Ecodan 11.2kva Controller location?
Hi All
We've got an Ecodan 11.2kva and the installers have located the integrated internal unit in the garage and then we are connected to the house with a domestic distribution pipe (big insulated send/return for HW/Heating). We've got Hive running in the house (1 as the house thermostat and 1 as underfloor/pump controller in an extension). We are not always getting heat to the house, when the Hive thermostats are calling for it. My suspicion is that the controller on the integrated unit (set to 21oC) in the garage, is reaching its temp and so when the hive thermostats call for heat from the house, it is not calling heat. I've spoken to the installer a couple of times and they are not sure, but would a simple solution to move the ecodan controller to the house (instead of with the integrated boiler unit in the garage)? We have a cable conduit that we could use, but would appreciate any thoughts/ideas before I go back to the installers.
Thanks in advance
Archibold
The Mitsubishi main controller will be where the system is reading the room temperature unless you are using the Mitsubishi wireless room controller which then is set to supersede the hard wired one and it will read the temperature of where ever it is sited.
Hive may be a problem as it is an on/off thermostat and the Mitsubishi wireless controller in auto adaptive mode is much more sophisticated. There are others here more knowledgeable than I who will surely comment.
The main controller or the wireless room controller needs to be in the house so it can read the temperature. The hive needs to be set a couple of degrees above the desired temperature so it acts as a limiter only and basically leaves the control to the heat pump. Weather compensation needs to be set up correctly, trvs if any on the majority of the emitters set above the desired temperature so they act only as limiters. The radiators or ufh loops if there are more than one need to be balanced . Your installer should have done all of this.
Basically, for efficient and effective operation, the heat pump controller needs to control the heat pump, not external controls.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks, appreciated. I don't think it has been done correctly (e.g. the controller is in the garage and not the house, but easy to move - they had to do quite a bit of re-work on piping etc). Pondering whether to replace the Hive with the Mitsubishi remote controller, so it is all on the same platform/system (it doesn't need to be hive).
I think the installer is out of their depth as reading between the lines they have only done it before where the system is in the house and there was quite a bit of staff turnover during the installation/commissioning. Also different staff came for different parts of the job (radiators versus ASHP) and I don't think they were talking to each other. To be fair, I'd assumed that they were project managing things, but in hindsight I should have checked that or got our builder involved.
As far as I can tell the system is not running on weather compensation, so won't be as efficient as it could be. It's all a learning curve! I need to figure out whether to go back to the installer, or find someone else to come and review (I'm assuming Mitsubishi won't be much help, but I haven't tried that route). Thoughts apprecaited!
Did you have Hive before the heatpump that was connected to a boiler, when the heat pump was installed the existing controls should have been connected to the heatpump.
Your Hive's should be telling the heat pump when to turn on and off as you are not using the Ecodan main controller as the thermostat as its not in the house.
That's what it sounds like from your description.
Yes you could move the controller inside the house and use it as a thermostat but then you don't need the Hive's or just connect the Hive's to the Ecodan.
What is the house Hive connected to if its not connected to a heat source?
Posted by: @garyYour Hive's should be telling the heat pump when to turn on and off as you are not using the Ecodan main controller as the thermostat as its not in the house.
It really shouldn't!
Posted by: @garyYes you could move the controller inside the house and use it as a thermostat but then you don't need the Hive's.
And you really should!
Most heat pumps should be controlled in most situations by their native controller. The use of external controls other than as temperature limiters (but definitely not temperature controllers) is pretty much certain to reduce efficiency.
Posted by: @abernyteMitsubishi wireless controller in auto adaptive mode is much more sophisticated.
Indeed, and designed specifically to control a heat pump, with its particular characteristics, not a boiler which has very different characteristics.
Using the heat pumps native controller with properly adjusted weather compensation will ensure that the heat pump is on for long periods operating at a flow temperature which is as low as it can be to deliver the energy required to the house. This massively improves efficiency (and comfort!). This is fundamental to the thermodynamics of how they operate which is very different to a boiler. Using an external thermostat/temperature controller will do the opposite. There is possibly a place for simple external controls, but not as the main temperature controller. The exception to this general statement is Homely, which is specifically designed to optimise some heat pumps. Whether Homely can do better than the sophisticated controller built into the Ecodan is an open question at present. Quite probably not unless you use the tariff optimisation/look ahead functions which I believe require a subscription
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks, really appreciate the response!
So sounds like I need to move the controller inside (or get a wirless one and pair) and remove the hive, as a first step!
Follow-on question is that the kitchen diner has under-floor with a pump and was using a secondary hive thermostat to control. Presumably I still need something that opens the manifold there and activates the pump? It is not set-up as a secondary zone from the ASHP as that would have required a second distribution pipe from garage to house - IIRC, and it isn't that large a property.
