Flow rate discrepancy between ASHP and manifold
Hello,
Firstly thanks for all the guidance on this forum, it has been a great help. I now get to the stage where I can't find the answer to my question on overall system design and would like some guidance.
Following best principles for efficiency I have tried to simplify my design to remove buffer tanks, manifold mixers etc. Running out as an open loop single zone.
My installers are going to put in an 11.2kw ecodan ASHP next week and connect to my 7 port manifold, with an average loop length of 80m going through 16mm pert al pert pipe at 150mm spacing in a 50mm cemfloor screed above 150mm Celotex.
No zoning, no pump/mixer on manifold, no buffer tank. Large 150l volumiser on the return. Large bore pipe size.
My problem is that the 11.2kw ecodan docs say it is most efficient at 32L/min flow, however my UFH wants probably around 17l/min flow. As I understand it If I run the UFH at 32l/min that is too much flow and could result in noise and reduced efficiency (delta T) because the water isn't in the pipes long enough to transfer it's heat to the screed.
How do I balance this isue being as I have removed the buffer tank and manifold pump from the design? I could drop the flow to the minimum the ASHP would take, 17l/min, but then the heat pump isn't working efficiently.
Thank you
If you have a UFH system that is a max design 6kW output (17lts flow) why are you installing a 11kw Ecodan?
Assuming the below is not far off either your loops need more flow to get up to 8.4Kw or you should reduce the ASHP to match closer to your design flow. Also the HP can capacity modulate down to the lower capacity but if you don't send the flow rate though or have a big enough emitter circuit it will not use the full capacity of the HP.
System Details:
7-port manifold → 7 loops
Average loop length: 80 m
Pipe type: 16 mm PERT-AL-PERT
Pipe spacing: 150 mm (0.15 m)
Screed: 50 mm Cemfloor (liquid screed, good conductivity)
Insulation: 150 mm Celotex (very good insulation, so minimal downward losses)
Step-by-Step Estimation:
1. Area Heated:
At 150 mm pipe spacing, each meter of pipe covers ~0.15 m².
Each loop (80 m) covers:
80 m×0.15 m=12 m280 \text{ m} \times 0.15 \text{ m} = 12 \text{ m}^280 m×0.15 m=12 m2
7 loops → total heated area:
7×12=84 m27 \times 12 = 84 \text{ m}^27×12=84 m2
2. Typical Heat Output per m²:
With 150 mm spacing in 50 mm screed and good insulation, you can typically expect 80–100 W/m² for standard flow temperatures (~45–50°C flow, ~35°C floor surface).
Using a conservative average of 90 W/m²:
84 m2×90 W/m2=7,560 W(7.56 kW)84 \text{ m}^2 \times 90 \text{ W/m}^2 = 7,560 \text{ W} \quad \text{(7.56 kW)}84 m2×90 W/m2=7,560 W(7.56 kW)
Estimated heat output: 7.5 – 8.4 kW
(depending on exact flow temperature, floor finish, and room air temperature)
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Welcome to the forums.
Your approach to stripping out the inefficiencies (buffer, mixer, zones, etc.) and keeping the system as open loop as possible is solid. It’s encouraging to see more homeowners and installers heading down this path.
You’re also absolutely right to raise the point about flow rates and potential mismatches between what your heat pump “wants” and what your UFH can comfortably handle. It’s a common pinch point in these simplified systems.
The 11.2kW Ecodan does indeed state an optimal system flow rate of around 32 L/min for peak efficiency and that’s based on a delta-T of 5C. However, if your UFH is designed for a lower flow rate (say around 17–20 L/min), pushing 32 L/min through the loops could result in excessive velocity, noise and a very narrow delta T, which could reduce the system’s ability to transfer heat effectively into the slab.
This is where your volumiser can play a useful role because it increases the system’s volume and helps stabilise flow rates and temperatures. It won’t allow for different flow rates on the primary and secondary circuits like a buffer with hydraulic separation would, but it still gives your system a bit more breathing room.
If the installer has selected the correct primary circulation pump (and it’s controllable), you can tune the system to match what the UFH can handle (perhaps 24–26 L/min) to see if that delivers enough power and keeps the heat pump within its happy place, even if it’s a touch below its ideal.
Once the system is commissioned, logging flow rate, delta T and run times will be key. If you’re seeing very short cycle times, high return temps, or a rapidly closing delta T, then you might need to revisit flow balancing.
It's an interesting question though, and I'll ask my panel about it this Friday on the podcast.
As a general reference (for others reading this), typical recommended flow rates for common ASHP outputs are:
- 5 kW: ~14 L/min
- 7 kW: ~20 L/min
- 8 kW: ~23 L/min
- 12 kW: ~34 L/min
- 16 kW: ~46 L/min
Let us know how it goes after commissioning because it's always good to see real-world examples.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks. I'm installing the 11.2kw ecodan because that is what the install company calculated. I'm pretty sure that the full 11.2kw will only be needed to for a quicker domestic hot water cycle (300l DHW tank). I don't trust the heat loss calcs the installers have given me so an not sure exactly what loss my building will be, though for what it's worth they calculated 9kw heat loss for the building.
