Posted by: @crimsonCan ignore that, I must have gone down to check at wrong time. It's 38C which is about right now, return is 36C, so it's close already. No doubt will turn itself off shortly giving no time for anything to heat up.
Do you still have the buffer tank?
If the heat pump controller is indicating a small DT but the heat emitters are not emitting sufficient thermal energy, then not all the flow is getting to the heat emitters or possibly mixing is occurring within the buffer tank.
Posted by: @derek-mPosted by: @crimsonI believe this is in reference to what they originally designed which was as an example:
A Stelrad Concord Lo-line 296x1600
v
A Eskimo 200x1694
I believe they're referring to the actual water capacity (builder said it's like 1/4 but taking that with a pinch of salt).
Found the 1/4 reference - this is by Eskimo themselves stating it uses 1/4 water volume compared to a steel rad.
According to the manufacturer's websites, the Stelrad is rated at 1784 Watts and the Eskimo at 1540 Watts, I assume at DT50.
What is the calculated heat loss for the rooms in question and the design flow temperature?
Living room 1: 1063W requirement
2x Stelrads at 1784W have 0.301 correction factor at D20 = 1063/0.301 = 3531 covered by 3568 from rads
2x Eskimo at 1320W (one room has smaller ones) have 0.41 correction factor at D20 = 1063 = 2592 covered by 2640 from rads
Eskimo correction factors here (in the download link) - https://www.eskimodesign.co.uk/technical-resources/correction-factors
I’ve been told the heat specialist double checked this but I’ll ask him as distrust what I’m told these days.
My suggestion has been to double the height to 400mm which would give 2x2457W v 2x1320W. Even at the more normal correction factor that would be a lot more output.
ATM the rad: basically get 30-45 min cycles to heat up and not often.
They’re proposing we add a buffer tank. Heat specialist did comment that the LLH seems physically short so probably doesn’t help with the Delta.
@crimson Derek is far more knowledgeable on these matters than I so I will sit back and read only now. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@crimson Derek is far more knowledgeable on these matters than I so I will sit back and read only now. Regards, Toodles.
Hi Toodles,
Sorry if I appear to be jumping in. I started writing a reply to the original post, but before I could complete, my Son called and we had quite a lengthy chat. Afterwards I completed the reply and posted, only to discover that you had been your usual helpful self.
3 zone valves. Only one water pump in plant room, set to speed 2/3. Apologies don’t have a diagram.
1 zone valve manually on for upstairs heat dump.
downstairs is always calling for heat
Underfloor tends to hit temp and not calloften
@derek-m Not at all Derek, I’m OK on first line trouble shooting but have little in-depth knowledge of the more technical matters really. No offence taken at all - please carry on! Regards, Still Learning Daily, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @crimson3 zone valves. Only one water pump in plant room, set to speed 2/3. Apologies don’t have a diagram.
1 zone valve manually on for upstairs heat dump.
downstairs is always calling for heat
Underfloor tends to hit temp and not calloften
I assume that this water pump is after the LLH and supplying the various heat emitters via the 3 zone valves.
My understanding is that a LLH is like a small volume buffer tank, so it is necessary that the flow rate in and the flow rate out need to be reasonably well balanced, possibly slightly greater flow in than flow out.
I would suggest that you measure the temperatures on each side of the LLH and try to balance the flowrates, though this may be difficult if zone valves and TRV's are operating.
So the smaller rad in living 2:
30.6C in / 27.3c out - 3.3C diff
larger rad in Living 2
26.6C in / 29.4C out - wasn’t expecting that. This is the rad that keeps clanking. In temps are TRV side, out lock shield side. This was the rad that had to turn the lock shield quite a bit anticlockwise. Incase of note
Posted by: @derek-mPosted by: @crimson3 zone valves. Only one water pump in plant room, set to speed 2/3. Apologies don’t have a diagram.
1 zone valve manually on for upstairs heat dump.
downstairs is always calling for heat
Underfloor tends to hit temp and not calloften
I assume that this water pump is after the LLH and supplying the various heat emitters via the 3 zone valves.
My understanding is that a LLH is like a small volume buffer tank, so it is necessary that the flow rate in and the flow rate out need to be reasonably well balanced, possibly slightly greater flow in than flow out.
