E121 error code on Samsung 12kw gen 6
Hi Craig,
First of all you will be using more electrical energy, since it is now colder outside. You should also be aware that electrical energy use by a heat pump is not linear with change in outside air temperature, but increases exponentially as the outside air temperature reduces. How much energy did you use?
I am assuming that the heat pump is no longer switching off for only 20 seconds?
One further interesting point is that the 'Inverter Pump' reading is now showing as 25%, which if you had a PWM controlled pump would mean that it would be running much slower. Don't change anything at the moment, but later it may be possible to try the pump on a slower speed setting.
What I don't understand is that the descriptions on the 'Master Indoor Zone Information' screen refer to an 'Indoor Unit', which you don't have in your system. I suppose it could just be that Samsung forgot to change the text in the software for the Monobloc heat pump.
Keep carrying out your tests, which I feel certain both you and others will find of use. One important thing to remember is that no two days are exactly the same, so making like for like comparisons may not always be possible.
@derek-m I had also noticed the reduction in pump speed. It also dropped to 45 when we turned of WC a few days ago.
What KW we were using is a little irrelevant as we didn't have the heating on much and it was much milder at over 10 degrees. We were using as little as 8.6 up to 15kw. Now yesterday was 20 but the outside temp has dropped again and we are on 3.6 outside temp.
The indoor unit bit threw me off aswell. I assumed it was something to do with the box on the front of the UVC.
Yes, we are no longer short cycling. Hooray. Just trying to get it to run as efficiently as possible now. I'll see tomorrow if the 2091, 2 and 3 at #3 is better or worse.
One of the difficulties I have is that we were on LPG before and on auto fill so had no real idea how much we used. We also rarely ran the boiler apart from a few hours a day when it got cold. So I've no comparison for electric Vs previous gas use.
@derek-m I've just read this article on this site
In your situation the simple answer is no.
Because your controller is showing a value of 0.0 at the moment, this indicates that your controller is solely in WC mode, and takes no account of the indoor air temperature. The thermostats can switch the heat pump on and off, but the controller will only vary the LWT dependent upon the outside air temperature.
I'm back now and having checked the energy use it seemed to run for longer and use more energy on #3 on all three settings although this could be down to outside temps as you said. I've put all three back to #2
I'm not sure if 2093 remote controller, room temp control should be the same as the others but that's what I've done so far.
@craig1980 it’s been two years since you posted on this topic. Curious to know what happened.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 530 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
@grahamf It was due to the clearances, would have prefe...
By Renewables345 , 23 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 2 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Hi @bobflux thanks for pointing out the difference in t...
By DaveC , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 3 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 5 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 6 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 7 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 13 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 20 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 23 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 24 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago