Are antifreeze valves essential for a glycol free ASHP system?
During a recent upgrade to my 12kW Samsung ASHP set up, the glycol was removed as requested. I expected one or more antifreeze valves to be fitted, but I was told on good authority that these were not required. So I wondered if anyone had any views on the pros and cons of fitting antifreeze valves? If fitted, is one on the return flow sufficient or should there be one on the leaving flow too? Is anyone in the same position, having no glycol and no antifreeze valves?
I must admit to feeling a little anxious when all occupants of our three terraced cottages were away at the same time after Christmas, when it went very cold and any power cuts would have gone unnoticed!
Great question. @heacol will know the answer.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
According to Samsung, you either have to have antifreeze valves or glycol. As glycol will add 20%+ to your heating bill, it is not really an option. In reality, if you want top install them, 1 will suffice on the lower pipe, however, it is nearly impossible for ice to damage the Samsung unit as the internal connecting pipes are rubber, and will expand on freezing.
It is up to you, I have about 600 units in the field, of all makes, and no glycol or antifreeze valves, and have not, in the last 15 years, had a single unit damaged by ice.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@heacol I’ve also wondered how that worked. Will the system remain protected if there’s a big winter storm with temperatures below zero and power lines get taken down, and we’re without power for a few days. Wouldn’t that do some damage and wouldn’t stuff that shouldn’t freeze, freeze?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I am not saying the units will not freeze in some conditions, and I have seen many, however it is the design of the unit it'self that will determine if there is any damage. Units that have standard circulator pumps in them such as Valiant, Midea/Clivet and others are vulnerable as standard circulators can easily be damaged by freezing, some units with pumps like Panasonic are not affected as they have taken the time and effort to make their own pump. Units that have no pump, like Samsung and Mitsubishi, are not usually affected.
As I said, it is your choice. My choice is Panasonic hands down, it is so far ahead of the pack for many, many reasons.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @heacolAs glycol will add 20%+ to your heating bill,
Really? That is an enormous claim, citation required. I am aware of talk around a small increase, but 20% plus ( by how much plus) is astonishing.
@abernyte Difficult to get specific figures but I work on
Water 4.184kj/kg.K.
Monopropylene glycol 3.884kj/kg.K (@30%)
Monoethylene glycol 3.712kj/kg.K. (@30%)
Pump at say 50W will cost 1p/hour to run, with glycol added 1.1p/hr.
I work for a manufacturer of heat pumps and boilers.
@david-i interesting. Thanks for sharing. So do you avoid glycol in systems too?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor No Glycol in our Daikin installation but we do have two antifreeze valves. When the ‘Boss’ came to do a little ‘snagging’, he was surprised (and I think, a little miffed due to their cost) that his installers had fitted them in both pipes rather than just one. I was rather pleased that they had fitted them in both as surely, if the pipes are both very cold, isn’t better that they both drain? (Or is not how this precaution is supposed to work perhaps?). (Daikin are coming today to carry out the first annual service) Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Anti-freeze valves provide some guarantee of a fail safe if the system is unpowered for a long period and all other forms of frost protection such as the unit pump circulating water and/or frost protection heating in the circuit fail. You are into double jeopardy however - a long power failure coincident with extreme prolonged low temperatures. Anti-freeze valves should be on both outdoor unit supply and return pipes at the lowest point. Glycol isn't really required in the UK provided external pipework is properly insulated and protected.
Glycol lowers the specific heat of water with increasing concentration, it's the renewable parallel of adding hydrogen gas to mains gas methane, which lowers the calorific value of the resulting blend. That's why using H2 for domestic heating is a dumb idea, aside from the cost of producing it and the safety issues it creates.
Which does not get us anywhere near a 20% plus energy cost increase caused by using glycol.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 43 Online
- 5,744 Members
Podcast Picks
Latest Posts
-
RE: How to choose Towel Rails for an ASHP
@grahamf yeah great shout, we have something similar he...
By Rob Nezard , 8 minutes ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 32 minutes ago
-
That's probably the most important point, maybe see if ...
By cathodeRay , 4 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 4 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 6 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 7 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 8 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 22 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 24 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 24 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 1 day ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago