E121 error code on Samsung 12kw gen 6
Hi Craig,
First of all you will be using more electrical energy, since it is now colder outside. You should also be aware that electrical energy use by a heat pump is not linear with change in outside air temperature, but increases exponentially as the outside air temperature reduces. How much energy did you use?
I am assuming that the heat pump is no longer switching off for only 20 seconds?
One further interesting point is that the 'Inverter Pump' reading is now showing as 25%, which if you had a PWM controlled pump would mean that it would be running much slower. Don't change anything at the moment, but later it may be possible to try the pump on a slower speed setting.
What I don't understand is that the descriptions on the 'Master Indoor Zone Information' screen refer to an 'Indoor Unit', which you don't have in your system. I suppose it could just be that Samsung forgot to change the text in the software for the Monobloc heat pump.
Keep carrying out your tests, which I feel certain both you and others will find of use. One important thing to remember is that no two days are exactly the same, so making like for like comparisons may not always be possible.
@derek-m I had also noticed the reduction in pump speed. It also dropped to 45 when we turned of WC a few days ago.
What KW we were using is a little irrelevant as we didn't have the heating on much and it was much milder at over 10 degrees. We were using as little as 8.6 up to 15kw. Now yesterday was 20 but the outside temp has dropped again and we are on 3.6 outside temp.
The indoor unit bit threw me off aswell. I assumed it was something to do with the box on the front of the UVC.
Yes, we are no longer short cycling. Hooray. Just trying to get it to run as efficiently as possible now. I'll see tomorrow if the 2091, 2 and 3 at #3 is better or worse.
One of the difficulties I have is that we were on LPG before and on auto fill so had no real idea how much we used. We also rarely ran the boiler apart from a few hours a day when it got cold. So I've no comparison for electric Vs previous gas use.
@derek-m I've just read this article on this site
In your situation the simple answer is no.
Because your controller is showing a value of 0.0 at the moment, this indicates that your controller is solely in WC mode, and takes no account of the indoor air temperature. The thermostats can switch the heat pump on and off, but the controller will only vary the LWT dependent upon the outside air temperature.
I'm back now and having checked the energy use it seemed to run for longer and use more energy on #3 on all three settings although this could be down to outside temps as you said. I've put all three back to #2
I'm not sure if 2093 remote controller, room temp control should be the same as the others but that's what I've done so far.
@craig1980 it’s been two years since you posted on this topic. Curious to know what happened.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 69 Online
- 4,531 Members
Podcast Picks
Latest Posts
-
New Vaillant aroTherm Plus in black - When will it come to the UK?
It looks like Vaillant are updating the aroTherm plus l...
By Sandy , 1 hour ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 2 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Ive called most of them over the years. By far the best...
By dgclimatecontrol , 2 hours ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
I've certainly seen that on their Ts & Cs page but ...
By Majordennisbloodnok , 1 day ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 1 day ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 day ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 2 days ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 2 days ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 3 days ago
-
@ecobaker May I ask a question of you please. I too hav...
By Papahuhu , 3 days ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 3 days ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 6 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 6 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 6 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 6 days ago