Ecodan flow rate tweak
Dear all,
I currently have the setup below.
- Zubadan PUHZ-SHW140 YHA (-BS) outdoor
- Ecodan ERST20C-VM2DR1.UK indoor
My dT is 10 around freezing temperatures, and I want to lower that by increasing the flow rate.
I adjusted the pump speed to 5 (maximum), but it doesn't give me a lot of flow. My outdoor unit supports a flow between 18 and 37 liters per minute, according to the specs. The max flow of my indoor unit is 27 liter per minute, but I only reach 21 liters per minute (probably piping, height resistance, etc). There is no button to control pump speed on the pump itself. The water pump is a Grundfos UMP3K 15-75-130.
I see that there are other indoor units (E*PT 20X series for example) that have the exact same water pump, but according to the specs of those units they have a max flow of 35 liters per minute. Besides, when I look up the specs of the water pump on the website of Grundfos, the max flow of my pump is much higher than the 27 liters (or even the 35) per minute.
I think the pump speed is restricted by the indoor unit, even when it is on speed 5. Unplugging the CNPWM doesn’t set the water pump on max performance either.
Does anyone have ideas how to increase the flow by speeding up the pump (which should be possible according to the specs of the water pump)?
1. Are all your radiator valves (both any thermostatic valves and the lockshield valves) fully open?
2. What diameter is your pipework to the radiators?
3. What size house?
Thanks for your reply.
Yes all radiators and floor heating is fully open. Pipes are 28mm or bigger. It is a 15kW heatpump used for both a big farmhouse and an apartment.
I think the 21 liter (out of the max 27) corresponds with the height resistance etc. I don’t think I can improve much on the piping and radiator sitution itself.
Therefore I am looking for alternative solutions to increase the flow.
Thanks for your reply.
Where did you find that table? The information in my installation manual is totally different (different flow rates, doesn’t say dT of 8 etc).
It mentions an additional pump. But what do they mean with that? Putting two pumps in series doesn’t result in extra flow, only in extra kPa.
@jingle86 Thats in the Ecodan ATW Databook Volume 6.0 https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_Vol.6_.0_.pdf#page-1.
No idea what they mean that's why I suggested calling the technical help line they are usually very helpful and its free.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 31 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 2 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 3 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I couldn't agree more. This is a case where you buy as...
By JamesPa , 12 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 1 day ago
-
Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ...
By immunity , 1 day ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
I have signed up as well. @belsnugg could you outline ...
By JamesPa , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 1 day ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 2 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 2 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 2 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 2 days ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 3 days ago
-
@drei When I was in local government we were of cours...
By JamesPa , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 4 days ago