My experience with ...
My experience with the Selpos Mason DIY kit
12 Users
76 Reactions
49 K Views
How do you feel about using combustible ply inside a battery enclosure @misterb ?
You're 'pushing' the boundaries a bit with using Melamine to provide a level base for the cells.
But at least it's recommended for use in kitchens and can withstand a boiling pan being placed on it at 100degC
I very rarely have high currents passing through my LiFePO4 batteries.
I'm confident that they 'run cold' under normal operating conditions, which I classify as 100A import or export.
But I have had overheating due to other conditions
  • a 125A-rated MCB (trip) which opened its contacts due to thermal overload at a steady current of only 80A
  • a bolt connecting a 600A copper busbar to a micro-resistance being used for current measurement. Thermal cycling had loosened the thread
  • a 6mm nut connecting a 25sq.mm cable, which I'd forgotten to check with the torque wrench when I'd changed a BMS
All of these items can also be found within your Seplos case. 😮
For this reason I generally use cementitious board if the sheet is going to actually be in contact with the cells.
And I keep plastic parts to a low-mass.
They will usually melt at around 200degC, but they'll be small enough parts not to cause a run-away fire.
The PVC tape I suggested would fall into that category, although I'd use a non-combustible tape if I had one to hand.
The problem with cementitious boards is that they are generally sold in large sheets (2.4 x 1.2m) and that they tend to be brittle.
It's great, provided you're not using it structurally.
The exception to this is Fermacell, which is a wall-board.
That can be used structurally... because I build walls using it (instead of plasterboard) in high-traffic areas. 👍
(@misterb)
the ply wasnt meant to be in contact and certainly not left in situ, it was potentially a way of stopping anything touching the terminal connections while assembling the top part ...
and whilst i obv wouldnt want an issue, the inverter, batteries etc are in an outside utility room far enough away from the house, if there ever was an issue as the fire loading isnt particularly large and wouldnt constitute a significant life threatening risk, if anything did happen.
everything can be isolated from within the house ...
thanks for your comments re overheating and i hadnt planned checks every now and again, but its certainly something i will consider AND i have just bought an double pole 100A circuit breaker to replace the single isolator i fitted originally (see, i do listen and take things on board LOL 👍 )
This post was modified 2 years ago by MisterB
My batteries are also in an (unheated) plant-room.
I have four other doors to the outside,
but I've also invested in a couple of these in case I make a mistake whilst actually working on the installation...
(@chickenbig)
Posted by: @transparent
Quick question; what is the best practice around how frequently these bolts/nuts should be checked? Once a year? The connections can undergo many thermal cycles a day (turning oven on, showery weather, etc) Or should we be considering some sort of thread locking solution to prevent it working loose?
The question might be quick @chickenbig but the answer open-ended, both in time and depth of physics 🤔
May I remind readers here that I'm doing R&D.
So I 'experiment' with things which I wouldn't propose here as being 'good practice'.
As far as I can tell, the connections which we make to our battery cells, fuses BMS units and inverters don't work themselves loose due to thermal cycling.
Those which I've had to 'attend to' have been due to errors on my part, such as an improperly crimped terminal lug.
The bolts I referred to above are on a micro-resistance link which can be seen in this photo
This is an off-the-shelf shunt supplied by a reputable manufacturer in China, and I've used the stainless steel M10 bolts which it came with.
The shunt produces a 75mV drop across it at its maximum current rating of 300A.
That makes it 0.0025ohms (2.5mΩ or 2500μΩ)  - hence the term 'micro-resistance'
and that means it produces 7.5W of power per 100A current.
You can see the visual effects of the heat which has built up during my tests, all of which are well below the rated 300A.
There is striated discolouration in the centre of the three copper-alloy blades which provide that resistance,
and the yellow sense-wire at the top has a small amount of black residue protruding from the heat-shrink sleeve where it joins the crimp connector.
