Buffer tank required? Samsung 12kW heat pump
I'm having a Samsung 12kw monobloc heat pump installed today. The fitter gets part way through the install then tells me there isn't space for the buffer tank. He says he's checked with the office and my 7 rad system doesn't actually need one.
This doesn't sound right to me but without the technical knowledge I can't be sure. Does anyone on here know if this is true?
Posted by: @riponowlI'm having a Samsung 12kw monobloc heat pump installed today. The fitter gets part way through the install then tells me there isn't space for the buffer tank. He says he's checked with the office and my 7 rad system doesn't actually need one.
This doesn't sound right to me but without the technical knowledge I can't be sure. Does anyone on here know if this is true?
Hi,
Look through the manual for your particular model of ASHP to find the minimum system water capacity requirement. Look at the specification for each of your 7 radiators and find the water volume of each. Add up the total volume of the 7 radiators and add maybe 10% to 20% for the volume of the pipework.
If the water volume of the radiators and pipework are greater than that specified by the ASHP manufacturer then it should be acceptable to operate without a buffer tank provide you don't have TRV's installed except in the bedrooms.
If you are still in doubt then ask the installer to explain in detail how, a buffer tank was initially specified, but is now no longer required.
@derek-m Thank you for responding. All the rads are specified to have TRVs on them (the install isn't finished yet). In fact I'd like to update them to smart TRVs eventually so I can schedule them for different times of the day.
Posted by: @riponowl@derek-m Thank you for responding. All the rads are specified to have TRVs on them (the install isn't finished yet). In fact I'd like to update them to smart TRVs eventually so I can schedule them for different times of the day.
Hi,
Did you specify TRV's or your installer? Are you also having thermostats?
@riponowl, this may help: https://renewableheatinghub.co.uk/why-do-you-have-a-buffer-vessel-with-a-heat-pump
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@derek-m A single Hive controller is being installed. My existing rads just had manual turn valves which never turned. I had to chase up the supplier after they sent the quote to make sure they would all the new ones would have TRVs so that they would be easy to replace with smart TRVs if I wanted to do that at a later date.
The most telling factor is that the installers turned up with a buffer tank, cut out a section of the vinyl flooring on which to fit it only to decide later that there wasn't space. It was only when I queried if they were putting in a buffer that installer came clean on what had happened. It was clearly part of the spec.
I'm going to get an update from them shortly, I'll report back in a bit.
@editor Thank you, that is really interesting. I almost feel bad for giving the installer a hard time now (almost). It seems to be at odds with this though
https://www.kensaheatpumps.com/buff-up-your-knowledge-of-buffer-tanks/
Now I really am confused.
@riponowl, I have to be honest, the buffer tank is a point of contention. We have one, and the industry seems to be split. Some installers insist on having them, others say that they are there to bail out poorly designed and installed systems. From what I've read, and I'm not an expert, having a well-designed system with no buffer tank and no TRVs on rads leads to much better efficiencies.
We have a buffer tank like I've said, and we have TRVs, and we have a SCOP of 2.7-2.8 which is quite reasonable and which we're not dissatisfied by.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Well, the install went ahead without the buffer, there was absolutely no space near the tank so I will so how it goes. I will have a better idea about how it is performing in a week or so. I have more pressing problems with non performing rads to deal with first 🙁
Thanks again to all contributors.
Posted by: @riponowl@derek-m A single Hive controller is being installed. My existing rads just had manual turn valves which never turned. I had to chase up the supplier after they sent the quote to make sure they would all the new ones would have TRVs so that they would be easy to replace with smart TRVs if I wanted to do that at a later date.
The most telling factor is that the installers turned up with a buffer tank, cut out a section of the vinyl flooring on which to fit it only to decide later that there wasn't space. It was only when I queried if they were putting in a buffer that installer came clean on what had happened. It was clearly part of the spec.
I'm going to get an update from them shortly, I'll report back in a bit.
Hi,
TRV's and thermostats were developed for use with gas and oil boilers, whose water flow temperature was much higher than that required to heat the home. An ASHP can control the water flow temperature down to much lower levels, in fact the lower the temperature, the more efficient the system will operate.
Of course it is your choice if you wish to have TRV's and thermostats installed in preference to the control system specifically designed for the ASHP.
@derek-m Thanks!
I just wanted to be a little more energy efficient by having the upstairs rads turn down during the day and the downstairs rads turn down a little at night. It's no deal breaker though, right now I will be happy if it just works.
It's unlikely to save you much if any money but you might want the option of TRVs in the bedrooms for comfort (if you like a cooler room). That's what I've done but they are fully open most of the time.
-
How to choose Towel Rails for an ASHP
20 hours ago
-
Samsung problems
2 weeks ago
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Sudden drop in COP
1 month ago
-
Surface mount or bury primaries for heat pump installation?
3 months ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 39 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 35 minutes ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 17 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 20 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 21 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 1 day ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 5 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 6 days ago