Ecodan ASHP Low COP and Unstable Compressor Frequency
Hi all, I’m trying to understand why my Mitsubishi Ecodan system has such a low COP. The system was installed in 2017 when the house was built but is new to me since moving in a few months ago. It heats the house well, but reported efficiency is poor, and energy usage seems fairly high. Although it has been serviced in the past, I have found many issues including blocked filter, and faulty 3-way valve. I would greatly appreciate any input on whether the behaviour I am seeing is normal or if performance can be improved.
Heat Pump Model: PUHZ-W85VHA2-BS
Controller Model: FTC5 version 15.00
Tank: Ecodan 250l pre-plumed cylinder with low loss header
Emitters: UFH downstairs, Radiators upstairs
Thermostats - All thermostats, TRVs and valves open.
HW Setpoint: 47 degrees
House Type: Well insulated modern 3 bed house built in 2017 (design temps not known)
Pump Setup: 3x pumps (Primary loop to HP, Heating system pump on other side of LLH, DHW pump on other side of DHW heat exchanger.
What I’m Observing
• COP for heating is typically ~1.5-2, which seems low for 10°C outdoor temps.
• COP for hot water is (47°C setpoint, 250 L cylinder) is typically ~1.3, also lower than expected.
• Flow temperature constantly oscillates even with a stable target
• At low - medium load, compressor frequency cycles repeatedly between ~45 Hz and ~70 Hz, rather than settling at a stable low modulation.
• At high load the compressor will run at a stable frequency (70 - 90hz)
• No active error codes.
• Heating Flow rate (according to FTC controller):17l/m
• DHW flow rate: 14l/m
• Difference between return temp of UFH and Radiators: UFH return temp is approx 2-2.5 degrees less than RAD return temp.
What I’ve Tried So Far
• Cleaned the outdoor strainer (was blocked resulting in a flow rate of 6l/m)
• Flushed the system with central heating cleaner.
• Cleaned magnetic filter regularly
• Replaced the 3 way valve (which resolved leakage of hot water to radiators during DHW cycles)
• Verified flow through UFH loops via manifold flow gauges.
• Opened all radiators fully to increase system load - didn’t solve hunting.
• Adjusted radiator lockshield valves to attempt to balance radiators - didn’t resolve issue
• Reduced primary pump speed to discourage short-circuiting through the LLH - no real change observed
• Tested thermistors in outdoor unit are reporting accurately. As far as I could tell the measured resistance matched the expected values given in the Databook.
• Run the system for short periods in the morning (according to time of use tariff), and run the system for long periods (24 hrs +) to let things stabilise.
Running Examples:
I have been monitoring the system via the melcloud and melpump apps:
Medium load - (Outdoor temp 7-9 degrees)
- From 0520 - 0820 flow temp is below target temp (35 degrees) and compressor frequency is fairly stable while load is high and system aims for target.
- From 0820 - 1000 the flow temp seems to match the target temp. Flow (and delta t) stabilise and frequency appears to modulate down in steps.
- Rest of day. Compressor and flow temp fluctuating.
- Energy Use during this time (according to smart meter app): 35-40KWH (1.25 - 1KWH per hr)
- COP Heating: 2.41
- COP DHW: 1.11
Looking at a close up between 1600 and 1720
High Load - Outdoor temp ~-2
Observations
- Steady frequency of 92Hz
- Fairly steady increase in Flow and return temps, but Flow can be seen to fluctuate up and down despite constant compressor load.
What I’m Trying to Understand
• Is the constant hunting between 45–70 Hz, and fluctuating flow temp normal for this generation of Ecodan, or should I expect a steady low-frequency modulation.
• Could the unsteady patterns simply just be an issue with the unit not being able to modulate lower for the given flow/return/room temps, or is there potentially a deeper issue with the unit (e.g EEV, low refrigerant etc).
Any comments or advice would be greatly appreciated.
Thanks!
First things first, @lukewarmbath, and welcome to the forum.
I see this is your first post, so let's see what we can do to help. I also have an Ecodan 8.5 kW so, whilst mine is an R32 model, we should be able to compare and contrast pretty reasonably. I am not one of the best here to talk about heat pump config but there are a few pertinent questions I can ask that should open things up for my more able peers here to comment on.
Given how long the system has been installed, your indoor display should be able to give you plenty of historical data. Have you taken a look yet at how much energy was consumed last year/this year and how much heat energy delivered for same period? I only ask because my heat pump is registering a COP right now of 5.11 whilst a minute ago it was 1.96. Mitsi's reporting of COP is nothing if not variable, so a far better indicator of whether there's a real problem or not is the last year's SCOP. Of course, if the 1.5-2 COP you mentioned actually is the SCOP, that's definitely low.
You haven't mentioned whereabouts in the country you are. A general idea of location might help with recommending a company for servicing that is likely to pick up on the things that seem to have been missed.
You also haven't mentioned whether the system is running in weather compensation mode or flow temperature mode. That is highly likely to affect the heat pump's performance so well worth letting us know a few more details.
I would also say that you seem to have a feeling that something isn't right. That is an important point and something you should only relinquish if we manage to satisfy your concerns objectively. You're getting to know your system far better than we ever could so your instincts are valuable.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Currently viewing this topic 1 user ( lukewarmbath ) and 8 guests.
Recently viewed by users: Morgan 13 minutes ago, ASHP-BOBBA 55 minutes ago, JamesPa 42 minutes ago, Majordennisbloodnok 32 seconds ago.
- 26 Forums
- 2,283 Topics
- 51.1 K Posts
- 244 Online
- 5,944 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Renewables & Heat Pumps in the News
Always keep a boiler replacement quote open, "just in c...
By Batpred , 24 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Sorry, only just seen this I don't know why. I was spe...
By AndrewJ , 30 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@majordennisbloodnok colourful post coming soon, probab...
By Mars , 33 minutes ago
-
RE: Confusion over Octopus Tariffs
@agentgeorge I can’t recall when and the details but Co...
By Toodles , 44 minutes ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
First things first, @lukewarmbath, and welcome to the f...
By Majordennisbloodnok , 56 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
I can't get any of those URLs to work...... even if I r...
By Transparent , 1 hour ago
-
RE: Who's your electricity provider and what's your tariff?
@technogeek Yep, the same here. Toodles.
By Toodles , 2 hours ago
-
RE: Maximising Home Automation: Integrating Octopus Energy & More
Thank you and I agree most people can stay clear of net...
By Batpred , 3 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@jamespa Yes that post.
By dgclimatecontrol , 3 hours ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey glad you got it sorted and agreed- being ig...
By benson , 4 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
50l LLH install would have introduced a shedload more a...
By JamesPa , 6 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@agentgeorge it has got 2, the other bleed screw is the...
By AdamK , 16 hours ago
-
I too felt the podcast was useful but think it could do...
By AndrewJ , 20 hours ago
-
@adamk apologies but did not understand what exactly yo...
By Eliuccio , 20 hours ago
-
Putting a 30 cm. radio controlled wall clock on Freegle...
By Toodles , 21 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@nickhorne Unfortunately not. We take the "normal" IOG ...
By HCas , 2 days ago
-
RE: Mixture of copper and plastic CH pipework. Will it be ok, or need changing?
In principle yes. Some heat pumps (I think including D...
By JamesPa , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Some of the circuits in my home are not protected by RC...
By Batpred , 2 days ago