Ecodan 14kW flow rates too low?
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).
The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
I can only speak from our own experience and the optimal flow rate for the Global Energy Systems ASHP is over 30 litre and it doesn't trigger alarms. 40 litre seems high, but I'm not an expert. Will be interesting to see what others say.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
28mm pipe can carry 16.8kW of power if the difference in temperature between flow and return is 5C, which it probably is. This means that assuming the pipe is not kinked or set up like a rollercoaster, it is not the pipe limiting the flow to 30L/m by itself.
My best guess is that your unit is modulating its power downwards because your house doesn't need 14kW right now. I actually emailed Mitsubishi to ask what their minimum output is yesterday, so I can update with what they say if they get back to me.
Have you been cold the previous three winters? If not, I would just wait to see what happens and not worry about it. Assuming the flow rate was limited by something - be it a pipe or a connection or a pump or anything else - it's still able to provide almost 11kW. It's possible that the length of the pipe run is having a limiting factor, but I don't know how to work that out. Again, I'd wait and see what happens when it's actually cold.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Our 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Hopefully you won't need anything like 14kW most of the time so a lower flow won't matter.
https://library.mitsubishielectric.co.uk/pdf/book/ATW_Databook_R32_2020#page-68-69
That’s a good point about output. I’ve been checking when it’s just ticking over at 25-30c flow temp.
I’ll check again when it gets cold.
it was fine last year aside from one day when it was about -6c outside and I got a flow fault. But that’s below design temp anyway. We have an immersion in the buffer tank that we can use with excess solar so switched that on when it was ultra cold.
let’s see what this winter brings!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Hi Benseb,
The fact that it has been operating correctly for three years should provide you with the answer.
Setting weather compensation should not have a detrimental effect on operation, and should improve overall efficiency. Remember the old adage 'if it's not broken, don't fix it'. 😎
Posted by: @kev-mOur 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Why be like that and not also say the minimum output of an Ecodan is generally 3-4kW in above-zero ambient temperatures.
Although are you sure this isn't about a monobloc unit on page A-58? That has a wider 2-7kW minimum range depending on ambient and flow temperatures. I think if you bump into the 6+kW minimum often, that can be problematic and may mean the heat pump is oversize.
Be like what? I was trying to be helpful and show the questioner the whole picture rather than just quoting one number. That link has lots of other information too. I always like to see a link rather than just an opinion.
And yes I quoted the wrong page so thank you for pointing that out; the monobloc 14kW Ecodan is on p 58.
Posted by: @kev-mI always like to see a link rather than just an opinion.
I like to see both. I admit it irritates me a little when only a link is mentioned because before getting our heat pump, I read lots of forum posts where no answer was given, only a link, and that link has broken: maybe the linked site moved the file, or maybe the link was incorrect all along. So please, think of future people reading these discussions ☺
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 13 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Solar Thermal DHW and ASHP
Since you already have the ashp it makes little financi...
By Judith , 4 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
I think you’ll find it depends on the room heat loss. A...
By Judith , 4 hours ago
-
DESNZ doing a survey which asks the right questions!
DESNZ have engaged ICF to do a survey of people who hav...
By Judith , 5 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 5 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil Fwiw I have the 7kW model with which I'm, ver...
By JamesPa , 6 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@grahamf you appear to value your recirculating loop de...
By Judith , 6 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 6 hours ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 9 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 10 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 1 day ago
-
Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ...
By immunity , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 2 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 2 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 2 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 2 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 days ago
Members Online
No online members at the moment