Sorry for the silly questions, I'm learning as we go along here.
Thanks!
Archibold
The OP's issue is that the house is not being heated when the Hive's are calling for heat this is because they are not wired into the Ecodan, to resolve this they should be.
I never said it should be used as a temperature controller or a limiter or anything other than to resolve the issue of the Hive's calling for heat and not activating the heat pump.
I said you could move the main controller into the house but in 2 of the 3 heating modes (fixed flow temp and WC) it will only work the same as the Hive will as a temperature limiter.
If you want to use autoadapt mode then you would need the main controller in the house but we are now into too much detail for the OP's original issue.
The first time people post with an issue who are unfamiliar with how heat pumps function, they want a response they can understand, I was merely trying to keep the answer simple.
Posted by: @garyThe OP's issue is that the house is not being heated when the Hive's are calling for heat this is because they are not wired into the Ecodan, to resolve this they should be.
I never said it should be used as a temperature controller or a limiter or anything other than to resolve the issue of the Hive's calling for heat and not activating the heat pump.
I said you could move the main controller into the house but in 2 of the 3 heating modes (fixed flow temp and WC) it will only work the same as the Hive will as a temperature limiter.
If you want to use autoadapt mode then you would need the main controller in the house but we are now into too much detail for the OP's original issue.
The first time people post with an issue who are unfamiliar with how heat pumps function, they want a response they can understand, I was merely trying to keep the answer simple.
I do agree with your final sentence! However...
If, as you say, the Hive isn't wired to the controller (do we actually know that?), and assuming that the heat pump switches on at least sometimes, then just wiring it in is unlikely to help so far as I can see. Currently the presumption, based on the behaviour, is that the heat pump is set up to respond to its own controller (which is in the wrong place). This means that (if the hive is disconnected) it is effectively behaving as if the Hive were permanently calling for heat (otherwise it would never switch on), and deciding what to do based on its own measurements. If you wire the hive in, the behaviour unlikely to change unless the heat pump autodetects the third party on/off signal and uses this to override its own controller, or you also change some other setting on the heat pump to tell it to ignore its own controller and respond only to the hive.
If the hive is in fact connected then the explanation is exactly as suggested by OP, but obviously wiring it in has already been done.
Either way I cant see how 'wiring the hive in' can alone fix the problem.
So to my way of thinking we need to go back to basics and set the heat pump up as its makers intended. In many ways that's simpler to understand, ditch the hive and use the ecodan controller but relocated to the correct place! Furthermore its what OP actually themselves suggested, which tends to imply that they understand it!
In short, and unless I have missed something, the simple answer to the question posed by OP is 'yes'.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks both, really appreciate the responses and attempts to explain!
I wouldn't go as far as saying I really understand, more likely proving that a little knowledge is dangerous again 🙂 Trying to improve as we go (like a lot of folks, including a lot of the installers it seems!)
Thanks again,
Archibold
Posted by: @jamespaIf you wire the hive in, the behaviour unlikely to change unless the heat pump autodetects the third party on/off signal and uses this to override its own controller, or you also change some other setting on the heat pump to tell it to ignore its own controller and respond only to the hive.
Exactly my point, once wired in to the FTC and appropriate dip switches changed the Ecodan will ignore the main controller and use the Hive to call for heat.
Currently, we have no idea to what if anything the hive is connected to.
Alternatively, as we have both said move the main controller into the house.
Like most things there is more than one way to solve the problem
Posted by: @garyPosted by: @jamespaIf you wire the hive in, the behaviour unlikely to change unless the heat pump autodetects the third party on/off signal and uses this to override its own controller, or you also change some other setting on the heat pump to tell it to ignore its own controller and respond only to the hive.
Exactly my point, once wired in to the FTC and appropriate dip switches changed the Ecodan will ignore the main controller and use the Hive to call for heat.
Currently, we have no idea to what if anything the hive is connected to.
Alternatively, as we have both said move the main controller into the house.
Like most things there is more than one way to solve the problem
Understood
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 381 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Finally, good news on my EPC assessment. Having got (...
By Mike Patrick , 8 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
My apologies @jamespa - I read what you'd posted here ...
By Transparent , 30 minutes ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Evening folks, Just wanted to provide an update after...
By Green_Fox , 40 minutes ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 1 hour ago
-
RE: Running from backup generaor in powercut?
@majordennisbloodnok Back in the 80’ or 90’ we had a te...
By Toodles , 1 hour ago
-
RE: Setback savings - fact or fiction?
Just as an aside, I notice your graph has come from Hom...
By Majordennisbloodnok , 2 hours ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 3 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 3 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 4 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 9 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 1 day ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-