Grundfos Secondary Pump Flow Rate
I've 2 x 12kW Samsung heat pumps operating as master/slave each pumping a constant rate of 26l/min into a buffer tank, ie input flow is either 26 or 52l/min depending if one or both units are operating.
I've not really looked at what the heating circuit pump is doing tbh, the installer never mentioned anything about it and I just left it as it was. It's a Grundfos UPS 2 15-50/60 (pic and characteristic curve attached) that was set at position I.
I've no idea what the system head is (static lift around 2.7m with 14 rads, not sure of pipework) but leaving the pump on the lowest setting intuitively doesn't seem right, especially as flow into the buffer tank can vary by a factor of 2. Anyone any idea what I should expect to see here.....?
Thanks
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
static head isn't relevant, the water goes round in a circle, what goes up must come down. What matters is the resistance to dynamic flow. Given that you have up to 24kw of heat input at 56l/min, into your buffer, you need to move that much heat out of the buffer through the rads: flow needs to try to match the input side.
I can pretty confidently say, that circulating pump is nowhere near enough.To hit 56l/min (2.8m3/h) your dynamic head would have to be less than 2m with that pump, which is highly unlikely for a 14 radiator sized house (unless possibly the radiator side pipework has already been highly optimised / rebuilt.)
suggest you think about:
- what is the pipework layout and sizing on the secondary side? draw it.
- get a heat metering setup installed on the secondary side to actually measure what you are getting through
- as a "can't make it worse, could make it better" - with zero plumbing changes: buy the most powerful circulating pump that you can find (And afford) that fits into the same space (thus making the swap trivial). it looks like a 130mm. then see what you get.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Thanks @iancalderbank, that's helpful and good shout re the bigger pump. I'll look into that. I might need to start lifting a few floorboards as well!
Whilst I might have 24kW of installed capacity, the reality I've seen is nowhere near that. I've been keeping records of heat generated lately and, even in this recent really cold spell, it's only been managing 10-11kW (and that's with master/slave operation). Frequent defrost cycles mean LWT never reaches it's set point but gets stuck around 43°C ish, and that ends up a few degrees lower by the time it's been through the buffer as well.
It's been able to keep the house comfortable and stable at around 18°C so in that sense it's working and has given me a good indication of my heat loss with OAT well below zero. I still feel there's a way to go on my efficiency journey though......
Simon
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn FWIW, I was running at about 9kw also on saturday (-2C here all day), flow rate of 28l/min , that kept us at 21C inside . pretty sure that is my circulating pump going flat out. I use a UPMM 25-95 130, 8.5m head at 28l/min.
you could also look at a UPML 25-95 130 which doesn't drop below the 9.5M head until about 40l/min.
surveying the pipes / valves is important too, if there are thin ones, it'll be harder to get the flow rate up just by adding more push.
it does sounds like having read your other posts, your 2x12 setup makes for hard work.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Thanks @iancalderbank. You're not wrong about the hard work. We clearly don't need 24kW but have made some improvements to the house since the system went in so the heating calcs (which I presume exist but have never seen) may have been right once.
The way the master/slave set up works on the Samsung doesn't seem helpful to me. I wanted the slave to come in to support at OAT below 2°C (which I can set) but the trouble is when the master goes into defrost (or into DHW mode) the slave switches off too! So, at the very time when the extra help is needed it switches off, which means the value of the second unit is diminished. Anyway, that's a whole other story. In hindsight a 16kW unit and no buffer tank may well have been a better bet but we are where we are!
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn would it be feasible to individually control your two units rather than rely on samsung's master slave behaviour?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Yep, they both have separate controllers (currently linked) but can be reconfigured to run individually, controlled from a single run signal from the thermostat, a Hive in this case. I was going to get my installer to sort this when they come for the annual service in Feb but may bring forward. I don't want tandem running all the while though, really I just need to switch the second one on at end Nov and switch off again in Feb - one unit is more than capable the rest of the time.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn I was just pondering a possible idea for you: you could take control of each heat pump individually via modbus, run them as 2 separate rather than a linked pair. By control I mean setting the value of run / don't run, setting target temp (either IAT or LWT depending on mode). Modbus will tell you when its in defrost mode, along with the temps and flow rate. It might then be possible based on that data as input, to write your own control loop that keeps them in antiphase. (I'm assuming you've done to death with samsung why they stay in phase with the controllers linked and it can't be resolved).
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Joule Samsung have just told me it's not possible to alter the 'slave' to remain on whilst the master goes into defrost. I thought though, if set up in tandem operation, it's perfectly possible for the second pump (heat only) to continue running, while the first pump (heat and DHW) is in a defrost or in DHW mode as they both separately feed a buffer tank.
I don't have the modbus modules fitted so that's £400 for a pair for starters, plus fitting, so I was going to try and get the simple conversion to tandem running done first and see where that gets me. I'm not into coding so may well end up going down the Homely route to get this working better without my endless fettling.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn yeah it should be perfectly possible to treat them just as independent heat sources, decouple the master-slave, if send them both a call for heat, they'll of course both run. you'd be relying on an element of luck that they don't go into defrost mode at the same time. I was trying to find a way for you to make it "better than relying on luck" but as you say if you don't have the modbus modules there is an outlay there.
one very simple idea that might work (after you've decoupled them and they are running as seperate heat sources) that requires no coding:
- connect the output 230v of your thermostat to the input "run" terminal of HP1 controller.
- also connect it to an on/off switch (this is the master for HP2 use / no use).
- then connect from the output of the on/off to a push button timer - has to be one that breaks rather than makes the connection - timed for X minutes. where X is at least the length of a defrost. output of the push timer to run terminal of HP2.
- If you detect by observation they are in phase : go press the button. delays run signal to HP2 for X minutes. should hopefully get them out of phase.
homely will require modbus by the way and you'd need to ask them if they can control two heat pumps.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks, that's really helpful!
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
Posted by: @iancalderbankI can pretty confidently say, that circulating pump is nowhere near enough.To hit 56l/min (2.8m3/h) your dynamic head would have to be less than 2m with that pump, which is highly unlikely for a 14 radiator sized house
Hi @iancalderbank. I've done some (crude) monitoring today with the system stable, looking at heat being generated and measuring secondary side flow and return. This yields flow rates between 17-21lpm for my Grundfos, depending on which setting it's on. So, less than even with a single heat pump running (26lpm) but when both are pumping into the buffer this means most inflow is effectively just mixing and being recirculated back! I'm sure this must be acting to throttle performance so the 'benefit' of the second pump is severely limited. Happily, the house has remained comfortable, just, but I'd like a bit more headroom!
The Grundfos pump curve says delivery head is around 4.5m at 21lpm so getting to 56lpm would mean a massive, and impractical, increase in head, without upsizing a load of pipe. Getting to 30lpm would probably need about 9m of head so may be a sensible aim and should allow a comfortable margin of kW transfer.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 30 Online
- 5,655 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 27 minutes ago
-
RE: ASHP heat output monitoring
Agreed with the one qualification that increasing the n...
By JamesPa , 3 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 19 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 19 hours ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 19 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 19 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 19 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 3 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 3 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 5 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 7 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 7 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago