@morgan I am assuming that there has been no change to the LED's or ASHP operation. Are there any error messages on the thermostat, or is there any form of indication to show that pairing has actually been accomplished?
Try increasing the thermostat setpoint to 30C, if the flame signal lights on the thermostat display but none of the LED's light on the RF-Switch, it would indicate that the thermostat and RF-Switch are not paired, that the thermostat has a fault on the RF circuit or that the RF-Switch is faulty.
Either way you will have to get the 'experts' back to replace the faulty equipment.
Posted by: @derek-m@morgan With your system switched on, set the desired temperature on your thermostat at 15C and wait for up to 15 minutes to see if the Boiler LED switches on or off and the ASHP stops.
Nothing happens. I seriously appreciate your time Derek but I think I need the installers back here because no matter what the only way I’ve successfully managed to turn it off is to shut off the power.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @derek-m@morgan I am assuming that there has been no change to the LED's or ASHP operation. Are there any error messages on the thermostat, or is there any form of indication to show that pairing has actually been accomplished?
Try increasing the thermostat setpoint to 30C, if the flame signal lights on the thermostat display but none of the LED's light on the RF-Switch, it would indicate that the thermostat and RF-Switch are not paired, that the thermostat has a fault on the RF circuit or that the RF-Switch is faulty.
Either way you will have to get the 'experts' back to replace the faulty equipment.
No change. No error messages. The only indication of pairing succeeding is after holding the CH1 or Boiler button for 5 seconds is the corresponding flashing several times then stopping and extinguishing to signal pairing is complete as per P12 of the manual. The 30c setting does nothing.
I can only assume that it was initially set and commissioned correctly but at hand over the guy tried demonstrating various scenarios to us. I can only assume he failed/forgot to return it to the proper setting and hence the unit, albeit paired, isn’t set to be controlled by the room stat.
I’ve waited all day for a call back which didn’t come. I’m still withholding about £6.5k of monies due so that should concentrate their efforts hopefully.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@derek-m That is what it was this morning with an ambient temperature od 3 deg C and an room temperature of 21 deg C, because the system runs continuously, without any third party intervention (thermoststs, buffer tanks or system seperation) Iw will remain at this level cindefernatly if the ambient tenlerature does not chainge, however it will get better if the ambient temperature goes up andn vice versa.
This is how an open zone radiator system performs, under floor is better than this.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@morgan Obviously I cannot comment on whether your system was correctly commissioned in the first place, since I was not there. Did you try my previous suggestion of changing the FTC6 controller from weather compensation to flow control?
@heacol The house must be very well insulated to produce that type of result, what was the water flow temperature? I didn't realise the temperature had fallen to 3C yet in the UK, where is the system located?
Posted by: @derek-m@morgan Obviously I cannot comment on whether your system was correctly commissioned in the first place, since I was not there. Did you try my previous suggestion of changing the FTC6 controller from weather compensation to flow control?
To be honest I don’t know. I’ve tried so many suggestions I don’t recall.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @derek-m@heacol The house must be very well insulated to produce that type of result, what was the water flow temperature? I didn't realise the temperature had fallen to 3C yet in the UK, where is the system located?
No, it is not well insulated, it has solid sandstone walls, double glazing and 200mm of insulation in the loft, build at the turn of the last century, it is just north of Glasgow.
COP has nothing to do with insulation, it is the result of system design. If you do not control your system properly, your radiators are incorrectly sized and your system is badly designed, (buffer tanks, system separation and third-party thermostats) you do not stand a chance of having a good COP.
If it is designed and controlled correctly, you can expect this level of performance regarbless of insulation levels. Insulation, levels, exposure, draft profing, buiding construction and occupent preferences all have to be taken in to account when the design is conducted. NOT the EPC, they are not worth the paper they are written on.
Do you drive your car at 70 miles per hour in third gear with your foot flat and control the speed with the key? Or, do you put it in 6th gear and switch on cruise control?
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @derek-m@morgan Good luck with getting your 'experts' back.
Thanks. It's very frustrating. The fact I'm holding back a considerable sum of money might concentrate their minds.
Thanks very much for your efforts on my behalf. Truly appreciated. At least I know that the system is very capable of getting my house toasty warm. Just needs fine tuning to get it as efficient as possible. Responding to the room stat will be a positive move because powering off to stop the heating is a bit of a PITA.
Cheers.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
-
UFH and ASHPs
4 weeks ago
-
Installing your own ASHP - DIY
2 months ago
-
ASHP install contract and BUS grant money
4 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
4 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
4 months ago
- 22 Forums
- 2,084 Topics
- 45.9 K Posts
- 18 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@bart Thanks for your help but I have already been ther...
By Dwynwen , 7 hours ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 11 hours ago
-
A good start but I’m glad I didn’t need to learn someth...
By Judith , 11 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 15 hours ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 19 hours ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 20 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@benson I have gone down the Home Assistant and wavesha...
By Grantmethestrength , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 1 day ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 1 day ago
-
RE: Vaillant AroTherm Plus 7kW
Depends on the flow temperature; the Czech data sheet i...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 3 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 3 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 3 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 4 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 4 days ago