@clairelp finally I can see that you have a volumiser, not buffer setup. So there should be not extra pumps on the system. The pump built into the Daikin is quite strong, I can't see a bypass (but it's hard to tell with the quality of pictures)
This is what they look like, it maybe in the airing cupboard, do you TRVs on every radiator.
Does the noise stop when doing hot water.???
@clairelp I'd expect the primary pipes - which is the ones that connect your heat pump to to the volumiser, to that black and red Esbe valve, and to any manifolds or branching off in your cupboard, to be at least 28mm diameter. From the pictures it looks like they >may< be 22mm? It's hard to tell though.
Apologies - I've forgotten the output of your heat pump..... There's a limit to how many kWhs you can get down each diameter pipe to not go over 0.9 - 1m/s velocity. For 22mm the limit is around 6kW. For 28mm it's more like 10kWh. * Could you please check what the diameter of the pipes going to your volumiser are please? The volumiser is the small gray tank thing in the attic.
Did you then say that each pipe heading off around the house is 10mm? You can get around 1kW down each one of these to not go over 0.9 - 1m/s velocity.
The reason you would want to keep to that velocity limit is it tends to get noisy above it. Also much above 1.5 and it starts to erode the internal of a copper pipe.
As Ken and others thought previously the pipe clips attach the pipe directly to the wood in your attic. An alternative would be to use a clip that goes to the outside of the insulation material. There is a brand called "Primary Pro" that is a favourite with heat pump installers. As you have a cold attic I'd advise consider this a cold space and upgrading the insulation up there - you'll save money in the long run.
Ken's suggestion to check the air vent is a good one too.
*These numbers assume you have glycol in your system, and that the dT of your heat pump is 5. dT means the delta T - it stands for the temperature difference between the hot pipe from the heat pump and the cold one. Delta means "difference" in Latin. As dT increases you can get more and more heat down a pipe within that velocity limit.
Planning your dream house? Book a simple one-to-one consultation to get you on a good path - here.
Hi, we not had chance to get in the loft to look at the valve yet, difficult to go up in loft making noise when children asleep in the evening.
I did look at pressure gauge in cupboard and it about 1.6.
Friday installers are coming so I will keep you posted. We also have installers msc compliance department checking the install following week. Hoping they will have an answer 🤞🙏
the ashp does have anti freeze valves, with it not been below freezing hoping be okay to keep turning off for a couple of nights.
also looking into sound proofing and insulation for the loft.
Hi,
Installers, have turned down the velocity to I think he said 21-22 and was previously 24. Think he said in the bypass valve. And I sorry can’t remember exactly but I think he said like it around 21 and maybe 24 was making too much noise.
At moment, I don’t think I could hear it and running quieter, it’s only just done so I will test it later when doing hot water and have to wait for a cold night.
🤞
They also did some settings on the frost cycle. They said it shouldn’t be coming on when not cold enough and shouldn’t be constantly going. Said there is two defrost settings one I think he said for the pipes and one for actual pump. They said if changes didn’t help they will contact Daikain, as some setting they can’t change.
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 748 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
You are very probably right, but it's still just possib...
By JamesPa , 39 minutes ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@transparent With the abolition of S21 long term ten...
By JamesPa , 46 minutes ago
-
RE: UFH downstairs and radiators upstairs balancing question
This is a tricky one. I'm having the same problem. A ...
By davidnolan22 , 2 hours ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 2 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 4 hours ago
-
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 13 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I have only just spotted this post, sorry I missed it e...
By JamesPa , 18 hours ago
-
RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 20 hours ago
-
RE: Electricity price predictions
Remember that almost all submissions to Government Publ...
By Transparent , 23 hours ago
-
@old_scientist I dont monitor the tank temperature but ...
By bontwoody , 1 day ago
-
RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 1 day ago
-
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 1 day ago
-
RE: Who has a V2G EV installation
Im looking at Anderson or Simpson and Partners, somethi...
By AgentGeorge , 1 day ago
-
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 2 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 2 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@allyfish It was going so well with month after month s...
By Toodles , 3 days ago
-