To save causing even more confusion to any prospective heat pump purchaser, I think that it would be useful to clarify certain points.
Based upon a normal home, with an accurately assessed heat loss of say 8kW, how would you define an undersized heat pump, a correctly sized heat pump and an oversized heat pump?
I am not certain how you arrived at the assessment of 50% on and 50% off operation for the larger pump in a comparison situation. Of the three comparisons that I considered, the worst case was the 6kW to 8kW, in which the 8kW heat pump would need to run for approximately 75% of the time to match the energy output of the 6kW unit running constantly. If the 8kW unit was to run for less than this figure it would mean that the heat loss had reduced, which in turn would cause the 6kW unit to start cycling. The maximum calculated increase in LWT was also with the 6kW/8kW comparison, which gave a required increase of approximately 2.2C.
What you need to remember is that the larger of the two heat pumps is cycling because the thermal energy demand is low, so differences in energy levels and changes in LWT are also quite low.
You keep quoting the laws of thermodynamics, so consider the following.
We have a gas boiler, which is controlled by an industrial type PID controller, in a Master - Slave configuration , which basically switches the gas boiler and water pump on and off. The gas boiler is set at its minimum output temperature, which is probably no higher than 50C.
The Master controller compares the actual IAT against the desired temperature setpoint, and calculates the required heat emitter temperature. A second sensor measures the temperature of one of the radiators, with this value being supplied to the Slave controller. When the radiator temperature falls below the required radiator temperature the gas boiler and water pump are started. It takes in the region of 4 minutes for the radiator temperature to increase above the calculated value, at which point the gas boiler and water pump are stopped. During milder weather conditions it can be more than 2 hours before the radiator has cooled to the point where the process is repeated. During colder weather conditions the heating is active more frequently, and for a slightly longer period, since the calculated radiator temperature is now higher.
This system keeps the IAT at a constant 21C +/- 0.2C throughout the day under varying weather conditions, although the actual radiator temperatures may vary by 5C or more.
The point that I am making is that when the heat pump stops the supply of thermal energy does not immediately fall to zero, but that on - off operation will tend to balance out, particularly under milder weather conditions.
Obviously running a heat pump in an on - off mode is not the most ideal, which is why permitting slight variations in IAT allows the on and off periods to be extended, and hence reduce the frequency of any cycling.
Great thanks everyone, lots of food for thought.
So the key takeaway is to not trust the nameplate capacity, and you have to size instead based around the nominal capacity (usually listed as -2c). And, for some models that's basically the same (e.g. the Ecodan 11.2kw still outputs 11.2kw down to -5c), and for others it's a massive difference (the Daikin 16kw HT drops to 11.5kw at -2c). So in this case the 11.2 Ecodan and the 16 Daikin are on a par. Confusing!
Posted by: @derek-mQuestion the need for such items as a buffer tank or plate heat exchanger, and if absolutely necessary then make allowance for these in the sizing of the heat pump.
I was chatting to my proposed installer yesterday, he said I would need a buffer tank (in fact 2, one for the rads and one for underfloor heating). I asked why, he said to deal with the expansion of the water in the heating system as it's heated, and to provide a buffer of hot water used when the heatpump does a defrost cycle. I've goggled needing a buffer tank with a heat pump and there are lots of articles saying that it's necessary.
You seem to be saying that a buffer tank is only rarely necessary. Why do you say that?
@Fazel @Derek_M
Well here is some interesting behaviour last night. I lowered the flow temperature at the top end of my WC curve by 2 degrees bringing it down from 37C at 15C OAT (top graph) to 35C at 15C OAT (bottom graph)
Although last nights was a shorter run length, cycling appeared much more quickly, COP was virtually identical. We were both warm enough in the house but the thermostat in the hall never reached the 23C set point
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@Kev_M
I was thinking about the right hand graph again last night Kev. My understanding of it is that the different plots for A12, A7, A2 and A-7 are for the different OAT's and all show peak COP at about 9kW load for the 11kW heat pump.
If that is the case shouldnt we be aiming for the most frequently used load to be in that 9kW region, not the peak load?
If Im reading this totally wrong, anyone feel free to jump in please.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody
Although last nights was a shorter run length, cycling appeared much more quickly, COP was virtually identical. We were both warm enough in the house but the thermostat in the hall never reached the 23C set point
As the flow temperature is degreased, the mean radiator temperature degreases, thus there is less heat transfer from the radiator to the air. As you cannot increase the radiators(only if you play with those pc fans) the only thing left is to have it off for longer, to allow the heat to dissipate.
Posted by: @bontwoody@Kev_M
I was thinking about the right hand graph again last night Kev. My understanding of it is that the different plots for A12, A7, A2 and A-7 are for the different OAT's and all show peak COP at about 9kW load for the 11kW heat pump.
If that is the case shouldnt we be aiming for the most frequently used load to be in that 9kW region, not the peak load?
If Im reading this totally wrong, anyone feel free to jump in please.
-- Attachment is not available --
I would see it like this:
Before anything else, don't constrain yourself with just one point 9kW, there is a range from 6kW to 11kW that is close to that peak, so use the range rather than the point
Usually you would size let's say 11kW for -5 then it automatically drops to lower at 2,7,12 degrees, so let's say 11,9,7,5kW ish
@fazel Ah, I see, that would account for what appears to be a smaller delta T at the lower temperature.
Does the increase in off cycles negate the potential increase in efficiency from having a lower flow temp as the COP appears the same?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@derek-m @editor @bontwoody shall we move/create @bontwoody own hp thread and move his topic there?
