Ecodan help - flow temperature spikes when operating in weather compensation mode

19 Posts
4 Users
1 Reactions
1,120 Views
(@eleusis)
Active Member Member
Joined: 5 months ago
Posts: 7
Topic starter  

Hi there. 

Currently I have my heat pump set to WC mode. Fairly low temps (under 30 degrees) because heavily insulated airtight house. 1 zone with no rads. .only underfloor heating.

Now and again for some reason the flow temp spikes massively. I'm hoping to understand why it is doing this. Can anyone tell me what's going on?. Any help appreciated. Thanks

Screenshot 20241121 215840
Screenshot 20241122 180524
Screenshot 20241122 180550

 

This topic was modified 5 months ago 2 times by Eleusis
This topic was modified 5 months ago by Mars

   
Quote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2346
 

Is it spiking or is it gradually reaching the required FT following a defrost.  You can tell it is going into defrost mode (which is expected given current weather conditions) because FT<RT.

 

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
(@eleusis)
Active Member Member
Joined: 5 months ago
Posts: 7
Topic starter  

It doesn't say anything to do with defrost on the controller when it's spiking. Even if it was, would a defrost cycle really be that aggressive with flow temp? Energy usage spikes too for the times it spikes


   
ReplyQuote
(@eleusis)
Active Member Member
Joined: 5 months ago
Posts: 7
Topic starter  

Just realized the 2 of the screenshots above have set tank temp instead of actual tank temp. It looks like it is calling for heat sometimes when there is only a 1 or 2 degree drop in tank temp. Here is updated screenshot with actual tank temp. However I'm pretty sure the controller did not saying it was heating DHW during that(but I'm not 100% sure)

Screenshot 20241123 092316
This post was modified 5 months ago by Eleusis

   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2346
 

The peaks in your graph (which I presume are the 'spikes' you are referring to) appear to be at different FTs.  What is the set FT, what is the set FT for DHW and when is DHW heating scheduled for (or is it scheduled 'continuously' ie DHW priority).  Also whats the 'tank' - is it the DHW tank?  If so your most recent graph clearly shows the Tank temperature increasing when the spike occurs, which clearly indicates its heating DHW.  Is it possible that the system is set up to give priority to DHW with only a small hysteresis?

This post was modified 5 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@eleusis)
Active Member Member
Joined: 5 months ago
Posts: 7
Topic starter  

@jamespa thanks for your help. I think the problem was that the "DHW max operation time" was too low on the DHW settings. It was at 30 mins. I think during cold weather it was just taking too long so was having to try twice. This is why it only happened occasionally.


   
ReplyQuote



 Gary
(@gary)
Prominent Member Member
Joined: 2 years ago
Posts: 336
 

@eleusis The high flow temps are when it is heating your hot water, I set mine to run for 90 mins and I don't reheat during the day 210L tank is enough for 2 showers and a bath and general washing up.


   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 2 years ago
Posts: 482
 

Posted by: @eleusis

Hi there. 

Currently I have my heat pump set to WC mode. Fairly low temps (under 30 degrees) because heavily insulated airtight house. 1 zone with no rads. .only underfloor heating.

Now and again for some reason the flow temp spikes massively. I'm hoping to understand why it is doing this. Can anyone tell me what's going on?. Any help appreciated. Thanks

Screenshot 20241121 215840
Screenshot 20241122 180524
Screenshot 20241122 180550

 

hi @eleusis 

these graphs are all DHW cycles and nothing to do with WC mode.

and as @jamespa says you’re first graph with the split reheat shows signs of being in defrost during a DHW CYCLE.

A 30 minute DHW cycle is not a problem for an Ecodan. This has been stated by some people on this forum, as a problem and this is incorrect. it’s  just down to other settings like immersion intervention or at what temperature you set it to reheat. By that I mean if it reheats when the water is 40c it should reheat adequately to 50c in 30 minutes and that’s very efficient. See below. 

58E31225 7708 4FD8 89CE 1E1405A07517

 This is also dependent on what type of cylinder you have fitted, eg performance between different manufacturers or technologies, ie a plate heat exchanger or a coil heat exchanger.

However if all else is equal if you operate a DHW reheat when at 30c it might take closer to 45 minutes to get to 50c.

98CB76F8 AB36 47C5 8D58 6F0E5FDB1D62

However the key point in terms of efficiency and economy is - the longer your hp is operating at a flow temp of 55c or above the less efficient your hp will perform. And obviously the more frequent the DHW reheats are the less efficiently also.

I first proposed 30 minute reheats as a way of shortening the period that a HP is in high temperature mode and it works. But as we personally often let our DHW go down to 30c before a reheat we have now opted for a 43minute DHW reheat period with a touch screen actuation when we need it. IE it’s not scheduled. But that’s just our intermittent needs.

this last graph shows 30 minutes reheat when starting at 30c and it doesn’t quite reach 48c

87670B9E 7535 4C99 A3E1 7055A3FBF3CC

 

This post was modified 5 months ago by SUNandAIR

   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2346
 

Posted by: @sunandair

i first proposed 30 minute reheats as a way of shortening the period that a HP is in high temperature mode and it works. But as we often let our DHW go down to 30c before a reheat we have now opted for a 43minute DHW reheat period with a touch screen actuation when we need it. IE it’s not scheduled. But that’s just our intermittent needs.

Presumably it stops heating when the DHW reaches temperature, so if it only needs 30 mins then it will only take 30mins and then return to space heating at WC temperatures.  At least thats how I would expect it to work...but you never can be certain.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 2 years ago
Posts: 482
 

@jamespa yes, I think you’re right but it might be worth checking.  it can also be seen that the target temp  usually over runs by a few degrees, presumably because the HW is rising in the cylinder and finding it’s level.

We have a 250 L cylinder and know that when the mid tank temp reads 50c the upper thermistor is reading 56c. This is read from a thermistor which is not part of the Ecodan setup but is part of our solar thermal system. So it’s handy information.

This post was modified 5 months ago 2 times by SUNandAIR

   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 2 years ago
Posts: 482
 

@jamespa 

so I put the DHW on while the existing hw temperature was elevated. (To see how the HP would react when it reached DHW target temperature early in the cycle)

981D30C3 37F6 46DE BDA2 9ABE6DFA9BB4

Even though it has a pre-set (Max) duration of 43 minutes, it reached target temp in 32 minutes and switched itself into standby. ( the room temperature was 21c so it didn’t return to space heating) 

 So on the Ecodan system it would appear that the system reacts to the set duration as a maximum duration if the target cylinder temperature is reached early.

 

 


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2346
 

Posted by: @sunandair

@jamespa 

so I put the DHW on while the existing hw temperature was elevated. (To see how the HP would react when it reached DHW target temperature early in the cycle)

981D30C3 37F6 46DE BDA2 9ABE6DFA9BB4

Even though it has a pre-set (Max) duration of 43 minutes, it reached target temp in 32 minutes and switched itself into standby. ( the room temperature was 21c so it didn’t return to space heating) 

 So on the Ecodan system it would appear that the system reacts to the set duration as a maximum duration if the target cylinder temperature is reached early.

 

 

That's reassuring.  Hopefully it would have returned to space heating if there demand was there.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote



Page 1 / 2
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security