Ecodan DHW Settings missing
What did you press to get to this screen, it doesn't look right at all, but try a long press of the menu button see if the screen looks any different.
If that doesn't work have you tried turning its on and back on again it does look like the screen isn't scaled correctly.
This screen was accessed by long pressing the menu button and selecting the first item 'DHW'.
I've power cycled the unit, reset the controller, reset the FTC, all to no avail.
I would suggest that you check the setting of DIP Switch SW1-3 which identifies the presence or absence of a DHW cylinder. If the setting of this DIP Switch indicates that a DHW cylinder has not been installed then the controller display is unlikely to show the parameters relating to DHW.
Also check the setting of SW3-7.
Hi Derek, that sounds promising. How exactly would I do that.
Gary, yes I think it is a tech issue, that's why I'm here...I live in an Overseas Territory and calling international support numbers is rather expensive unfortunately!
Posted by: @pingu807Hi Derek, that sounds promising. How exactly would I do that.
Gary, yes I think it is a tech issue, that's why I'm here...I live in an Overseas Territory and calling international support numbers is rather expensive unfortunately!
Look at section 4.3 Dip switch functions on page B-57 of the attached document.
Hi, thanks for your help.
It was all working properly only a few days ago and noone has touched any physical switches. Before I go opening it up, is it possible these switches could have moved themselves?
I have also lost both the temperature readouts for room temp and DHW temp on the 'home' screen now.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
2 weeks ago
-
British Gas Heat Pump Installation Complaint
2 weeks ago
-
Heating Turned Off but Radiators Still Warm
1 month ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
1 month ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
2 months ago
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 262 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
we are talking the same thing. Its crazy if its really...
By JamesPa , 8 minutes ago
-
RE: Electricity price predictions
I agree, the operation of a system managing hundreds of...
By Batpred , 8 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa Yes, the OAT sensor is situated on the back pa...
By Toodles , 9 minutes ago
-
RE: DHW heat loss through pumps.
Ah, you have a water circulation loop, (like in hotels)...
By JamesPa , 14 minutes ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
Just to clarify, returning water from UFH is colder tha...
By lukewarmbath , 23 minutes ago
-
RE: 10kw heat pump run in 24*7 data?
A different heat pump (Midea 14kW) but a stark reminder...
By cathodeRay , 31 minutes ago
-
From what I see, the work to upgrade the cable, etc all...
By Batpred , 54 minutes ago
-
RE: Confusion over Octopus Tariffs
That's sounds great. I have no ASHP, but 15kwh storage....
By Batpred , 2 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Locked environments are difficult to manage, it also me...
By Batpred , 2 hours ago
-
RE: Do Heat Pumps need to start up at Full Power?
@steelbadger Attached is the plot for various parameter...
By Toodles , 6 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Hi all, I had a 15kw installed 3 weeks ago. The past we...
By jamesh , 6 hours ago
-
Adia Therma - 'autopilot for heat pumps'
Thought I'd pop this one in here as the Adia proposal a...
By seatonian , 20 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Don't know answer to final question. Your contract p...
By JamesPa , 21 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Ah, it seems PACE BMS are easy to source on AliExpress,...
By Batpred , 21 hours ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
@jamespa Agreed I don't feel concerned about this, espe...
By jeegnesh , 23 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@toodles Yep, and it is not even a sticking plaster ...
By Jeff , 1 day ago
-
RE: Renewables & Heat Pumps in the News
I agree, imperfect systems like voting for politicians ...
By Batpred , 1 day ago
-
RE: Gov wants to alter our FIT contracts from rpi to cpi
The consultation is just part of the normal process for...
By Jeff , 1 day ago
-
@transparent @old_scientist Quick update, I submitted...
By Batpred , 2 days ago