That is almost certainly charred insulation from the yellow wire, which is specified for 80°C.
I had assumed that the large mass of copper bar to which the shunt was bolted would adequately dissipate the heat.
the lower busbar is 25x3mm (75²mm cross-sectional area)) and the upper one 25x4mm (100²mm).
But as the shunt heats up, the stainless steel bolt threads expand at a lower rate than the threads I've cut into the copper.
That increases thermal resistance where the shunt meets the copper bar, meaning that the shunt itself gets hotter.
There are two possible solutions which immediately present themselves:
  • fit an M10 locknut where the bolt protrudes behind each busbar, thus clamping the ends of the shunt more securely to the copper
  • replace the stainless steel bolts with a pair made of brass or copper
That doesn't directly answer your original question...
... but it needs addressing here because this thread has several contributors who are planning to link up multiple batteries, each of which might be expected to deliver 100A under normal operating conditions.
This post was modified 2 years ago 6 times by Transparent
(@chickenbig)
As we are also mentioning inverters to use with the Mason boxes, and I kept on mentioning Sunsynk, I thought I would mention my current experience as one has been installed in a relative’s house.
  • The inverter manual is pretty vague about key safety features such as earthing of the case using an external fixing (and makes no mention of the earth bar inside the case).
  • Key workflows such as the pairing of logging stick and inverter to a “plant” do not document possible errors. This may be more of an “installer competence deficit”.
  • Sunsynk are currently undergoing a cloud change where the world is being divided up into regions. This creates problems as I can have an account in region 2 which can not be connected to an inverter in region 1 … the name of the account does not make the namespace (I.e. region) obvious.
  • The logging stick broadcasts an always-on Wi-Fi network with password ‘12345678’. Well, I say always on, but once it did stop broadcasting (or doing anything) until restart, I guess it had probably hung due to the intermittent internet connection (see next point).
  • The inverter does not play nicely with (TP-link AV600) power-line Wi-Fi extenders when in “zero export” mode, but not when there is a surfeit of PV. Presumably the harmonics are bad when trying to clip the power exported to the grid.
  • The touchscreen user interface does not have great labels, so with something like “Zero Export” activated it is still possible to export 5kW (if that is coming from solar). Naming things is hard, but 0 != 5000.
  • I have found that some settings keep on getting reverted (“Use Timer” and “Prioritize Load”) after a few seconds or tens of seconds. This is in the absence of the logging stick (and so internet connectivity).
  • I have also found that the charge/discharge schedule spontaneously gets strange entries added (to charge from grid and generator to 100%) when there is internet connectivity.
  • It is not clear to me how or why export or import decisions are made; perhaps this is lack of knowledge on my part. For instance today I have had a situation where a 100% full pair of batteries (with 200A discharge enabled) was not used to power the house, despite having the “Priority Load” box ticked. Instead power was drawn from the grid.
That detailed feedback needs sending back to SunSynk.
They are very keen to establish a good reputation in the European market.
One question I raised with them resulted in a phone call from a senior engineering manager in South Africa - impressive!
They are aware of inconsistencies in installation practices and regulations between the countries they export to.
If you look at the installation diagrams, you'll see that there's a mixture of different wire colours being used(!)
That's why it's also difficult to specify the 'correct' way to provide an earth.
Here in the UK we have two different earthing arrangements for EV-chargers, for example.
So it's tricky for Sunsynk to write a definitive manual.
They really do need this level of feedback. In the long run it helps everyone.
(@chickenbig)
For me the video on https://www.sunsynk.org/post/battery-bms-and-restart-shutdown-voltages says something deep about how the UI and core software interact. There exist 2 firmware versions on the device and one on the logging stick, so somehow communicate through an interface. The video (from 2020) states that startup and shutdown battery voltages can only be set when in non-lithium battery mode, but still should be set for lithium. It suggests the interaction is via a (super-)set of registers, only some of which are (modally) displayed but all of which can have an effect on the behavior. That is the UI software is a skin over the top of the MCU software (which is more carefully controlled as it appears to be specified for G98/G99/G100 approval), and displays a subset of active values.
I suspect that the lack of using battery power to support solar is a result of this hidden configuration since it stopped working after I tried limiting grid power (per G100 feature … although it was not password protected, unlike the G100 declaration).
Although trying to debug software can be an interesting activity, it is getting too close to actual work (and without the benefit of access to the source code, API documentation or monetary reward).
Posted by: @chickenbig
That depends on when SunSynk wrote that code.
A video from 2020 can't refer to inverter controls which will comply with later regulations.
Our UK regulations are not static; they evolve over time.
For example, you can read the latest  G100 Issue 2, Amendment 2 regulations from the Electrical Networks Association
and note that this now applies to the import of electricity to charge off-grid storage batteries.
However, there is no matching form or application guidance yet available on the customer-facing website of my DNO. 🤔
This makes it very difficult for manufacturers, suppliers and installers of inverters which are designed to manage off-grid batteries.
I don't know of any such inverters which have been designed with a compliant Customer Export or Import Limitation Scheme (CLS)
because the customer could readily circumvent the import limitation by reconfiguring the inverter from an App or front-panel LCD menu system.
Nor do I yet know if the G100 Amendment 2 regulation is retrospective to sites where batteries existed from an earlier date.
It's possible that SunSynk are attempting to comply with the new G100 release by making changes to their control/management software in the cloud, without needing to re-flash the firmware within existing inverters.
But to do that they'd need to separate the world into different zones.
You don't want the European-based regulations being applied to Africa, China or Australia for example.
And that's what you've just complained about... because it isn't properly implemented.
This is an issue which really needs raising with the House of Commons Select Committee on Energy.
They want to know if the UK statutory bodies and Government are sufficiently encouraging new technology which will help achieve Net Zero
Update:
Earlier in this discussion @chickenbig and I were recommending to @misterb a manual transfer switch (MTS) and I posted a photo of a couple I have here.
I've now come across a much cheaper/smaller MTS from the Chinese Manufacturer Earu.
It too is double-pole, and thus switches the live and neutral simultaneously. That's important when using off-grid batteries.
Better still, it has a central position where both inputs are disconnected.
That provides reassurance that the switch really does offer Break-before-Make operation.
(@vaugi)
I agree the instructions are pretty bad, and worse, not updated correctly over time I think (different screenshots vs reality).  Did the inverter get installed by an approved Sunynk installer out of interest?  I did my 5kW with my own electrician, but it does look like Sunsynk are making it hard for self installs by making it hard to contact/discuss anything with them - I haven't yet tried, but I need to about my new 3 Phase due to a problem setting it up as AC-coupled, and all postings on the web seem to suggest tech support is for installer not end use user only.
One other clarification  of your points, are you accessing the inverter via the Sunsynk app, or directly on the display?  I haven't got access to settings on the app as it's in end user access level at the moment and keep meaning to request upgrade to installer level.
I haven't had any issues with the Wifi install, or settings getting reverted, which is why I am checking if you are using the APP or direct.  On the touchscreen you need to make sure you press OK each screen to save settings, otherwise it won't save.
Also - so we have a reference, what is the set up/use case for the inverter - does it have solar attached, or just battery?  Will it be used on TOU? How is the inverter set up - with a grid and load connection, or just grid?
The "system mode" screen is probably the most important, yet the manual description is very vague and hard to understand.  There is confusing language, and inter-changable "Load" is used to mean the loads on the Grid connection, but also the meaning only the Load on the "essential Load" connection.  I think, but not 100%, that the Priority Load means the "essential load" connection.  I have it unticked on my system.
The other thing to check is, if you are using the timer function, is that the timeslots start at midnight and don't straddle the day (e.g. don't use 23:30 to 05:30 for Octopus Intelligent, and that there are no gaps.
Perhaps take a few screenshots of the pages - if you have "Use Timer" selected, perhaps you also have a time slot that has "Grid" ticked with 100% SOC, which would mean that the battery would charge until full in that timeslot and not discharge until the next timeslot that has Grid unticked and <100% SOC.
Below is a copy of some text from a Sunsynk facebook group I saved as I thought it was a really good explanation - although please be aware even in this the terms are different to the newer firmware:
The timer screen can be quite confusing at first but it is quite simple. It only works if "use timer" is ticked. You can't sell unless use timer is ticked as well.
Apparently if its not ticked your battery will fill to 100 with solar and stay there and only get used in a power cut. So UPS mode.
So how does the timer work?
Each slot defines a time period, you want the periods to join up to cover the 24hr period. START YOUR FIRST SLOT AT (OR AFTER) MIDNIGHT, NOT BEFORE. Don't have your first slot starting at 11pm and have it span over midnight.
The power value is the size of your battery charge/discharge rate (limited by inverter size) and you don't normally change it. It seems it may only limit power coming out of the battery, not going in
The Charge Rate on Battery Settings can be used to slow your battery charging however. More on that at the end.
The SoC (State of Charge) is the amount of charge you want in the battery in that time slot. Set a value 20% to 100%.
Important. Once your battery hits SoC in that time slot, the battery is NOT used again until the next time slot. However, it would be used if there is a power cut and solar will always try to charge to 100% regardless
The "Grid" tick is whether you want to charge the battery to the SoC from the grid should it be below that SoC when the period starts.
The "Gen" tick is for generators. I will not cover that here.
Don't forget to tick Grid Charge in Battery Settings if you want to charge from the grid at all
When a period starts the inverter will use the battery if it's above SoC until it reaches the SoC. If it's below the SoC already, it doesn't use the battery in that period at all. If it's below SoC and you have ticked Grid Charge it will charge until it reaches the SoC.
So as an example if you get cheap electric 00.30 to 7.30am (eco7) you would set the first slot to 00.30 to 07.30, SoC 100%, Tick Grid. In the first few hours it will charge the battery to 100% and stop. It will continue to use the grid until 7.30am, leaving the battery at 100%, while the electric is cheap. At 7.30 it will revert to using the battery if the next slot has a SoC less than 100%
If you expect to have plenty of solar the next day (a guessing game!) you may want to reduce that 100 to 80, 70, 60 because you want to leave space for excess solar. In mid summer you may even set 20% or untick grid charge altogether to leave plenty of space. There is little point moving 7.30 earlier in summer as solar would be used in preference to the grid anyway.
You would set all your other slots to 20% and NOT Tick Grid. Now it will use battery all day when there is insufficient solar. It will stop and go back to the grid when it hits 20%. Solar will however be keeping it charged, so you may never get close to 20%. At 00.30 it will take the battery from 20 (or whatever) back to whatever you set
In SA where there is no notion of cheaper rates at certain times and you want your battery full at certain times to cover load shedding you might charge in the hour before the power cut just in case solar hasn't done enough.
The cycles you create will depend on your usage.
The new Flux tariff at Octopus may want a full battery charge 100% between 2am and 5am from the grid. Then you would set all other slots to 20% and export all your solar. Between 4pm and 7pm you might want to sell a portion your battery power back to the grid. More on that later
Solar will always fill the battery with surplus energy until it reaches 100 and then it will export if you have set that up (export solar). If your battery is full and you don't export the inverter will actually draw less from solar, it will only draw what you are actually using
Priority battery. This prioritises Solar to recover back up to SoC target. It then looks as though it supplements the load, but battery will stay at SoC target until Solar greater than Load. The behaviour once at or above SoC target is the same as Priority Load.
