@carlo - not much better, is it. It looks more like a user guide than a technical manual, see if you can find the latter. It just might have more detail (if it exists and you can find it).
Midea 14kW (for now...) ASHP heating both building and DHW
@carlo I have a 16kw LG Therma V. Installed 2020 so even less data available!
Can you join the Facebook LG Therma user group? They have some good technical people & installers.
Are you using weather compensation (AI) ? My usage dropped from circa 8000kwh a year to 5800kwh. Facebook user group has an excellent document that helps setup correctly. PM me if you want it by email
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 Sadly (?) I don't use Facebook but I would still like the link to the user group, I might peruse through my wife.
I still haven't set weather compensation, I will send you a PM with my email for the Grail, thank you.
Whoops, no PM, I still don't qualify due to forum rules. Can you send one to me? Maybe I can reply
10kW PV
14kW LG Therma V ASHP
Induction heater
Posted by: @carloI still haven't set weather compensation, I will send you a PM with my email for the Grail, thank you
Setting up WC correctly is pretty much the most important thing to do with any heat pump.
In summary:
Turn up all thermostats and TRVs to full so they are permanently on. Make sure the heat pump has any room influence function disabled, ie it's operating purely on wc.
Operate your heat pump 24*7
Set the high OAT end of the WC curve to say 25C flow temp at 20C outside temp (or 23 C ft if you have ufh)
Set the low OAT end of the WC curve to the design flow temp at the design outdoor temp. If you don't know these set it to ft 55 (radiators) or ft 40 (ufh) at -10 OAT
The house will overheat!
Turn down the ft at low oat end until it just keeps to the right temperature. Do this slowly, changing the flow temp by no more than 1C per day as you approach the correct value.
Leave and enjoy cheaper, more comfortable, heating!
You may need to balance the radiators to get if rooms settle at different temperatures. Separate instructions needed for this which can be provided.
If you wish you can set trvs in any rooms that suffer from occasional ocerheating a couple of degrees above target. Basically however you want to leave both trvs and thermostats out of the loop, ie have them permanently on.
This is best done in the coldest months because you get a more accurate setting then, but you can do it roughly in the shoulder season and tweak when it gets colder
This is the polar opposite to how we operate boilers in the UK, so is a bit counterintuitive at first.
It's worth reading this guide to heat pumps to understand better some of the differences between them and boilers.
Can post more detailed instructions if you don't connect to the lg specific ones on Facebook for any reason, the process is model independent, make and model only affects some detail of which burtons exactly you have to push to set the curve
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Time of Use tariffs are important in the mix - if available as an option. e.g.
1. With Intelligent Go overnight tariff just 7p it makes sense for us to INCREASE temps overnight (opposite of setback). In our case by 1 deg
2. Similarly we heat hot water at night on a schedule to 50deg (with top up daytime heating just 40deg if necessary). In any case hot water can have a lower target for most people - try 47deg at first and then tweak lower if possible. Will be more than sufficient for most households - unless several teenagers!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441Time of Use tariffs are important in the mix - if available as an option. e.g.
1. With Intelligent Go overnight tariff just 7p it makes sense for us to INCREASE temps overnight (opposite of setback). In our case by 1 deg
2. Similarly we heat hot water at night on a schedule to 50deg (with top up daytime heating just 40deg if necessary). In any case hot water can have a lower target for most people - try 47deg at first and then tweak lower if possible. Will be more than sufficient for most households - unless several teenagers!
Agreed with the one qualification that increasing the nighttime temperature should ideally be done by increasing the flow temperature at night not by reducing/controlling the daytime temp using a thermostat.
Some heat pumps allow you to do this, some don't. For ones that don't it may be better just to operate at the same temperature 24*7, or get either homely or havewise to do it for you.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I knew of the importance of weather compensation but I wanted to identify and solve the problems with the system that I think are there before adding other variables to it.
Correct me if I'm wrong, but if I'm running the heat pump at fixed 37° flow temperature, with the outside temperature varying between 4° and 17°, I think that, at the very least, I should get the COP corresponding to 37° flow with 4° outside. But, according to my measurements, I'm getting way less than that.