If I'm reading your reply correctly I could run the UFH system at a lower flow rate with the heat pump modulated down to 70% or so at max when it's supplying the UFH.
My next question then is... What is more efficient...
1) 11.2kw open loop with modulation on the heat pump and lower than nominal flow rate for the heat pump. Open loop no buffer tank
Or
2) 11.2kw with buffer tank and a second pump/mixer on the manifold, so that the heat pump is running at it's nominal 32l/s efficiency and the UFH is running at its 17l/s.
It's too late to change the UFH loop design now.
Posted by: @ashp-bobbayou have a UFH system that is a max design 6kW output (17lts flow) why are you installing a 11kw Ecodan
That was my thoughts exactly, something is wrong.
Posted by: @ashrollsHow do I balance this issue
By having the correct sized heat pump installed or if your heat loss calculation is correct, your floor heating will not be good enough.
If your house heat loss is 6kW, you heat pump would be sized to match at design outside temp (with an allowance to heat DHW).
Then system flow rate reduces to about 15l/min max. You then start with all UFH loops fully open at the flow meters, this allows heat pump flow to maximise flow without resistance. You then tweek down the flow on loops where the room is too warm.
Posted by: @ashp-bobba35°C floor surface
If they have designed for that hot a surface temperature, expect issues with floor covering and your feet.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Forgot to mention with the right size of heat pump and UFH you could delete the volumiser. I operate 7 loops on a 6kW heat and open loop no cycling issues. The floor readily takes the heat away.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
@ashrolls Open loop is better, MY AI went a bit daft with the floor surface temp, 35 is to hot, run the loop at 35 and have a floor temp at 25.
The ecodan 8.5kw does the 300ltr cylinders just to let you know, if you have 8kw of emitters you will not get much more than 8kw out of the system regardless of size of the ASHP above that.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashrolls11.2kw ecodan
Looking at the data for that heat pump, it looks to have very good modulation, down to 4.5kW at 7 degs. So if your heat loss is near 9kW at design you will need about 4.5kW at 7 degs. So should not cycle unduly. So questions is do you really need a volumiser either?
If you set the circulation pump to variable speed, you should have a heat pump that does the job even though it's oversized.
From your options no buffer would be the only choice and although not mentioned no UFH mixer and pump.
For your info I am currently pumping 19L min through 7 loops you can hear nothing. So close to 7kW.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @johnmoIf you set the circulation pump to variable speed, you should have a heat pump that does the job even though it's oversized.
This is where I'm still a bit confused, If the minimum flow of the heat pump is 17l/min and the maximum flow I can put through the UFH is 19l/min surely I can't have the circulation pump on a variable speed?
Is it that when the heat pump is modulated down to a lower kw output, the optimal/nominal flow rate is also reduced down from the 32l/min in the documentation?
Posted by: @ashrollsThis is where I'm still a bit confused, If the minimum flow of the heat pump is 17l/min and the maximum flow I can put through the UFH is 19l/min surely I can't have the circulation pump on a variable speed?
Is it that when the heat pump is modulated down to a lower kw output, the optimal/nominal flow rate is also reduced down from the 32l/min in the documentation?
Think you need to download the technical manual.
This is an extract from it, the min speed isn't 17 it's 14.4.
As you will see the pump range is between 14.4 and 32L min. But also read note 3 - to get that rate (32L) you need an additional pump. The pump isn't a fully variable speed (as said earlier ) you select a speed and it's fixed. If you were going through a buffer the recommendation for flow rate is only 20.2.
So pretty simple for the installer. They will match the heat pump output to what the floor needs. The heat pump will add or reduce load through modulation.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
That's useful thanks, I hadn't seen that table before. Since I'm not having a buffer I don't know how useful the 20.2 figure is. If I'm interpreting this correctly the range I can use is 14.4l/min (minimum of heat pump) to around 19l/min (maximum of UFH). Anywhere within this range still leaves me far below the recommended heat pump flow of 32l/min so my concern remains about the efficiency loss running in the lower flow range will cause when the heat pump is operating.
- 22 Forums
- 2,072 Topics
- 45.4 K Posts
- 55 Online
- 3,350 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 4 hours ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 6 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
Hi Bobba, thank you so much for the considered and deta...
By MelonBuffet , 7 hours ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 9 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 10 hours ago
-
RE: What’s the modern take on advised types of insulation?
The former Energy Secretary claims his 1930s house is “...
By Mars , 14 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
I would switch it off and see if anyone noticed. We use...
By Johnmo , 1 day ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Actually I might try just turning it off and on again…....
By benson , 2 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 3 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 4 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 4 days ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 4 days ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 4 days ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 4 days ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 4 days ago