ASHP for small garage and workshop
Posted by: @bobtskutterYou have a plate heat exchanger for system separation don't you?
Yes, I do. I also have glycol in the primary circuit, and use a specific heat capacity of 4.05 for that (I noticed you use 4.2 ie pure water). The secondary circuit has quite a large volume, I haven't formally worked it out, but there is one huge K3 in the kitchen (15L?) plus several medium sized K3s and a few smaller ones, Perhaps (guessing here a bit) 100L in all just in the rads.
Posted by: @bobtskutterWith a plateHex i get 7.7kg ice, no hex 4kg.
Either way, that is a lot of ice. Credibility/sanity check?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @transparentIt's mainly sold in Australia & NZ where they want cooling as well as heating.
Mitsubishi heat pumps works great in low temperatures. Requires minimal maintenance. Here in Victoria, they are offered under government rebate program.
Heat pump installer at ipromiseaustralia.com.au
Hello everyone, time for a dumb question.
Am I allowed to self install a heat pump in the UK?
It would be the only one on the property.
It would be at least 1m from the boundary.
The size of the machine would be less than 0.6m3.
I am not MCS registered.
Thanks
Bob
@bobtskutter A significant number of us have Bob. see this https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/can-i-install-my-own-ashp, also look up Glynn Hudson on Youtube
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
That's a good question @bobtskutter
Yes, you can install a heat-pump on a DIY basis.
The legal requirements you need to fulfil are:
- Apply to your DNO using their online process for Low Carbon Technology (LCT)
- Get the mains electrical connections installed, or approved by, a qualified electrician who will supply you with a Building Regs Part-P certificate
- Apply to a Building Control organisation, such as your Local Planning Authority, to address Part-L and any other issues such as noise complience
Let us know if you want any of the above explained more fully.
Save energy... recycle electrons!
Thank you. The proposed ASHP would be a low power (4kW) device connected to an existing supply. Do I still need to inform the DNO?
Thanks
Bob
Yes Bob.
An LCT Application is for all sites where a heat-pump or EV charger is to be connected to an existing supply.
To see an example of where I believe the assessment has 'gone wrong' have a look at my comments on the topic about Twin 10kW ASHPs with volumisers.
Save energy... recycle electrons!
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 90 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 hours ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 6 hours ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 18 hours ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 2 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 3 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 5 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 6 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 6 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 6 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 6 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago