Posted by: @s_gatoratorHi @cathodeRay , aren't all of the cycles in your chart defrost cycles? The clue I'm seeing is in the OAT graph, which has a small spike just after the compressor stops, presumably due to your outside temperature sensor being near the external unit and it getting some heat from the warm air at the end of the defrost cycle when the fan restarts. I have the same think on ours.
Of the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
The OAT spikes are indeed down to the sensor being, in my (Midea) case, inside the main case, meaning it is really the AIT (air intake temperature) rather than the true OAT. In normal cycling, when running, the unit exhausts cooler air, which lowers the OAT/AIT, when it is off the OAT/AIT recovers a bit with a small spike visible. In defrost cycles, this spike is more marked as the unit, as you say, exhausts warmer air. We've had quite a lot of discussion about the problems of using AIT rather than OAT on other threads, because of course it is the OAT which is actually the IAT that the weather compensation curve uses. The OAT being actually the AIT also complicates assessments of heat loss, because the rest of the house is sitting in the true OAT rather than the AIT, and finally, the local slightly cooler air around the heat pump has at least some detrimental effect on performance. My heat pump by the way isn't in a so called cold well, but it is 1ft in front of a wall, and inevitably some of the air drawn in at the rear comes from the cooler air in front of the unit. Some heat pump brands do have true OAT sensors, placed away from the unit, but many don't.
If the temperatures are lower, as in Europe, the moisture freezes out of the air and it looks like frosting does not occur below -7C or above 5C (quick internet search). Otherwise, here, I agree, it's a problem.
This is indeed what one hears. One wonders whether there is a sort of tinkling of breaking ice as the moisture drops out of the air at -7 degrees. More seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayOf the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
Ah! OK, that's interesting, thanks @cathodeRay, I stand corrected. NIBE have a separate OAT sensor. I now know about Air Intake temperature sensors!
Another way I can see defrost cycles is the evaporator temperature, which goes positive.
Posted by: @cathoderayMore seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
That's a very good question. I wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
End 1980's terrace in Southern England
NIBE 12kW air source heat pump
2 solar water panels
1 x Ohme ePod
1 x VW ID Buzz
Posted by: @s_gatoratorI now know about Air Intake temperature sensors!
That is indeed what they are, though Midea calls readings from it the Outdoor ambient temperature. As ambient is in practice rather vague (does it mean immediate surroundings, or just surroundings? And surrounding what? The heat pump? The building?), and on top of that given ambient temperature is often used interchangeably with outside air temperature, there is a recipe for confusion. As a result, someone on this forum, maybe @jamespa, used the unambiguous term Air Intake Temperature to name the variable.
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
I echo this!
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
We need to be on the lookout for a person with a name that sounds vaguely Eastern European or Scandinavian.
@editor might know someone.
Save energy... recycle electrons!
@transparent I'm actually working on a podcast episode along these lines and will start looking for homeowners in the next couple of weeks with surnames ending in "wicz" and "ski" 🤣
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Great! 😆
I'd also been keen to attract here some people who might later play a part in rebuilding Ukraine.
There's a lot of content on the Forum which would allow them to provide heat and light in locations which may only have intermittent power for years to come.
They don't need to replicate the energy supply system as it was before,
nor in the style we have here in UK.
It would a lot cheaper/quicker to create community clusters which can use multiple sources of energy when they are available, including micro-hydro which is more abundant in winter.
That would provide them with systems that are more resilient to outages.
Save energy... recycle electrons!
@editor Don’t forget you have lady readers too so include “ska” for the married ladies. 😉 Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Vaillant's comment about de-icing is:
It is hard to say how often a de-icing cycle will take place as it depends on several things…
• The humidity of the air
• The amount of energy being taken out
• The period of time the energy is being taken.
The de-icing cycle will happen more often when the outside air temperature is around 2.5°C but will happen less often when the air temperature is below 0°C, as there is less water in the air.
From page 4 of
Posted by: @johnrbut will happen less often when the air temperature is below 0°C, as there is less water in the air.
Of course, that should be a key thing, warmer air can hold more water than cooler air. But in practice my heat pump seems to do much the same defrost activity (duration and frequency) at -4 degrees (0600-0900) as it does at 0 degrees (1800-0000):
Do any Vaillant owners have similar charts for their heat pumps?
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Ditto my Grant ASHP, During last week's cold spell it spent much of each day frosting then clearing, even down to -6C which was the lowest temperature we reached in West Oxfordshire. But then I know my overall installation was done far from optimally in terms of the kWh used at any OAT.
Mike
Grant Aerona HPID10 10kWh ASHP
@cathoderay & @transparent I have attempted to measure start up current spikes but don’t have high speed monitor devices. The monitor on our battery system monitors at once per 5mins which isn’t a fast rise but that’s not an adequate resolution. The octopus mini samples at one per min and shows a steady rise, so for me there is no fast switch on issue.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith - thanks. Can you get leaving and returning water temperature at one minute intervals? That would let us see frequency and duration of defrosts on a Vaillant if you can get a chart covering a defrost period.
Midea 14kW (for now...) ASHP heating both building and DHW
-
ASHP install contract and BUS grant money
6 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Running ASHP efficiently, general thought process. (Low and slow)
2 months ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 77 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 56 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 1 hour ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 3 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 22 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 23 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 24 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago