Ecodan DHW Settings missing
What did you press to get to this screen, it doesn't look right at all, but try a long press of the menu button see if the screen looks any different.
If that doesn't work have you tried turning its on and back on again it does look like the screen isn't scaled correctly.
This screen was accessed by long pressing the menu button and selecting the first item 'DHW'.
I've power cycled the unit, reset the controller, reset the FTC, all to no avail.
I would suggest that you check the setting of DIP Switch SW1-3 which identifies the presence or absence of a DHW cylinder. If the setting of this DIP Switch indicates that a DHW cylinder has not been installed then the controller display is unlikely to show the parameters relating to DHW.
Also check the setting of SW3-7.
Hi Derek, that sounds promising. How exactly would I do that.
Gary, yes I think it is a tech issue, that's why I'm here...I live in an Overseas Territory and calling international support numbers is rather expensive unfortunately!
Posted by: @pingu807Hi Derek, that sounds promising. How exactly would I do that.
Gary, yes I think it is a tech issue, that's why I'm here...I live in an Overseas Territory and calling international support numbers is rather expensive unfortunately!
Look at section 4.3 Dip switch functions on page B-57 of the attached document.
Hi, thanks for your help.
It was all working properly only a few days ago and noone has touched any physical switches. Before I go opening it up, is it possible these switches could have moved themselves?
I have also lost both the temperature readouts for room temp and DHW temp on the 'home' screen now.
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
2 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
3 weeks ago
-
Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
4 weeks ago
-
Ecodan consuming 100kwh per day in new build!!!
3 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
6 months ago
- 26 Forums
- 2,197 Topics
- 48.4 K Posts
- 58 Online
- 5,854 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Large heat pump options for church building
Hi Mars thanks for the mention. Church projects are n...
By Aventus Eco , 18 minutes ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
Agreed. There’s tricky, and then there’s diving into a ...
By Mars , 23 minutes ago
-
RE: Why Air Release Valves and Deaerators are Non-Negotiable
I have one installed when my heat pump was done, connec...
By JamesPa , 30 minutes ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick fo you use ChatGPT? Could be worth a conv...
By Tim441 , 38 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
@dgclimatecontrol yes the wall fixings are mostly aroun...
By AdamK , 10 hours ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia, I hear you on the lagging and insulation front....
By Mars , 11 hours ago
-
@majordennisbloodnok And of course, ‘No deliveries betw...
By Toodles , 17 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold 😆 Toodles.
By Toodles , 19 hours ago
-
RE: Moving FIT array onto a Tesla Powerwall 3 possible?
@judith The PW3 can accept AC or DC inputs. Regards, To...
By Toodles , 19 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Its great to hear of your approach and success with the...
By JamesPa , 1 day ago
-
RE: Samsung Gen 6 - Schedules not working
@old_scientist Yes they are. Ive found a detailed discu...
By bontwoody , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
The logic currently changes the max flow temp setting v...
By Grantmethestrength , 2 days ago
-
RE: Which thermostat should I get (or do I need one?)
OK. It may be best to run it through the wint...
By JamesPa , 2 days ago
-
RE: Samsung 5kW R32 Monobloc Gen 6 ASHP
Hi @Nick Owens, welcome to the forum. My Sam...
By Old_Scientist , 2 days ago
-
Heat pump and wifi kit connection.
Currently trying to connect my Samsung MIM-B19N board t...
By Alfapat , 2 days ago
-
RE: Heat Pump + Tado Setup: Smarter Control for Secondary Pumps?
I suspect this is one for @pirate-rich
By Mars , 2 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Yuck, yuck and more! Others have pointed out lots alr...
By Judith , 2 days ago