Ecodan Cascade system conflicting views
Hi All
Great content and reading so far.
We have 2 x 14kw R32 single phase Ecodan's on their own phase with a 500l HW tank and a 500l buffer.
The house is 5200 square feet but 2/3 of it are double height ceilings. Its very well insulated as was completely modernised/extended 10 years ago and the guy really went to town on insulation - even the dry lining is insulated plasterboard. We have since the heat-loss calc changed 3/4 of the windows to triple glazed so improved still further from the 22mm double glazed units.
I have loads of questions but will start with this that had divided opinion:
Should the heating for the buffer tank be set to temperature compensation?
Currently its at 45 degrees with hot water priority (10 degree drop)
They only went live just before Christmas so quite early in ownership/experience
Thoughts?
Hi JPST21. delighted to see another Ecodan Cascade system on the RHH. I was beginning to think I was the only one! I have 2X 11.2KW R32s with Mitsi FTC controllers and the wireless room stat. Also switched on December 9th just before the temperature dropped and scared the pants off me watching the power meters spin.
Have you worked out how to get a COP figure out of this system? Mine says that the energy monitors are not installed?
Happy to compare notes.
Best regards
Tom
Hi Tom
We’re having the Wi-Fi link installed to be able to use the app rather than go to the plant room to make setting changes.
The energy usage parts are missing which may not be a bad thing although the new supply meter was at zero it’s now reading almost 1900 in 12 days. That did include the end of the cold snap and heating 1000 litres from 11 degrees.
There must be a way to see the usage v generation
The units were supplied as a kit but one terminal block was missing and support told the installers it could be done with the dip switches but this was incorrect and we lost 10 days waiting for the part!
It’s been a bit of a bumpy road so far to say the least
Jez
Hi Jez Very few on this forum seem to be bump free. The wireless kit is good though my software writer son was very rude about the limited functionality of the app interface. It certainly does allow one to control the setup remotely. Though I keep reading threads here that suggest that if we only get the weather compensation process right it will not need to be touched! I have not worked out how to do that yet.
Between December 10th startup and Monday January 2nd (23 days) my system consumed 1140 KWh. ( but in a much smaller house 281m2, heat loss estimate 16.5KW)
Posted by: @tommclHi Jez Very few on this forum seem to be bump free. The wireless kit is good though my software writer son was very rude about the limited functionality of the app interface. It certainly does allow one to control the setup remotely. Though I keep reading threads here that suggest that if we only get the weather compensation process right it will not need to be touched! I have not worked out how to do that yet.
Between December 10th startup and Monday January 2nd (23 days) my system consumed 1140 KWh. ( but in a much smaller house 281m2, heat loss estimate 16.5KW)
I have not looked in detail at a cascade system, since the necessity has only just arisen. I have attached a copy of the very comprehensive manual that Kev posted some time ago, it may throw some light of the subject.
There are also various YouTube videos giving details of how to set up and adjust the parameters for weather compensation. I think that many on the forum would be interested in details of what your son found.
- 26 Forums
- 2,151 Topics
- 47.2 K Posts
- 43 Online
- 5,666 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@transparent The only reason my DNO knows of these is b...
By Lucia , 47 seconds ago
-
RE: Rodents! A word of warning for heat pump owners
@tim441 I will need to give some thought to protect the...
By Lucia , 6 minutes ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
🙁🙁🙁🙁🙁
By Lucia , 14 minutes ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
@jamespa thank you. You may well be correct regarding t...
By pash44pump , 41 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 2 hours ago
-
RE: is a home battery without an EV worth it?
@jamespa having just had a heat pump installed I do won...
By AdamK , 11 hours ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 14 hours ago
-
RE: Electricity price predictions
Seems a lease to a 3rd party to place a battery inside ...
By Scalextrix , 15 hours ago
-
RE: Octopus tariffs - a quick comparison
Interesting comparison! Another good angle is the dif...
By HCas , 16 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@julianc Our solar PV has produced more this August tha...
By Toodles , 23 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 2 days ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@transparent that is a very interesting suggestion, tha...
By GrahamF , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Sorry to resurrect this thread, but it is sort of relev...
By cathodeRay , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I missed your 22nd June post on this. I am sure it can ...
By cathodeRay , 3 days ago
-
Now posting on the right topic.... With general build...
By benson , 3 days ago
-
RE: How to waste energy (and time) playing with AI.
I’m sure like many software toys that it is addictive! ...
By Judith , 3 days ago
-
RE: Does anyone have experience of a smart water meter?
@judith With Anglia Water it was a compulsory upgr...
By TechnoGeek , 4 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
We’re high energy users other than the ashp so the OVO ...
By Judith , 4 days ago
-
RE: Ecodan & MelCloud scheduling
Yes, the 2 are separate. To add to the complex desig...
By HCas , 6 days ago