Ecodan ASHP Low COP and Unstable Compressor Frequency
Hi all, I’m trying to understand why my Mitsubishi Ecodan system has such a low COP. The system was installed in 2017 when the house was built but is new to me since moving in a few months ago. It heats the house well, but reported efficiency is poor, and energy usage seems fairly high. Although it has been serviced in the past, I have found many issues including blocked filter, and faulty 3-way valve. I would greatly appreciate any input on whether the behaviour I am seeing is normal or if performance can be improved.
Heat Pump Model: PUHZ-W85VHA2-BS
Controller Model: FTC5 version 15.00
Tank: Ecodan 250l pre-plumed cylinder with low loss header
Emitters: UFH downstairs, Radiators upstairs
Thermostats - All thermostats, TRVs and valves open.
HW Setpoint: 47 degrees
House Type: Well insulated modern 3 bed house built in 2017 (design temps not known)
Pump Setup: 3x pumps (Primary loop to HP, Heating system pump on other side of LLH, DHW pump on other side of DHW heat exchanger.
What I’m Observing
• COP for heating is typically ~1.5-2, which seems low for 10°C outdoor temps.
• COP for hot water is (47°C setpoint, 250 L cylinder) is typically ~1.3, also lower than expected.
• Flow temperature constantly oscillates even with a stable target
• At low - medium load, compressor frequency cycles repeatedly between ~45 Hz and ~70 Hz, rather than settling at a stable low modulation.
• At high load the compressor will run at a stable frequency (70 - 90hz)
• No active error codes.
• Heating Flow rate (according to FTC controller):17l/m
• DHW flow rate: 14l/m
• Difference between return temp of UFH and Radiators: UFH return temp is approx 2-2.5 degrees less than RAD return temp.
What I’ve Tried So Far
• Cleaned the outdoor strainer (was blocked resulting in a flow rate of 6l/m)
• Flushed the system with central heating cleaner.
• Cleaned magnetic filter regularly
• Replaced the 3 way valve (which resolved leakage of hot water to radiators during DHW cycles)
• Verified flow through UFH loops via manifold flow gauges.
• Opened all radiators fully to increase system load - didn’t solve hunting.
• Adjusted radiator lockshield valves to attempt to balance radiators - didn’t resolve issue
• Reduced primary pump speed to discourage short-circuiting through the LLH - no real change observed
• Tested thermistors in outdoor unit are reporting accurately. As far as I could tell the measured resistance matched the expected values given in the Databook.
• Run the system for short periods in the morning (according to time of use tariff), and run the system for long periods (24 hrs +) to let things stabilise.
Running Examples:
I have been monitoring the system via the melcloud and melpump apps:
Medium load - (Outdoor temp 7-9 degrees)
- From 0520 - 0820 flow temp is below target temp (35 degrees) and compressor frequency is fairly stable while load is high and system aims for target.
- From 0820 - 1000 the flow temp seems to match the target temp. Flow (and delta t) stabilise and frequency appears to modulate down in steps.
- Rest of day. Compressor and flow temp fluctuating.
- Energy Use during this time (according to smart meter app): 35-40KWH (1.25 - 1KWH per hr)
- COP Heating: 2.41
- COP DHW: 1.11
Looking at a close up between 1600 and 1720
High Load - Outdoor temp ~-2
Observations
- Steady frequency of 92Hz
- Fairly steady increase in Flow and return temps, but Flow can be seen to fluctuate up and down despite constant compressor load.
What I’m Trying to Understand
• Is the constant hunting between 45–70 Hz, and fluctuating flow temp normal for this generation of Ecodan, or should I expect a steady low-frequency modulation.
• Could the unsteady patterns simply just be an issue with the unit not being able to modulate lower for the given flow/return/room temps, or is there potentially a deeper issue with the unit (e.g EEV, low refrigerant etc).
Any comments or advice would be greatly appreciated.
Thanks!
First things first, @lukewarmbath, and welcome to the forum.
I see this is your first post, so let's see what we can do to help. I also have an Ecodan 8.5 kW so, whilst mine is an R32 model, we should be able to compare and contrast pretty reasonably. I am not one of the best here to talk about heat pump config but there are a few pertinent questions I can ask that should open things up for my more able peers here to comment on.
Given how long the system has been installed, your indoor display should be able to give you plenty of historical data. Have you taken a look yet at how much energy was consumed last year/this year and how much heat energy delivered for same period? I only ask because my heat pump is registering a COP right now of 5.11 whilst a minute ago it was 1.96. Mitsi's reporting of COP is nothing if not variable, so a far better indicator of whether there's a real problem or not is the last year's SCOP. Of course, if the 1.5-2 COP you mentioned actually is the SCOP, that's definitely low.
You haven't mentioned whereabouts in the country you are. A general idea of location might help with recommending a company for servicing that is likely to pick up on the things that seem to have been missed.
You also haven't mentioned whether the system is running in weather compensation mode or flow temperature mode. That is highly likely to affect the heat pump's performance so well worth letting us know a few more details.
I would also say that you seem to have a feeling that something isn't right. That is an important point and something you should only relinquish if we manage to satisfy your concerns objectively. You're getting to know your system far better than we ever could so your instincts are valuable.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Thanks for the reply and the welcome !
Located in Inverness (Scotland)
Heatpump has been running in weather compensation mode for the last couple months. Currently at Flow=32@15 outdoor and Flow= 42@-15.
Regarding historical data unfortunately the energy consumption and production data seems to have been reset before I moved in to the property. I think this might have been done during a service. I do have data for the past few months though.
