@morgan I am assuming that there has been no change to the LED's or ASHP operation. Are there any error messages on the thermostat, or is there any form of indication to show that pairing has actually been accomplished?
Try increasing the thermostat setpoint to 30C, if the flame signal lights on the thermostat display but none of the LED's light on the RF-Switch, it would indicate that the thermostat and RF-Switch are not paired, that the thermostat has a fault on the RF circuit or that the RF-Switch is faulty.
Either way you will have to get the 'experts' back to replace the faulty equipment.
Posted by: @derek-m@morgan With your system switched on, set the desired temperature on your thermostat at 15C and wait for up to 15 minutes to see if the Boiler LED switches on or off and the ASHP stops.
Nothing happens. I seriously appreciate your time Derek but I think I need the installers back here because no matter what the only way I’ve successfully managed to turn it off is to shut off the power.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @derek-m@morgan I am assuming that there has been no change to the LED's or ASHP operation. Are there any error messages on the thermostat, or is there any form of indication to show that pairing has actually been accomplished?
Try increasing the thermostat setpoint to 30C, if the flame signal lights on the thermostat display but none of the LED's light on the RF-Switch, it would indicate that the thermostat and RF-Switch are not paired, that the thermostat has a fault on the RF circuit or that the RF-Switch is faulty.
Either way you will have to get the 'experts' back to replace the faulty equipment.
No change. No error messages. The only indication of pairing succeeding is after holding the CH1 or Boiler button for 5 seconds is the corresponding flashing several times then stopping and extinguishing to signal pairing is complete as per P12 of the manual. The 30c setting does nothing.
I can only assume that it was initially set and commissioned correctly but at hand over the guy tried demonstrating various scenarios to us. I can only assume he failed/forgot to return it to the proper setting and hence the unit, albeit paired, isn’t set to be controlled by the room stat.
I’ve waited all day for a call back which didn’t come. I’m still withholding about £6.5k of monies due so that should concentrate their efforts hopefully.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@derek-m That is what it was this morning with an ambient temperature od 3 deg C and an room temperature of 21 deg C, because the system runs continuously, without any third party intervention (thermoststs, buffer tanks or system seperation) Iw will remain at this level cindefernatly if the ambient tenlerature does not chainge, however it will get better if the ambient temperature goes up andn vice versa.
This is how an open zone radiator system performs, under floor is better than this.
@morgan Obviously I cannot comment on whether your system was correctly commissioned in the first place, since I was not there. Did you try my previous suggestion of changing the FTC6 controller from weather compensation to flow control?
@heacol The house must be very well insulated to produce that type of result, what was the water flow temperature? I didn't realise the temperature had fallen to 3C yet in the UK, where is the system located?
Posted by: @derek-m@morgan Obviously I cannot comment on whether your system was correctly commissioned in the first place, since I was not there. Did you try my previous suggestion of changing the FTC6 controller from weather compensation to flow control?
To be honest I don’t know. I’ve tried so many suggestions I don’t recall.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @derek-m@heacol The house must be very well insulated to produce that type of result, what was the water flow temperature? I didn't realise the temperature had fallen to 3C yet in the UK, where is the system located?
No, it is not well insulated, it has solid sandstone walls, double glazing and 200mm of insulation in the loft, build at the turn of the last century, it is just north of Glasgow.
COP has nothing to do with insulation, it is the result of system design. If you do not control your system properly, your radiators are incorrectly sized and your system is badly designed, (buffer tanks, system separation and third-party thermostats) you do not stand a chance of having a good COP.
If it is designed and controlled correctly, you can expect this level of performance regarbless of insulation levels. Insulation, levels, exposure, draft profing, buiding construction and occupent preferences all have to be taken in to account when the design is conducted. NOT the EPC, they are not worth the paper they are written on.
Do you drive your car at 70 miles per hour in third gear with your foot flat and control the speed with the key? Or, do you put it in 6th gear and switch on cruise control?
Posted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @derek-m@morgan Good luck with getting your 'experts' back.
Thanks. It's very frustrating. The fact I'm holding back a considerable sum of money might concentrate their minds.
Thanks very much for your efforts on my behalf. Truly appreciated. At least I know that the system is very capable of getting my house toasty warm. Just needs fine tuning to get it as efficient as possible. Responding to the room stat will be a positive move because powering off to stop the heating is a bit of a PITA.
Cheers.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
-
Rodents! A word of warning for heat pump owners
1 week ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 weeks ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
1 month ago
-
How to choose Towel Rails for an ASHP
1 month ago
-
How to Zone with a Single Room with UFH
1 month ago
Currently viewing this topic 3 guests.
- 26 Forums
- 2,242 Topics
- 49.9 K Posts
- 606 Online
- 5,903 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson can you post an example of your automation plea...
By Grantmethestrength , 12 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 51 minutes ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 56 minutes ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
Yep that's it, but the current design would re...
By DREI , 1 hour ago
-
RE: Buying large amp bidirectional RCD and RCBO
There won't be many RCBOs with a 100mA trip rating beca...
By Transparent , 2 hours ago
-
RE: Electricity price predictions
Because its what the investors demand, simple as that. ...
By JamesPa , 2 hours ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 4 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
@dgclimatecontrol I only have 1 cylinder and I can conf...
By Ecoste , 5 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 5 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Midea has introduced the R290 series, which...
By Tasos , 6 hours ago
-
RE: Grant Aerona 3 and Drayton system questions
Good man/woman that plumber! Very likely....
By JamesPa , 6 hours ago
-
RE: New build installation query
@paullacey Hi I have managed to save the fil...
By JamesPa , 7 hours ago
-
Thanks for the response @batpred Your conversational ...
By Transparent , 9 hours ago
-
RE: What should we do with our Aga?
One slightly off-the-wall suggestion is that, if you li...
By Majordennisbloodnok , 10 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
If you paid for any of the assessments try asking for t...
By JamesPa , 1 day ago
-
I've created a separate post here, wondering about radi...
By DREI , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@ecoste, @walnut-tree-cottage these are both great piec...
By JamesPa , 1 day ago
-
RE: Solar inverters - where does the energy go when clipping?
You will, of course, check the dimensions and weight be...
By Transparent , 1 day ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
17l/min is enough for only 6kW at 5C DT, not surprising...
By JamesPa , 1 day ago