Air in the heating system
Our underfloor (ASHP powered) system has air in it. I can hear water trickling through the pipework at night and every day canbleed air out of the heated towel rails.
I know this makes it less efficient and have an engineer visiting next week, hopefully to rectify it. He has already been once and identified that the pressure gauge on the heating expansion vessel isn't working so always shows zero pressure instead of what I'm told should be about 1 to 2 bar.
With the current very cold weather our electricity consumption has of course gone through the roof and I'm hoping to see some improvement from fixing this.
But how does the air get into the system? How do you eliminate it? There is no sign of fluid leaking out but the plumber thinks it should be topped up via the fill tube (which the installers helpfully put downstairs while the pressure tank and other pipework are upstairs!).
Grant Aerona HPID10 10kWh ASHP
Few ways. Easiest is to isolate return manifold, close all zones (loops) but one and install hose to return drain point and open. Then open filling loop unit air clear. Repeat for each loop.
seemingly very few installers know yet alone do this
These guys have "deaerators" that can remove microbubbles that are left flowing around a system, might improve matters. They also sell exotic "vacuum degassers" I think those need electric mind, to directly remove dissolved gasses.
Never used any of them myself, we have conventional rads with bleed valves all over the place- every time I have ever had the system emptied and refilled it has taken weeks to settle down and stop gurgling. When I refill it I wish we had a clever pump that jerked on/off as some now do to help clear air locks. It's only done every 5 years/never, so no worries. I've trawled around the website looking for pressure versus flow on them, they just say "low pressure drop".
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 122 Online
- 3,393 Members
Join Us!
Latest Posts
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 23 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
Hi all, thanks for your help. The installer has confirm...
By Rikiarn , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
Just in case anyone is looking at Planet Atmo- we've ma...
By benson , 2 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 2 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 3 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars….
Toodles.
By Toodles , 3 days ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 3 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 3 days ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 4 days ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 4 days ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 4 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 6 days ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 6 days ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 6 days ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 7 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 7 days ago