Do I have a bad install and what can I do to improve it?
Hi all
We finished our house last year and were so glad to be in we just let the heating system be however it did seem expensive to run.
The system installed is a Mitsubishi EcoDan 8.5 (PUZ-WM85VAA) this is connected to the pre plumbed 210L tank (EHPT21X-UKHDW) The house is only UFH. The downstairs is in screed upstairs is tiled in bathroom and low tog / underlay carpet in bedrooms. after seeing the HeatGeek YouTube channel and finding this forum more things about my system are starting to concern me.
One of the concerns I had during install was the fact the pre plumbed cylinder has pumps for the heating zones however this just pumps to the manifold that has mixing valves and its own circulation pump? at the time I was told this was normal and fine however I could never understand the point of two pumps and the mixing valve.
downstairs is fully open plan however they split this into three zone each with a thermostat to control it, I have since wired this so one central stat controls all of downstairs as the old system ended up with noticeably hot and cold floors.
upstairs every bathroom bedroom and the hall have a thermostat, I think this caused us problems as the 3rd bedroom always felt cold and this one room was always calling for heat, looking at the manifold another thing that concerns me is all zones have been opened right up 4l/min and I can see no real temperature difference on the flow and return.
Any advice you have would be great
Thanks
Richard
How does your heat pump run and at what temperature?
Thanks for your reply,
I only have the standard MELcloud app for reference until today it has been on the standard weather curve this would heat downstairs fairly quickly and turn off.
unfortunately the app wasn't setup until April this year, I do remember when the one bedroom was the only room calling for heating seeing the heatpump cycle Alot. (I'm not sure how often it should cycle in an hour but the graph of flow and return temperatures was very spiky)
after looking through the forum I have adjusted the weather curve today this had a flow temperature of about 31C this morning while heating.
@rich It's normally better to avoid too many zones. As you've found out, this can lead to only one room being heated at a time. As well as potentially causing unwanted cycling, it's inherently inefficient. BTW 3 cycles per hour is OK, much more isn't.
The flow and return temps should be about 4 degrees difference. It's easy to tell this by touch so it's worth having a feel of the rad pipes to confirm that (or otherwise) if Melcloud is reporting correctly. It's important the temp probes are installed correctly (mine weren't).
One thing you could try is to turn all stats up full and see what happens, e.g, do some parts of the house end up warmer than others This will also allow you to tweak your compensation curve so that it works without the room stats.
Posted by: @kev-mThe flow and return temps should be about 4 degrees difference. It's easy to tell this by touch so it's worth having a feel of the rad pipes that to confirm (or otherwise) if Melcloud is reporting correctly. It's important the temp probes are installed correctly (mine weren't).
How did you figure out your probes weren’t installed correctly @kev-m?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@rich, welcome to the forums. Is your house adequately warm and what’s your heat pump efficiency like?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editorPosted by: @kev-mThe flow and return temps should be about 4 degrees difference. It's easy to tell this by touch so it's worth having a feel of the rad pipes that to confirm (or otherwise) if Melcloud is reporting correctly. It's important the temp probes are installed correctly (mine weren't).
How did you figure out your probes weren’t installed correctly @kev-m?
Hi Mars,
I suspected because I thought the rads were hotter than the compensation curve was set at. I bought some cheap aquarium thermometers and confirmed that the flow was actually 4 degrees hotter than the comp curve said it should be. I got the installer to fix it when they were fitting my MMSP and it's OK now.
@derek-m yes I did thanks. They came back and fitted the energy meter properly and it's up and running. I also managed to apply for and get the extra RHI. I can now see energy used and delivered by the minute, which will be useful for this winter's tinkering.
sorry for the slow reply I was away this weekend.
in regard to the house feeling warm it does and can easily become too warm, the heating isn't really in use yet as the house is saying warm via large windows and evening sun. The smallest bedroom did struggle last winter overnight but I am going to check the insulation when it the temperature drops as I think this room is losing a lot more heat than any other.
Efficiency is harder to tell not having access to detailed figures, The apps estimated figures also record about 2Kwh per day even when not in use. looking over the info I have it looks like 2.5COP at my best guess
The system was probably cycling about 5 or more times when just the smaller bedroom was calling for heat so less than ideal.
The downstairs manifold shows a nice temperature drop however the upstairs looks to be only 1c or 2c drop. I think on the above advice I will buy some cheap aquarium thermometers and check everything out.
When the temperature drops, I will try putting all the stats up at the moment it would just overheat the house. Based on last year I would guess downstairs will overheat and upstairs will feel a bit cooler
@rich if your house is overheating when you whack the stats to full your weather curve is set too high, or your flow temperature mixer into the underfloor is too high. I think this time of year is just a time when things will cycle.
You can see below the heat pump cycling on and off over night and then not working at all during the day. Its not ideal, but its just the nature of cold nights and mild days.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 69 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 3 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 18 hours ago
-
RE: Buffers, hot water and cooling
@prunus, @jamespa is correct, but removing the buffer ...
By Brendon Uys , 23 hours ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 2 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 2 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 2 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
Hi @topher - you might be interested to see this very r...
By Transparent , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 4 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 5 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 5 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 5 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 5 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 7 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 1 week ago