Thanks Craig, now lower the LWT setting to 30C and see what happens to how the system operates.
Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Posted by: @craig1980Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Hi Craig,
I'm afraid that I have run out of suggestions.
There appears to be something fundamentally wrong with your heat pump, and/or how the system has been installed. The only thing that I can see that appears to be incorrect is the Teva_out temperature reading of -50C, which could possibly be due to a faulty or disconnected temperature sensor.
I would suggest that you e-mail Samsung Technical Help and ask them why your system may be operating as it is doing.
In the meantime set your system back onto WC mode and adjust for the required indoor temperature.
Â
Okay, many thanks for all of your help. I'll update if I find anything from Samsung. Thanks again. Much appreciated.Â
Interestingly, when I put the settings back to WC I get error E121. Upon looking this up in the manual it saysÂ
"Short-or open- circuit error of the room temperature sensor of the zone 1 indoor unit (detected only when the room thermostat is used) Error source - Hydro unit.Â
Posted by: @hughfPosted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
@hughf Please see the topic about Samsung install and buffer tank
https://renewableheatinghub.co.uk/forums/postid/11342
Freedom Heat Pumps claims a buffer tank is required to be within the Samsung warranty, even though the manual implies otherwise and Joule make a pre-plumbed cylinder without a buffer tank.
Â
@mike-h Ah yes, good old freedom. I’d trust the instructions from midsummer wholesale personally. I know that GH was always getting 911 errors (low flow) on his early installs, so they probably mandated a buffer to deal with that issue, allowing the primary pump to run at full speed to charge the buffer.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 114 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 4 minutes ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
Just thought id add an update just in case it helps in ...
By LCH07 , 35 minutes ago
-
RE: Octopus tariffs - a quick comparison
Absolutely. That’s one of the reasons I wouldn’t want t...
By Majordennisbloodnok , 37 minutes ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
I do wonder how many of the 'failed' systems that are r...
By JamesPa , 45 minutes ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 Oh my, thats a lot of pumps and is certai...
By ASHP-BOBBA , 57 minutes ago
-
RE: Renewables & Heat Pumps in the News
I'm still going through the latest ENTSO-E report on th...
By Transparent , 7 hours ago
-
@editor The season to start inviting prospectives to ‘V...
By Toodles , 7 hours ago
-
@bontwoody how long has it been now since you started t...
By Mars , 7 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 7 hours ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 9 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@darrell-p There's another new Forum Member, @wully who...
By Transparent , 9 hours ago
-
RE: Forum updates, announcements & issues
We've had a slight glitch with our security software fo...
By Mars , 11 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
If you do suggest you consider repurposing it as a 2 po...
By JamesPa , 23 hours ago
-
RE: Say hello and introduce yourself
Fully agree with @cathoderay. My journey took 2 years ...
By JamesPa , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Tim, Yes ChatGPT thought I could get another...
By Mike Patrick , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
No problem, @richdorm; glad it helps.
By Majordennisbloodnok , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I do already have the same basic setup, all room influe...
By cathodeRay , 1 day ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK. You dont say whether it is from the feeds to/from ...
By JamesPa , 2 days ago