Grant Aerona3 13kW Noisy pipes after balancing
Hi @grantmethestrength, looks like your pump setting is on speed 3 in your Grant ASHP, grab the installation manual, read up on circulator pump dip switch settings and drop it to speed 2, circa 3000rpm. You may have to open up some rad lockshields and recheck, but getting a pump speed appropriate to the required flow with a reasonably open circuit is preferable to the pump running flat out against closed valves. The Grant ASHPs are defaulted to speed 3 when supplied, and few installers bother to change that, because throttling the flow on the Grant supplied flow setter/indicator is the lazy, quicker and easier option.
Thanks guys, I will open up the valves again and check the dipper switches when I get home tomorrow. Quick follow up question, if the flow has been limited at the ahem new to me flow valve 😜 if I change the pump speed to 2 do I just open the flow valve up to get say 28l/min or just open it as wide as it can go (well until it gets noisy again lol)? Is there a sweet spot?
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w Solar Panels
Solax 3.5kW Hybrid Inverter
@grantmethestrength The new to you flow valve is summat I know not of at this stage but, my gut feeling is that if it is in the water circuit, is partially closed and you have noise then, it is well worth noting its’ position then openi9ng it up fully to see what happens. If at this point, everything runs happily still but the noise hasn’t disappeared, then try the heat pump’s pump by reducing the speed a little. little by little improvements will come your way! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @grantmethestrengthif I change the pump speed to 2 do I just open the flow valve up to get say 28l/min or just open it as wide as it can go (well until it gets noisy again lol)? Is there a sweet spot?
Pretty much, noise is caused by high fluid velocity and turbulence created by restrictions, which is caused by things like nearly closed balance valves, TRVs, etc. Noise is also wasted energy, as is a pump on max speed against partly closed valves which could be on a lower speed setting. Open all the valves up, including the flow setter/indicator, set the primary circulator to an appropriate speed to get the required system velocity, and go from there 🙂
- 26 Forums
- 2,112 Topics
- 46.4 K Posts
- 47 Online
- 3,405 Members
Join Us!
Latest Posts
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 3 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 6 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
My installer fitted one of these as his choice for moni...
By Broadsman , 7 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 20 hours ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 20 hours ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 23 hours ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 1 day ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 1 day ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 3 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 4 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 5 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 5 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 5 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 5 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 6 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 6 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 6 days ago