But at the beginning of the 8 min cycle they are both within 0.5 degree of each other at 22
Outside unit heat pump fans run for around 5 mins then it's quiet until 8 mins and 20 seconds then it starts again.Â
I will have a look at the data and get back to you tomorrow.
In the meantime, with the system running, measure the temperature in the central section of each radiator at both the top and the bottom, along with the relevant room temperature.
Posted by: @transparentLet's label a few bits:
-- Attachment is not available --
Am I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
Â
@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
Did you measure and record the radiator temperatures?
Posted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @craig1980@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
-- Attachment is not available --
The white one is the expansion vessel for the domestic hot water (from the unvented cylinder) and the grey one is the expansion vessel for the heating/ashp circuit.
As you have an unvented cylinder, there is no need for any tanks in the loft, and also no need for that shower booster pump. I'm not sure why you still have those in your installation.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Below is a link for the controller instructions. Select the home screen and monitor the outdoor temperature whilst your system goes through its cycling process.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 95 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 10 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 13 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 16 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 18 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 18 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 1 day ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago