@gfletcher 

That’s the weather comp setting but you have to set the curve in settings.

 

Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.

2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.


   
ReplyQuote
(@gfletcher)
Trusted Member Member
243 kWhs
Joined: 2 years ago
Posts: 24
Topic starter  

@morgan Brilliant - thanks, I'll look at the curve settings.


   
👍
1
ReplyQuote
Morgan
(@morgan)
Noble Member Member
4702 kWhs
Joined: 4 years ago
Posts: 563
 

@gfletcher 

you’re welcome.

Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.

2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.


   
ReplyQuote



(@derek-m)
Illustrious Member Member
15282 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4433
 
Posted by: @gfletcher

@morgan Brilliant - thanks, I'll look at the curve settings.

Hi Gavin,

Obviously you need to set the slope of the weather compensation to the requirements of your particular home. I would suggest that you start with the following settings and then fine tune as necessary.

Cold end: LWT of 50C at amb. of -5C.

Warm end: LWT of 25C at amb. of 20C.

The indoor temperature will probably change very slowly, so monitor your system for quite a number of hours and let it stabilise before making any adjustments.

I hope that this helps.


   
👍
1
ReplyQuote