Failed install (initial SCOP1.8), clueless installer compounded by poor manufacturer support. Help needed desperately!
Hi All,
My first post. I've learned a lot from reading this forum, wanted to validate my understanding and thought others might learn from my terrible experience.
Having completed a 5 month complaints process and made limited progress with the installer I've now had to escalate to the scheme provider/trade association. Given apparent collusion I'm not specifically sharing details (publicly) of the companies involved at this time.
Improvements
- reducing legionella cycle settings to minimum required (temp 60, scheduling & duration)
- reducing DHW to minimum required settings (temp 45, scheduling & duration)
- running in compensation curve setting to discover required water temps for desired internal temps for any given outside temp (45@-2 & 25@15)
- adjusting flow rate to maintain delta 5-8 (ie. gap between flow and return temps)
- Freeze stat function disabled as glycol had been added to the system
All the above increased COP to 2.7 on a perfect day ie. 30% (Thank you RHH!)
Problem
The system was short cycling
I couldn't achieve internal temp above 19+ regardless of water temp
I couldn't achieve a delta 5+ even with pump running at 8l/min (manufacturers guidelines state optimal is 17l/min) and the pump wouldn't couldn't achieve 14+l/min.
This suggested:
- the ASHP was too large for my property AND/OR
- the radiators were too small
- the pump was insufficient
- something else?
1. A 6kwh system had been installed. My heat loss survey=3.6 (however u values, room sizes, layout were all wrong) and it was amended (post install) =3.1
2. The installer 1st requested additional payment for a bathroom radiator, then refused to fit it, then only complied after I refused to sign off completion. However the amended heat loss survey has subsequently found that the kitchen radiator is also too small (K3 needed).
3. As yet no reply at all regarding the pump that can't achieve optimal flow rate
4. Flow/return temps don't tally with flow/return temps at the radiators. Also flow temps never fall below 25 and return temps never fall below 20.
"The Game's Afoot"
I queried the proximity of the design with the installer and manufacturer
At the installer's insistence a sales manager from the manufacturer attended, later emailing: "all I can advise.... it's been installed as per our instructions" and sharing a document that suggests "initially setting min flow temp to 35" (erm I get it my flow temp is low but don't I get to decide how hot my house is?)
"You need a volumiser- Yep like a hole in the head"
In the interim 3 months the installer had decided to add a 32 litre volumiser in my loft (without my consent) on the longest radiator run in the house not on the main return (although I'd like it on flow for defrost cycles).
- My entire system was less than 40 litres
- Narrow delta continues
- SCOP remains 2.3
- Half of the heated volume of water is now located outside the insulated envelope of my house (wasted heat not included in SCOP)
- Balancing radiators is a nightmare (7 vs 50 litres)
The same sales manager has defended this ridiculous decision sharing the turn down datasheet
HELP?
- The manufacturer's home help technical team have yet to respond to my request for 5kw turn down data- can anyone help?
- I've argued this would appear to show that my ASHP is too large, not that I need a bucket of warm water in my loft- Anyone have any resources that might confirm this please? The missing K3 in the kitchen would add volume but not much.
- I've argued that a pump that can only achieve 14l/min given an ASHP that requires 17l/min optimal flow isn't compliant as it isn't fit for purpose. Anyone have any resources that might help please?
- I've argued that flow/return thermostats that don't record flow/return temperatures aren't compliant as they aren't fit for purpose. Anyone have any resources that might help please?
Thank you for reading.
Will reply later in detail. Who’s the manufacturer?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@bart great. editor@renewableheatinghub.co.uk.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@bart Hi Bart,
Well done for the improvements, there is room to make these system run cop 3.6-4.5 so there must be some more tweaks that can be done, its super important to match the ASHP to the flow rate and emitters output which starts with design (also works in reverse and essential to match the emitters to the output of the ASHP.
- The manufacturer's home help technical team have yet to respond to my request for 5kw turn down data- can anyone help?
Will need to know which manufacturer for the sheet, Mars no doubt will help you with this not to disclose at this point.
- I've argued this would appear to show that my ASHP is too large, not that I need a bucket of warm water in my loft- Anyone have any resources that might confirm this please? The missing K3 in the kitchen would add volume but not much.
Please share the extensive heat loss and design report the installer and designer would have completed.
- I've argued that a pump that can only achieve 14l/min given an ASHP that requires 17l/min optimal flow isn't compliant as it isn't fit for purpose. Anyone have any resources that might help please?
What is your pump model, where in the home (what floor) is it installed and how high is the highest radiator?
- I've argued that flow/return thermostats that don't record flow/return temperaturePosted by: @bart
Freeze stat function disabled as glycol had been added to the systems aren't compliant as they aren't fit for purpose. Anyone have any resources that might help please?
Are you talking about sensors here? if so not all manufacturers record in the log what they say but the system will be reading them to maintain that perfect 5º(DT)
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba Hi Bobba,
Thanks for your reply
I'm trying to find a way of sharing the latest heat loss survey (having removed all identifying info) and will share ASAP. My impression is that all ground floor rads are undersized as their 1st effort was an exercise in creative writing I've lost any faith in their data.
Pump is below:
For metering I've relied on outputs from the ASHP manufacturer's controller. (low =8, med =11 high =14l/min) Its on the 1st floor same height as highest radiator. x3 heating loops which combine before the main ASHP feed and return.
1. kitchen rad
2. x2 bd2 and bathroom rads
3. goes up through the loft to feed the BD1 & lounge rads (which is where they've put the volumiser I believe on the return).
Thermostat/ sensors. Yes hence my concern. They appear to track rad F/R temps above 25/20 OK, (compromised by the 50litre lounge/bd1 loop)
Today DHW heating cycle (roughly delta 5)
Thanks again
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Recently viewed by users: Majordennisbloodnok 60 minutes ago, Abernyte 55 minutes ago, Bart 53 minutes ago.
- 22 Forums
- 2,082 Topics
- 45.7 K Posts
- 18 Online
- 3,370 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron will it bring the rating up in a property with G...
By AF1 , 1 hour ago
-
RE: To relocate or add extra PV panels..advice required
The situation you are currently experiencing is represe...
By apollogrid , 6 hours ago
-
RE: DHW SET UP with Samsung gen 5
no it’s not it just a search of user manuals , being ca...
By Alfapat , 12 hours ago
-
RE: I don't need any heating in the summer. How do I turn my Samsung heat pump off?
SmartThings indeed allows remote control over the heat ...
By HCas , 14 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
@jamespa I have not had a heat calc yet that is below 4...
By ASHP-BOBBA , 15 hours ago
-
RE: Remaining hot water/hot water flow meter
@lakey Hi, I had a quick read through and wanted to see...
By ASHP-BOBBA , 17 hours ago
-
@bart Which county are you in? Kent by any chance? S...
By ASHP-BOBBA , 19 hours ago
-
RE: I worry I've messed my Samsung settings up somehow
@ecobaker I missed this, sorry So 3031 was set to...
By Joshua , 20 hours ago
-
RE: Flow Rate & Low Loss Headers
It sounds like you have thought about this a lot and ev...
By JamesPa , 20 hours ago
-
RE: Forum updates, announcements & issues
@old_scientist thank you, and thank you to @Morgan for ...
By Mars , 22 hours ago
-
RE: Say hello and introduce yourself
I am a UK based product manager for an energy storage s...
By shawnlee , 1 day ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
That's great and in principle I wouldn't disagree, but ...
By JamesPa , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Mitsubishi 8.5 kW Ecodan Standalone (PUZ-WM85VAA)
By Nell , 2 days ago
-
-
RE: Jokes and fun posts about heat pumps and renewables
This is the plan to get our next heat pump installed an...
By Mars , 3 days ago
-
Thanks! That is most useful. I've had a look at the Mid...
By benson , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I found that Homely blog a few days ago and was tempted...
By cathodeRay , 3 days ago
-
RE: Home energy storage & battery register
I love that! Unfortunately there doesn't appear curr...
By JamesPa , 4 days ago