Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still getting to grips with. It's not quite the same but you may find there's enough similarity.
If you haven't already found a solution you're happy with, here are some thoughts:
- if all you want is to schedule the timing of DHW heating, then you probably don't need HA to manage it - the Daikin MMI has enabled me to manage it.
- my MMI has a setting for User Profile (use the left knob to move to it). There are 3 different settings (right knob to set them). pin of 0000 gives you basic user settings; 1234 gives you Advanced User settings (my standard setting); pin 5678 gives you Installer Settings (which you'll need to make some of the more fundamental changes)
- In the Installer Settings menus, the "Tank" setting (icon of a shower head) gives me a submenu that lets me specify the operating mode: Reheat; Schedule; Schedule+Reheat. Reheat tries to keep the water temperature constant, Schedule does what it say, and Schedule+Reheat, which is what I've chosen, tries to do both. I've scheduled the DHW with a setpoint of 48 between 1am & 3am every day, and Reheat with a setpoint of 43 between 14:30 & 15:30 to try to recover from morning showers while the sun is up and before the really expensive rates kick in. The temperatures were set using their "Comfort" & "Eco" setpoints, which are set separately, to make it easier to manage the schedules should you want to tweak them.
- The Installer "Tank" submenu also includes the Disinfect schedule, where I could set the day of the week & time (I chose Sunday morning at 03:00 while the rate is likely to be cheap, and the normal heating cycle will have completed). You also get to set the Disinfect temperature & duration. Octopus set this to 30mins at 60deg. If you listen to The Heat Geek on Legionella, you'll be able to decide what works best for you.
- Remember to set the user profile back to 1234 once you've finished.
- The Onecta app in theory lets you manage schedules, but I found that it was all greyed out until I'd set something up with the MMI
Finally, I note that you have a Solar iBoost+. I had one of these that was useful when I was with OVO, who were paying me 5p/kWh. Any time that the battery was full, I diverted any excess power into the hot water. This wasn't that helpful, because my DHW was heated by gas, and the immersion heater was intended as a quick boost, and was at the top of the tank. I stopped using it once I switched to Octopus (15p/kWh). Have you thought about how you'll use it (if at all), now that you have your ASHP?
Currently viewing this topic 3 guests.
Recently viewed by users: Majordennisbloodnok 23 minutes ago.
- 26 Forums
- 2,360 Topics
- 53.5 K Posts
- 224 Online
- 6,026 Members
Join Us!
Worth Watching
Latest Posts
-
Sadly, no, @agentgeorge. The inverter will handle 5kW t...
By Majordennisbloodnok , 1 hour ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent The readings are 0 for amps, 0 ...
By Batpred , 1 hour ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 2 hours ago
-
RE: Speedcomfort radiator fans
I watched the video to see whether they'd potentially b...
By Sheriff Fatman , 2 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
@ecoste For what it's worth, this is my equivalent data...
By Sheriff Fatman , 3 hours ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 3 hours ago
-
RE: Setback savings - fact or fiction?
Will come back to the above points, but for now, I've j...
By cathodeRay , 3 hours ago
-
@jamespa I have found that it comes as a shock when we ...
By Toodles , 5 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
I suspect a good chunk of the "losses" are power consum...
By Bash , 6 hours ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Hi @mickamills . Welcome to the forum. It sounds like...
By bontwoody , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 7 hours ago
-
RE: External pipework insulation
@transparent I hope you are not being admonished @trans...
By Toodles , 7 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
The FT levels off at either the set point OR the minimu...
By AndrewJ , 1 day ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent Thanks, this helps. Could it be that St...
By Batpred , 1 day ago
-
RE: Clivet ASHPs and weather compensation
Simon did share a lot of very helpful advice. On furthe...
By ambris , 1 day ago
-
-
RE: Advice on internal circulation pump noise
Extend the primary branch and make sure you have more t...
By ASHP-BOBBA , 2 days ago