@allyfish the system was flushed maybe 6-8 months before the install happened. I did ask at the time and the installer said the system was already clean and didn't need another flush. Maybe another example of cutting corners
When the heating started after the summer this year I got an FU fault a couple of times but has been good for a while now. This is when Grant said there is a flow issue somewhere in the piping.
Posted by: @soniksYou just reminded me I have a pizza oven thermometer which I can use
In my lounge
There are 4 radiators. I took the readings from
2m K2 radiator new - top : 32c, bottom : 24.8c
1m K2 radiator new - top : 34.1c, bottom : 29.8c
1.6m K2 radiator new - top : 22.3c, bottom : 17.1c
low height 43cm double radiator existing - top: 35.7, bottom : 32.9
Did you get warm water to the cold radiator? If not then remove the TRV actuator head and ensure that the valve plunger moves freely.
@allyfish No I don't have a flow setter/guage AFAIK - where would it be installed normally.
The pump is a Wilo 25/80 pump attached image. Can't see the model number anywhere but I think it may be a Wilo-Yonos Pico pump. I think it's on the highest setting at the moment.
I do agree with you the flow rate needs to be resolved first before balancing. From the discussions the discussions on the forum perhaps it is a piping issue as the property has been extended a couple of times by the previous owners and I wonder whether the piping has been done properly. Are there are any heat detectors that could show where the pipes are layed if I turned on the heat pump to the max and potentially give an indication of the pipe size based on the heat emitted from pipes.
There is a Mag one filter installed. How can I tell if the heat pump heat exchanger is blocked?
@soniks thanks for that, the in-built pump in the Grant Aerona 17kW can provide 50l/min at 5m head on the highest speed setting. A Wilo Pico RP25/80 in series with that can provide 50l/m at 3m head. (25/80 is a common fixed speed CH pump badged up by various manufacturers) Pumps in series raise the head, so in combination you have 50l/m at 8m head. That's more than enough pumping capacity. I would recommend a specialist heating engineer is brought in to investigate further.
Flow gauge and flow setter. For properly commissioning a Grant ASHP setting the flow is essential. The grant units have fixed speed pumps and no internal flow sensing, so they rely on the installer commissioning this to suit the make/model and design water leaving temperature. If you don't have one installed I would recommend fitting one. You can DIY but it's probably a system drain down job.
The condition of the MagOne filter might give you some idea as to how clean or not your system pipework is. You can open that up for inspection & cleaning without drain down, but stop the system first. If there's a lot of build up of black sludge on the magnet and/or evidence of other contamination, then a power flush of the piping system may be a good idea.
You can't really check the plate heat exchanger without a full drain down, disconnection of the outdoor unit flow and return pipes, and reverse flushing to see what comes out! A competent heating engineer who has power flushing equipment could do that for you at the same time.
When the system is being power flushed the engineer would be able to look further into the circuit pipework for any obvious issues.
Sorry I should have clarified in my last post - reliable heating engineers that covers the Surrey region
Posted by: @soniksSorry I should have clarified in my last post - reliable heating engineers that covers the Surrey region
Adam Chapman of heatgeek is based around Guildford, he should be able to advise on any local engineers who are competent.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@derek-m I measured the temperatures on the radiators again the I can see the following readings. Slightly higher than before without changes. Perhaps it's because it's not as cold at the moment.
Top Bottom
K2 1m 36.7 31.1
K2 1.6m 33.1 25.5
K2 2m 31.2 23.9
Out of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
Posted by: @soniksOut of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
Over the last 24 hours, mine have ranged between 28 and 38 degrees while heating. If you set the flow to 50, I expect at least one radiator should be achieving near that (45+?) at the top. There's a discussion on here somewhere where people with temperature sensor guns pointed them at their radiators, which you might find by searching.
Posted by: @soniks@derek-m I measured the temperatures on the radiators again the I can see the following readings. Slightly higher than before without changes. Perhaps it's because it's not as cold at the moment.
Top Bottom
K2 1m 36.7 31.1
K2 1.6m 33.1 25.5
K2 2m 31.2 23.9
Out of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
If the temperature of the water coming out of your heat pump is in the region of 50C, then you should be seeing temperatures not much below that at the top section of your radiators. If you are not getting such temperatures then there must be some mixing and cooling of the water within your system. If that is the case then it can seriously reduce the overall efficiency.
I would suggest that you measure the temperatures on the pipework around your system to try and locate any problem areas.
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 52 Online
- 4,531 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
As you say its poor either way. Can you start a n...
By JamesPa , 8 minutes ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 2 hours ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 3 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
The current FAQ says it's not compatible with existing ...
By Old_Scientist , 3 hours ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 5 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 19 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@terry1812 Oh Good! Pleased to help if I can! Regards, ...
By Toodles , 1 day ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 1 day ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 4 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 4 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 4 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 5 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 5 days ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 5 days ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 6 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 7 days ago