Like most on here I'm not a heatpump engineer either. My background is in physics and engineering with a recent diversion into local government. So I tend to try to understand broad brush principles as an aid to homing in on specific solutions, which of course then need testing' against the specific requirement.
To answer the questions
Posted by: @derek-mBased upon a normal home, with an accurately assessed heat loss of say 8kW, how would you define an undersized heat pump, a correctly sized heat pump and an oversized heat pump?
An 8kW house will spend most of its time at 4kW and towards the end if the season will be at 2kW or less. Given that many heat pumps have a modulation ratio of about 3 or a bit less I would therefore say anything over 12 kW is oversized by more than is comfortable. Allowing for a bit for dhw I'd say anything from say 9-12 is OK,. Between 8 and 9 is 'tight' and on continuous really cold spells supplementary heating will likely be needed. Anything less than 8 is undersized, but if householder has a supplementary form of heating that they want to use, still a valid choice (logburners can be several kW and many people actively like using them.). I make this observation conscious also that the BRE plots referred to earlier definitely point in many cases to undersizing. Having said that the grant requirement is to deliver 100pc of dhw and ch requirement, so less than 8 and a bit wouldn't strictly qualify.
In all cases I mean actual capacity at design OAT, not sticker capacity, and I'm assuming 24x7 operation in the coldest season so no allowance for reheat (in the coldest season).
This being the case and all other things being equal I would steer a techy friend who likes to live on the edge towards the bottom end of 9-12, and a non techy one who liked creature comforts at all cost towards the top end. However unit sound power, appearance and size also become factors at this point, perhaps more so than capacity.
So in summary I would not argue against a 50% uplift on an accurately assessed heat loss, provided the chosen heat pump has a decent modulation capability. However I would argue against the blanket application of a 50% uplift on top of a spreadsheet based loss assessment which in all liklihood already has margin or actual error built in.
Posted by: @derek-mThe point that I am making is that when the heat pump stops the supply of thermal energy does not immediately fall to zero, but that on - off operation will tend to balance out, particularly under milder weather conditions.
I agree and said so earlier. Obviously the rate at which the heating system cools down so the radiators stop emitting depends on the thermal mass of the central heating system. My radiators cool very quickly even in mild weather, taking I would guess less much than 30mins to reach something quite close to room temperature.
I did speculate above that fast cycling, at a frequency such that the radiators don't cool much between cycles, may be better than slow cycling. Of course this goes against hp 'lore' but if @fazel is correct that cycling per se (as opposed to the change in lwt necessary to compensate for cycling) doesn't, with modern heat pumps, cause much of a penalty then it seems to me that extending the modulation range by fast cycling is not such a bad idea.
Posted by: @derek-mI am not certain how you arrived at the assessment of 50% on and 50% off operation for the larger pump in a comparison situation
That wasn't an assessment it was an example, for the purpose of illustrating the uplift in ft needed in a cycling situation. That said I have certainly seen 50:50;on off ratio or worse at fairly low OAT in plots people have presented. To get to the uplift in lwt required I assumed rad output goes as deltat (rad-room)^1.3, which is the case for most rads, and that the no-cycling delta t (rad-room) was 20. This leads to an uplift of 10C on the basis that (30/20)^1.5 is roughly 2, corresponding to the doubling in output required.
Overall I think a couple of things have come out of this:
A bit more thought, and possibly experiment, is needed, with up to date info on the performance of heat pumps, on whether fast/short cycling is actually good or bad. I don't _think_ it's as obvious as it used to be with modern inverter driven pumps!
It would be good if we had some actual figures averaged over the year for the theoretical cycling 'penalty', initially assuming no averaging of the type discussed above. If I could find some figures for OAT over the year in' buckets' I'd happily do the spreadsheet. It might be possible to get some sort of estimate from a year's worth of smart meter readings. Thus calculation would inform the cost/comfort debate in relation to sizing.
And of course: we really don't have a commonly accepted method which is capable of determining the required load with sufficient accuracy.
For me the last of these remains the stand out issue, unless it can be shown by some work on the first two that the penalty for gross oversizing is not as bad as it might be. Given the frequency of complaints which can be traced in part to gross oversizing, I'm not hopeful for this but still open minded if the figures were run.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@fazel Agreed, but the highest COPs are clustered around the 9kW load so shouldnt we aim for the mode output to be in that region?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@fazel Ah, I see, that would account for what appears to be a smaller delta T at the lower temperature.
Does the increase in off cycles negate the potential increase in efficiency from having a lower flow temp as the COP appears the same?
At the point where it starts cycling because it cannot lose the heat in the system, even if the COP is the same, it is up to you if you want to allow it to run like that, or do different. Having it off, allowing the water to cool should basically help with the efficiency in theory. Because the heat pump regardless of the type, likes to loose the heat it produces, there is a fine line and in time you might be able to notice or not a small difference in COP.
Posted by: @bontwoody@fazel Agreed, but the highest COPs are clustered around the 9kW load so shouldn't we aim for the mode output to be in that region?
you sure can at -5, but as the OAT increases your radiators cannot put out 9kW thus you are starting the cycling prematurely.
you sure can at -5, but as the OAT increases your radiators cannot put out 9kW thus you are starting the cycling prematurely.
There sure are a lot of variables to consider here! 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 58 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
All agreed. if you want to delete our exchange for cla...
By JamesPa , 8 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 53 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 2 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 4 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 23 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago