Interested in hearing from others on their Heat Pump evaporator temperature just prior to a defrost. A few other bits of data might be useful. My details are:
Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes. Southern England.
Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1
2024 build bungalow
Southern england
179 m2
High level of insulation
Underfloor heating
All 12 circuits are fully open all the time
1 thermostat in family room
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels
Energy used by heating 2527 KWh - 7527 KWh (SCOP 3.5 approx)
For an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Typical minimum evaporator (saturation) temperature for R32 heat pumps
–25 °C to –30 °C which is common for modern domestic R32 ASHPs.
Note, some manufacturers restrict operation to –20 °C for efficiency and reliability reasons (reduced thermal stress).
High-performance “cold-climate” units may reach –35 °C, but these are less common in the UK/EU market.
Why the limit exists
At very low evaporating temperatures:
Suction pressure drops very low (R32 saturation pressure at –25 °C ≈ 1.7 bar abs).
Mass flow and capacity reduce sharply.
Risk of liquid floodback to the compressor during defrost increases.
Compressor discharge temperature rises significantly.
Most manufacturers provide an operating envelope showing safe combinations of suction (evaporating) and discharge (condensing) temperatures.
Rule of thumb
If the outdoor air temperature is –10 °C, the evaporator surface will usually sit around –15 to –20 °C (because it must be colder than the air to absorb heat).
This matches what owners see during winter: coils often frost at –5 to –15 °C saturation.
Hitachi Yutaki units predict defrost requirements by a combination of:
1. Outdoor coil temperature sensor
2. Ambient outdoor temperature sensor
3. Refrigerant pressure sensor
4. Runtime / algorithmic prediction
Defrost begins when both the coil temp and calculated saturation temperature indicate that the coil is at or below freezing and the system sees an expected reduction in heat-extraction efficiency.
This means the unit will sometimes enter defrost before you see thick ice, because it's detecting the early film of frost that you can’t see.
Posted by: @iaackFor an air-source heat pump the minimum evaporating temperature depends on the compressor design and the manufacturer’s operating envelope.
Rule of thumb
Thank you for the reply. I think you are saying that what I am seeing is normal (Evaporator -23C. OAT -4C. Defrost cycle every 46 minutes).
2024 build bungalow
Southern england
179 m2
Underfloor heating
7KW heat pump
3.6KW solar panels
@trebor12345 Yes, expect defrost cycles to initiate at evaporator temperatures between -20 and -35 degC depending on refrigerant gas, plant design and application.
The cycle time is dependent more on environmental conditions, heat extraction rates (how hard the compressor is working) and forced airflow rates to the evaporator.
If you imagine a heat pump where the airflow to the evaporator is restricted in some way (caused by poor clearances between surrounding walls, evaporator fan not attaining the correct speed due to incorrect factory setup or maybe the early failure of the evaporator fan bearings) then the defrost cycle would still occur at the expected temperatures but the period between cycles would definitely decrease.
Referring now to your other post on this forum, the ice buildup on your unit does, in my experience, seem a little heavier than I would expect. Hopefully others will contradict me!
- 261 Online
By Deltona , 26 minutes ago
@benson I see, I misunderstood obviously. So you set LW...
By Tasos , 44 minutes ago
By JamesPa , 10 hours ago
By Bash , 11 hours ago
By Batpred , 12 hours ago
By cathodeRay , 12 hours ago
By DavidB , 15 hours ago
By Batpred , 15 hours ago
By Slartibartfast , 16 hours ago
By JamesPa , 17 hours ago
By Batpred , 17 hours ago
By Papahuhu , 19 hours ago
By Bash , 20 hours ago
By Odd_Lion , 20 hours ago
By F1p , 1 day ago
By RICHARDF5033 , 2 days ago
By Will H , 2 days ago