Ecodan Compensation Curve Minimum Temp 25 Degrees
My Ecodan doesn't seem to allow me to set a compensation curve that will drop flow temp below 25 degrees celcius. In essence at 10 degrees outside I want all heating turned off with normal DHW function. Is my only option to turn off heating completely? I Assume I'm missing something; I can only find oblique reference to the 25 degree lower limit on the Web.
Any advice would be very much appreciated.
Well, generally a heating system is controlled by demand rather than another parameter. Even if you could lower the compensation curve further it would still be running – but I suspect it would become less efficient trying to put so little heat in.
However, in the controller settings you can find Service Menu > Operation Settings > Summer Mode, which is set to Off by default. But you have the options to set Heating On (4—19°, default 10°) and Heating Off (5—20°, default 15°) temperatures for ambient temps, and Heating On and Heating Off Judgement Times (both 1-48 hrs, default 6). These aren't explained anywhere, so perhaps a call to the Ecodan support line is in order, but I would presume that the temps are just setting on below/off above values with a hysteresis to allow it to run for a while and the judgments perhaps set a minimum time it has to be below temp before the heating is actually run, and a maximimum run time for while it is operating below the off ambient temp, after which it turns the heating off again until ambient drops below the on temp. Perhaps.
My summer mode is completely off via a schedule. Keep us informed if you try this option out!
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Thanks Harri. Interesting idea. I'll give it a go and let you know what happens.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
2 weeks ago
-
Ecodan consuming 100kwh per day in new build!!!
4 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
7 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
7 months ago
-
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
8 months ago
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 613 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa I would guess it's a deliberate choice due the...
By swwils , 20 minutes ago
-
Hello All Our solar system consisting of 2 x 6Kw inve...
By AlanB , 51 minutes ago
-
RE: BUS grant voucher expires before install date
@bornagain That is what our installer is pr...
By Bash , 1 hour ago
-
@sheriff-fatman Interesting because I am considering so...
By DavidAlgarve , 2 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
I'm not so sure. New gas boiler £10...
By Bash , 3 hours ago
-
RE: DHW heat loss through pumps.
I have a recirculation pump that we had fitted when the...
By Marzipan71 , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
I thought an aircon doubling as a heat pump could do ou...
By Batpred , 5 hours ago
-
British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
This week we brought together five of the biggest names...
By Mars , 5 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Just wanted to share some info for anyone facing challe...
By Batpred , 6 hours ago
-
Daikin Altherma HT Temperature Sensor Question - Caution: Mentions AI...
Hi All - first post for a while, hope you are all well,...
By Marzipan71 , 7 hours ago
-
RE: Do Heat Pumps need to start up at Full Power?
@steelbadger We have an LLH with secondary pump; the se...
By Toodles , 10 hours ago
-
RE: Electricity price predictions
We live in a democracy on a crowded island so everyone ...
By JamesPa , 10 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And the saga continues… So today a Senior Grant Engin...
By Crimson , 1 day ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa Yes, the OAT sensor is situated on the back pa...
By Toodles , 1 day ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
Just to clarify, returning water from UFH is colder tha...
By lukewarmbath , 1 day ago
-
RE: 10kw heat pump run in 24*7 data?
A different heat pump (Midea 14kW) but a stark reminder...
By cathodeRay , 1 day ago
-
From what I see, the work to upgrade the cable, etc all...
By Batpred , 1 day ago
-
RE: Confusion over Octopus Tariffs
That's sounds great. I have no ASHP, but 15kwh storage....
By Batpred , 1 day ago