I would suggest that you measure the temperatures on each side of the LLH and try to balance the flowrates, though this may be difficult if zone valves and TRV's are operating.
sorry Derek, think I keep replying then not seeing all your posts. Same with Toodles.
water pump is after LLH before the zones yes.
heat specialist tried to balance flow rates. I have a number of photos of the temps around the LLH. Seem to get the heat through after plumbers worked out LLH was wrong way round (yes it’s been that messy).
often what I’m seeing with milder temps is not a big different top right (coming in) and bottom right (going out). If there is it’s short lived hence the cycling of the ASHP.
this is something the specialist commented on. With the LLH being so physically short it’s not helping maintain a difference to modulate at lower temps.
Photo attached but ASHP not actually running at this point
The direction of water flow through the larger radiator would appear to be in reverse, which could be part of the problem. My understanding of radiators is that where the inlet and outlet pipes connect near the bottom, the flow from the inlet pipe is directed up one or two of the vertical tubes to the top header, which runs the full length of the radiator.
The top header is therefore filled with warm water, which gradually flows down the remaining vertical tubes to the bottom header, which in turn is connected to the outlet pipe. The warm water therefore flows slowly down most of the vertical tubes distributing thermal energy as it does so.
If the water flow is in reverse, it could be that only certain parts of the radiator are fully being warmed and therefore distributing thermal energy into the room. This may be apparent if you have a thermal camera or measure the surface temperature at various points.
It would be useful to see the LLH temperatures with the system operating.
Will see if can do some surface temps of that rad when ASHP is running at some point today.
Photo attached of LLH whilst ASHP running this AM. I’m going to check the top left probe as it doesn’t report same temp as just before heating zone on the same pipe. Will move it as probably not getting as good a connection.
- 21 Forums
- 1,972 Topics
- 42.8 K Posts
- 23 Online
- 2,303 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
If you haven’t voted on this poll yet, please take a mo...
By Mars , 6 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
I should add that my system has two circulating pumps: ...
By JohnR , 7 hours ago
-
RE: Transforming a Derbyshire Property into an Energy-Efficient Haven
I feel that this is a good campaign for me to embark an...
By Mars , 7 hours ago
-
RE: Replacing knackered oil boiler with ASHP - Perthshire
On the basis that 1l oil = 10kWh and 1cu m wood = 2500k...
By JamesPa , 8 hours ago
-
RE: Battery storage to run Heat Pump.
@jeff The government are quite happy for the network ...
By Lucia , 8 hours ago
-
RE: Grant ASHP not reaching target temperatures
We may have similar and could share experiences: I ha...
By Hillswick , 8 hours ago
-
@sandman1600 Yes, you have the idea of what you need to...
By bontwoody , 9 hours ago
-
RE: Setback savings - fact or fiction?
OK, so I'm just thinking out loud here: You loose ene...
By BobTSkutter , 9 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist The OE guidelines mention that their con...
By Toodles , 11 hours ago
-
RE: Adjusting 6kW Daikin's Weather Compensation Curve
@jamespa I'm grateful for your advice.
By Ubert767 , 12 hours ago
-
@heatgeek thanks! I contacted them too.
By Eliuccio , 12 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
Thanks. I've seen the video several times at the beginn...
By cliffhanger , 15 hours ago
-
RE: Say hello and introduce yourself
@carrownisky where are you based? Would you like me con...
By Mars , 17 hours ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@transparent Good morning, the installer sorted our m...
By Cathyem1 , 18 hours ago
-
@roodo welcome to the forums and I’m really sorry to he...
By Mars , 19 hours ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
Don’t rip out a IVT! Amazing heat pump! Unless your com...
By greenlight , 21 hours ago
-
RE: Sunamp Thermino Heat Battery
Wow, I knew they were pricey, but didn’t expect it to b...
By Mars , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
@matthew_w good luck with the quotation and proposal pr...
By Mars , 1 day ago
-
RE: Should I make my radiators smaller?
Mine are also upstairs because I upgraded them before I...
By JamesPa , 1 day ago
Latest Topics
-
Adjusting 6kW Daikin's Weather Compensation Curve
By Ubert767 14 hours ago
-
Replacing knackered oil boiler with ASHP - Perthshire
By DowallyDrifter 16 hours ago
-
Should I make my radiators smaller?
By Scalextrix 2 days ago
-
Daikin Heat Pump Cycling Frequency?
By Ubert767 2 days ago
-
Battery storage to run Heat Pump.
By Broadsman 3 days ago