 😆
I'd also been keen to attract here some people who might later play a part in rebuilding Ukraine.
There's a lot of content on the Forum which would allow them to provide heat and light in locations which may only have intermittent power for years to come.
They don't need to replicate the energy supply system as it was before,
nor in the style we have here in UK.
It would a lot cheaper/quicker to create community clusters which can use multiple sources of energy when they are available, including micro-hydro which is more abundant in winter.
That would provide them with systems that are more resilient to outages.
Save energy... recycle electrons!
Vaillant's comment about de-icing is:
It is hard to say how often a de-icing cycle will take place as it depends on several things…
• The humidity of the air
• The amount of energy being taken out
• The period of time the energy is being taken.
The de-icing cycle will happen more often when the outside air temperature is around 2.5°C but will happen less often when the air temperature is below 0°C, as there is less water in the air.
From page 4 of
Posted by: @johnrbut will happen less often when the air temperature is below 0°C, as there is less water in the air.
Of course, that should be a key thing, warmer air can hold more water than cooler air. But in practice my heat pump seems to do much the same defrost activity (duration and frequency) at -4 degrees (0600-0900) as it does at 0 degrees (1800-0000):
Do any Vaillant owners have similar charts for their heat pumps?
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Ditto my Grant ASHP, During last week's cold spell it spent much of each day frosting then clearing, even down to -6C which was the lowest temperature we reached in West Oxfordshire. But then I know my overall installation was done far from optimally in terms of the kWh used at any OAT.
Mike
Grant Aerona HPID10 10kWh ASHP
@cathoderay & @transparent I have attempted to measure start up current spikes but don’t have high speed monitor devices. The monitor on our battery system monitors at once per 5mins which isn’t a fast rise but that’s not an adequate resolution. The octopus mini samples at one per min and shows a steady rise, so for me there is no fast switch on issue.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
@judith - thanks. Can you get leaving and returning water temperature at one minute intervals? That would let us see frequency and duration of defrosts on a Vaillant if you can get a chart covering a defrost period.
Midea 14kW (for now...) ASHP heating both building and DHW
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
2 months ago
-
Running my new Nibe ASHP efficiently
2 months ago
-
Weather compensation- why you should use it
2 months ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 639 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
@fretless6, where are you based? I might be able to con...
By Mars , 34 minutes ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 1 hour ago
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 3 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 4 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 5 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 9 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 16 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 16 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 20 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 20 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 23 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago