Thanks @hem 

HemMeterbox

That looks like a SMETS1 meter with an Elster (Honeywell) Communications Hub operating at 900/1800MHz for connection to the National Smart Meter Network operated in the southern and central territories by Telefonica.

I like the inclusion of a separate 100A 2-pole isolation switch.
That allows an electrician to work safely within your consumer unit, without needing to break the seal on the Service Fuse.

I dislike what looks like a whole-house residual current detector (RCD) in that location.
Any earth-leakage fault within the house electrics will cause that trip to open, thereby plunging everyone into darkness. Ugh!
You then need to correct the fault, before going outside with a meter-box key to reset the trip. That's unfriendly.

Since your house is supplied from a PME substation, your EV charger must have its own earth stake rather than being connected back to the house earth-block.
The house earth is being provided by a link to the Neutral incomer to the property.

EV Earth types

 

Cars have metal bodies.

In the event of a broken neutral wire between your house and the substation transformer, it's essential that the metalwork can't 'float' upwards.
That would present a shock hazard to anyone touching the car.

ChargerEarthingB

There are 550,000 substations in Britain.
Each year about 300 of these have a neutral fault which requires the DNO to repair it.

So you need to check with PodPoint whether they'd accept a 2-core SWA cable.
The armour would still be connected to earth at the house end to protect against cable damage.
But it wouldn't connect to anything at the garage end.

This post was modified 2 weeks ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
 Hem
(@hem)
Eminent Member Member
59 kWhs
Joined: 2 weeks ago
Posts: 9
Topic starter  

@transparent 

Thank you once again.

Message from podpoint

"For areas where the cable crosses a path or a garden, we require the cable to be laid underground in ducting..

When organising the works, please ensure they follow the full specifications below:

  • The trench needs to be a minimum depth of 450mm except for driveways where depth should be at least 600mm.
  • There needs to be continuous twin walled flexi-duct with a minimum diameter of 50mm for the entirety of the underground run.
  • A 6mm - 9mm nylon rope (draw cable) for cable pulling is expected to be installed in all ductwork for current cabling AND future use/capacity.
  • Yellow warning tape to be placed in trench before being filled in.
Please let us know how you’d like to proceed "
 
I can check about 2-core SWA cable only tomorrow..
Regards
Hem

   
ReplyQuote
(@ianmk13)
Estimable Member Member
1026 kWhs
Joined: 1 year ago
Posts: 67
 

@transparent   If it's a Podpoint Solo EV charger, a quick look at the installation guide suggests it has has a form of PEN fault detection and can be connected to a TN-C-S supply without need of a separate earth electrode.

@hem  Again, if it's a Podpoint Solo EV charger, there doesn't appear to be a wired network option so you will need good WiFi coverage at the front of the garage.  A low voltage two-wire connection back to a current transformer on the incoming grid live supply will also be required, so a cable with integral cat5 core will be useful.  At that distance, I would choose the 6sq mm version. Your electrician will need to register the installation with your DNO and building control.


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
8122 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1354
 

Posted by: @hem

For areas where the cable crosses a path or a garden,

It's not 'crossing' a path or garden except for one point near the back door.

The intended cable-run is mainly along a fence...
which we don't yet know whether you own.

HemPlanA

We only have a plan view to go on, and a photo of the pathway near your back door might help.

I can't see why a cable can't cross between the house and the fence at high level (say 2.5m above the path).
The fence may require a post to be extended upwards. But that could be done using a piece of aluminium angle.
I'd be paying more attention to how the SWA cable gets attached as it crosses that back path.

A thin stainless-steel wire rope could provide the required support.
Go to Amazon and type in Steel Wire Kit; there's loads of possibilities.

Save energy... recycle electrons!


   
ReplyQuote
 Hem
(@hem)
Eminent Member Member
59 kWhs
Joined: 2 weeks ago
Posts: 9
Topic starter  

@transparent 

It is Podpoint Solo3 indeed. 

Thanks once again. much appreciate your help.


   