Daily Breakdown (Total Consumed KWH, CoP Heating, CoP DHW) for October
Daily Breakdown (Total Consumed KWH, CoP Heating, CoP DHW) for November. Note: data reading between 2nd Nov and 9th Nov is incorrect as I mistakenly adjusted the return thermistor (THW2) reading resulting in lower than actual reported COP figures. All thermistor offsets are now at 0.)
CoP Heating and Energy Consumed for Heating only by Month
- October Heating COP=2.18 for 309 KWH consumed
- November Heating COP = 1.47 for 201 KWH consumed. (actual values likely higher due to mistake mentioned above)
Let me know if there is any other info I can provide to give a better idea.
that ASHP is working, from the looks of it, way too hard all day. I know you know this, but something is not right. where is the heat going?
yup, it is definitely over working. You can hear the compressor running hard continuously when getting up to temperature after a stop or setback, then repeatedly ramping up and down once up to temperature. Both of these behaviors can be seen in the original screenshots.
Ultimately it results in the house overheating to the point where I have to shut it off completely overnight. - I have mostly been running it in the morning and afternoon according to my off-peak rates to avoid over heating.
I actually had some luck running it in Auto adapt mode yesterday for the first time since the summer. Although it was still running hard, it did seem to start modulating slightly before shutting off when room temp was met.
As I have read in other threads that older ecodans have trouble modulating at lower flow temps or low outside temps, I tried cranking the curve up back in weather compensation mode but behavior returned to normal (ramping up and down rather than modulating to a lower frequency)
I am probably going to explore using Auto-adapt for now to see if that helps.
My main question at the moment is, should the flow temperature fluctuate so much? Even with a stable compressor frequency, the flow temp fluctuates up and down by 3.5 degrees or more every 10 minutes. This seems to happen regardless of load and temperatures so maybe it is just normal behavior but seems a bit strange to me.
Here is my last 24hrs, its very stable and steady. its likely complex why yours is doing what it's doing and without knowing the set up, will he hard to get to the bottom of it. Those are quite high temps for UFH. Even when its stable, the compressor is running at 90 odd Hz, that is working very hard. the graphs look odd to me. you probably need someone to see how it's all piped and working. are you running zones? are things coming on and off all the time?
Thanks for the graph. That's really useful!
Agreed, these temps are too high but behavior is similarly chaotic at lower flow temps. First screenshot in thread was for 35 degree flow at ~5-10 OAT and behavior is similar. I will reduce further and get further screenshots.
UFH and RADs are running on a single zone. Piping is as shown below, with only difference being that the RADS and UFH simply split at a T junction to divert the water to each. Only flow control for the RADs is the Lockshield valves. Each UFH loop can be individually throttled - all are full open besides one short loop that is throttled to reduce return temp slightly. They are approx 1.5 - 2.5l/min. All room thermostats are fully open and set so high they will never close. All radiators warm fairly evenly.
At this point I have tried everything including balancing the system, running pumps at different speeds to prevent recirculation through low loss header and also adjusting flow temps. Although I see some minor differences, I think the problem goes beyond simply having an unbalanced system. I feel there is something wrong with the outdoor unit resulting in these unhinged flow temperatures.
Things I have considered are issues with the linear expansion valve, refrigerant or sensors in the system, but I am not getting any errors on the controller.
Don't know the house heat loss unfortunately.
Downstairs UFH: 5 loops (downstairs dimensions approx size 8m x 9m)
Upstairs Radiators: 6 total
- 2x 600x600mm
- 3x 600x1000mm
- 1x 600x1300mm
its a little odd that your UFH comes back warmer than the rads. normally the other way around. if they are all fully open, the water might be travelling too fast to give out much heat. I'm very weary about getting people to tinker with their systems as I'm not qualified and no idea of your full set up. But have you tried closing the valves to the flows a bit to slow the water down in the UFH. whats the area of your house. is it well insulated? you got an 8.5kw? sounds quite big for your emitters.
Just to clarify, returning water from UFH is colder than returning water from radiators. Just checked with a infrared thermometer and approximate temps were:
Flow temp to emitters: 31.5
Return Temp from UFH: 24.8
Return Temp from Rads: 28
Combined return Temp: 27
Would need to measure properly but its a fairly large 3 bed with approximate size downstairs is 8x9m. So say 140m2 total? Seems well insulated modern house: cavity timber frame construction with a rendered block outer leaf.
Its definitely possible the unit is oversized. But at the same time, the return temps look to me to be coming back stable and reasonable. Delta T seems to be in the right ballpark and flow rate is decent. So I just can't understand how the system can be performing so badly.
I will play about a bit over the next few days and see if throttling the RADs or UFH has any effect.
Edit to add - Not sure if this is important but I have never seen the compressor fully cycle when running - as in fall to 0hz and re-start.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 536 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 36 minutes ago
-
RE: What determines the SOC of a battery?
Thanks. It is not clear how @bash concluded the chargin...
By Batpred , 45 minutes ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
I've been using this heatpump for two winters now and a...
By GoodbyeGas , 2 hours ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
That would make sense. I've found the effects are prett...
By Majordennisbloodnok , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 3 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 4 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 15 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 17 hours ago
-
RE: Setback savings - fact or fiction?
I also need to correct something I said by mistake earl...
By cathodeRay , 17 hours ago
-
RE: Electricity price predictions
@judith Thanks for sharing, and nice to see how the ...
By Batpred , 18 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 20 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 20 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 21 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 22 hours ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 22 hours ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 24 hours ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I don't know about Solis inverters. It isn't a featur...
By Transparent , 2 days ago