Check the thermistor readings as detailed in the attached video.
If the controller is indicating -39C then check to see if the controller is correctly configured. Also check to see if the thermistor is wired to the correct connection.
@ngillam now you have access to the app at the bottom of the screen is a reports tab then press hourly temperature it will display the flow and return temps for the most recent hour. At the top of the screen will be the time press that and you can select any hour in the last 24 hours so you can see exactly when the heat pump was on and what temp it was running at.
As your system is running off 3rd party thermostats that -39C reading won’t matter it’s the temperature near to the controller unit.
Hello Gary,
Still struggling with this, seems we can't get the house cool enough, won't go below 22degs, if I alter the WC curve to its lowest temp (20degs) then I suffer cycling which I've seen on other threads. It seems the house is really well insulated and we're just not losing the heat, the other half is getting a bit annoyed at the high temps.
Any suggestions?
Thanks,
Neil
At this time of year you will need to use your thermostats to limit overheating. Are they heatmiser as well? Now you have set the warm end of the curve you can set the thermostats to the max temp you want then the heat pump should shut off unless you have multiple zones in the UFH linked to numerous thermostats?
@gary This is my set up, I thought the idea was to let the heatmisers (in each room) run free? Mine are at 35 degs but sit at about 22 degs. my partner wants to open windows to cool the place off but that seems wasteful. All underfloor heating is hard to control.
If you can’t control the house temp through the flow temps you will have to have thermostats to stop the house getting hotter than required.
@gary By flow temps you mean those set via WC curve? Just had a thought, all the trickle vents are closed on the windows!!
I think you said your set up was similar to mine Gary, can I ask your KWH for Oct? heating and DH combined?
Thanks,
Neil.
Yes the flow temps in the WC curve you are running as cool as possible but that is still overheating the house so all you can do is turn it off when the house gets hot enough.
I don’t measure the heat pump consumption separately but I estimate it about 10kwh a day for water and heating in October. This is all done overnight at cheap rate the house doesn’t cool down enough during the day for the heating to come back on again.
Posted by: @ngillamall the trickle vents are closed on the windows!!
Not the best option for ventilation! You will end up with a house that hot and stuffy, the stuffy feeling isn't because it's hot, its rubbish air quality, humidity and high CO2 levels
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 54 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Is that heat loss, or maximum output of the ASHP? Unde...
By Scalextrix , 16 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan Fully agree with you. It shouldn't be the homeo...
By HCas , 17 hours ago
-
RE: Solar Thermal DHW and ASHP
@judith That makes sense to me! If I was in @alex_n '...
By HCas , 18 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
Good unit. And the 10 kW is the same as the 12 kW I ...
By HCas , 18 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 21 hours ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 23 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 1 day ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 2 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 2 days ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 2 days ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 3 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 4 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 4 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 4 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 4 days ago