Priority Load seems to do what you expect. Solar goes to the house first and the excess goes to the battery. Most tick this option
Lastly if there is a power cut and you have "islanding" configured, the battery will always drain to 20% and then shutdown, these settings are ignored. It uses the values on the battery settings page. More on that later
Grid Trickle is for some pre pay meters that get upset if you export anything. If you don't have one you can set this to zero
The other options that can be confusing are the Selling First and Zero Export. These only apply to the battery, not solar. The "Solar Export" Tick handles solar exporting
If you select Selling First and enter a value into Max Sell Power (1000 is 1Kw) the inverter will immediately start dumping your battery (including solar if present) to the grid at the rate you set. The dumping will stop at the SoC value for the current time slot and then it will revert to using the grid. This is actually bad if you are on eco7 or flux, grid at peak times is expensive. So keep an eye on it and turn it back to Limited To Home.
Don't forget when you switch selling off, to set Max Sell Power back to the max otherwise ALL your exporting is throttled.
Limited to Home (previously labelled Zero Export) means keep it for your use. The Zero Export - Limit to load, option means only use battery power to send to the "load". That means only ever use the battery for the essentials circuit, the rest of the circuits ALWAYS run from the grid (even though the overview diagram will not show this grid usage). You wouldn't normally pick this option as you would want the battery to be used to power your whole house when there is grid available. It's for people using it as a UPS really.
The is a strange anomaly with Export Solar. If ticked the inverter uses 40w from the grid, rather than solar, when solar is charging the battery. Untick it and it uses 0w. So it's pays to untick if you know you won't be exporting for a while. Don't forget to turn it back on though!
Battery Settings
First there are two values worth looking at. Charge and Discharge Rate. These are set in DC Amps.
A rough guide is every 10A is 500w. So 20A charges/discharges at 1000w and 100A at just over 4500w from what I can see.
You can find your limits on the LiBMS screen on the inverter. It's not shown in the App
So Discharge Rate is simple enough, it limits the amount of power allowed to be drawn from the battery.
Charge Rate is more interesting. You can slow down your battery charge rate across everything. Setting 20A for example would limit ALL your charging to 1000w across all the batteries. (There is a separate Grid Charge Rate which limits grid charging alone). It would also limit your solar charging, so if you were generating 3000w, 1000w would go to the battery and 2000w would be exported even before the battery is fully charged. If you want to export in the morning rather than putting everything in your battery reduce this value. Hint. If you can generate more than you can export, ie. 3.6 inverter, space in your battery at 1pm is very useful and let's you save ALL the solar
Obviously you would need to set this value depending on circumstances like the number of batteries, how low you let them get and how long you have to charge then back up again.
Finally 3 settings on the Battery Settings page that can confuse.
Low Battery is when the alarm (if enabled) would sound. It is also used with the new Low Power mode where the inverter sleeps to re awake when solar is detected
Shutdown is when it stops using the battery
Start-up is when, after you hit Shutdown and it has started to recharge, that the battery can be used to power your house
Typical values are 25, 20, 35 respectively
This post was modified 2 years ago by vaugi
(@chickenbig)
Posted by: @vaugi
Part of the problem was that (unknown to me) the installer set up Octopus Agile integration with zero prices which seems to trigger the charge logic. Don’t quite know why zero prices do that for charge logic. Anyhow, this Octopus integration is only visible from the Connect app or web interface, and gets turned into the System Mode 1 schedule which is pushed to the inverter. So good luck to me trying to find that stuff on the inverter UI (and one has to think about whether there is a race condition in there). This does not explain why some other settings are reverted even when the inverter has no internet connection.
Posted by: @vaugi
I now see that they are not on the approved installer list … guess that is better than being on the not approved list.
Posted by: @vaugi
Solar and battery. Moving to Octopus Flux, if the smart meter works out in the sticks, so hopefully TOU.
The problem with discharging not happening turned out to be related to the charge voltages (float/absorbtion/equalization), but I got to that conclusion by fuzzing the configured values until it started taking energy from the batteries. There is no visibility about why a decision is made by the inverter.
Page 16 / 21