I know there is a lot to set and tweak, but I would like to start from a known good system/installation. For example I can set the flow temperature to rise a bit when there is overproduction of photovoltaics (I have a 10kw array). Very rare in winter but during autumn should happen more.
Right now I'm a bit at a loss, that's way I want to gather more data.
10kW PV
14kW LG Therma V ASHP
Induction heater
Posted by: @carloCorrect me if I'm wrong, but if I'm running the heat pump at fixed 37° flow temperature, with the outside temperature varying between 4° and 17°, I think that, at the very least, I should get the COP corresponding to 37° flow with 4° outside. But, according to my measurements, I'm getting way less than that.
Yes you should, or thereabouts, but only if you are operating without thermostats or TRVs. If you have a thermostat constantly cycling it on and off, or TRVs/zone valves shutting down much of the system, then you will almost certainly achieve a COP which is poorer, possibly quite a lot poorer, depending on how it is working. Worst of all is a 'smart' thermostat with 'proportional' control, they can really knacker heat pump performance.
Posted by: @carloI knew of the importance of weather compensation but I wanted to identify and solve the problems with the system that I think are there before adding other variables to it.
My initial reaction was fair enough. On second thoughts (and referring to the above) its almost impossible (exception - a very low temp UFH system) for a heat pump to be working properly without WC and the house to be simultaneously comfortable, simply because of the need to match emitter output to demand.
There isnt that much that can go wrong with a heat pump system, unless the heat pump itself is at fault, which is pretty rare. The principal issues are
- substantially oversized (and thus cycles a lot and/or operates permanently at an inefficient part of the compressor curve)
- presence of buffer, low loss header, or plate heat exchanger between heat pump and emitters, or mixers if you have UFH
- pipework restrictions/inadequate primary flow/blocked filters
- undersized emitters
- overuse of external controls, most particularly smart stats like Hive and TRVs
- incorrectly adjusted weather compensation
- poor insulation of primary pipework
Combinations of these are not unknown and that can really mess things up!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I run 24x7 with weather compensation. So flow temps will normally increase at night.
As my ashp was a retrofit I use simple digital thermostats to manage the target temp increase overnight.
Afaik havenwise is a bit limited on compatibility and while Homely supports many more they don't support my 2020 installed LG. I guess both are worth considering if compatible.
I think I've got my setup reasonably good now after a few years:
1. Move to weather compensation
2. Reduced daytime DHW target temps with higher temps scheduled overnight
3. Use higher temp targets overnight for room temp to maximise cheap overnight tariff
4. Best time of use tariff (in my case Octopus Intelligent Go) ... linked to zappi charger and ev
5. Maximise IOG to fill batteries at night. I use WonderWatt to help with that (again only suited to certain compatibilities)
6. Export solar prod + force discharge batteries outside of heating season.
So inevitably it very much depends on setup, usage, tech saviness, etc etc. This forum has helped a lot with understanding options & questions to ask!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@carlo picking up on potential inefficiency from cycling if Oversized heat pump..
One option in LG is to run in Silent/Quiet mode. I don't use it but know others have .. quite successfully reducing cycling.
Personally I'd go for weather compensation as priority .. its a chicken & egg thing! With WC set changes should become clearer.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 572 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
Heat loss and radiator sizing are necessary, but they’r...
By Mars , 3 minutes ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
Well I've had an interesting few days and would like to...
By giganto , 47 minutes ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Yes, here's mine. From the service manual parts numbers...
By bobflux , 5 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
Thanks for sharing your observations, both of you. From...
By Jonatan , 5 hours ago
-
Had to learn the hard way 🤣 now I'm sharing T...
By bobflux , 5 hours ago
-
RE: Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Im assuming from your original post that hysterisis ref...
By JamesPa , 6 hours ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 8 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 9 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 13 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 14 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 19 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 1 day ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 2 days ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 3 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 4 days ago