RE: Heating theory doesn’t match reality

Before calling an Engineer, trace back along the warm pipework until you find the motorised 3-way diverter valve, or do you have two 2-way valves? T...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

Without being able to see how it is actually piped up, I suspect that one pump is pushing the return water back to the heat pump, and hence required f...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

@mike-h The simple way to check if your water pumps are operating in PWM mode is count the number of cables that are connected, if there are two the...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

I'm afraid you wouldn't be offered a job, you are too knowledgeable. Think of what you could do with your £5 million share. 😋

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

Maybe they should have just given the £15 million to Hugh and myself. 😋 I could live with that, how about you Hugh? 😎

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

Yes, the heat pump is the outside unit. Kev ordered some aquarium style thermometers, the details of which your can find in one of his posts. Use a ...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

It would be best if you have a thermometer that can measure room temperature, when place about 1 metre from the floor in the central area of the room....

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

@mike-h Thanks for the information Mike, I having delaying the pleasure of reading through the Samsung manual again, to remind myself of the various...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

Hi Craig, I remember reading that one of the manufacturer's has a controller that limits the restart of the compressor to help prevent short cycling...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

If you still would like some assistance in trying to resolve your problem, then please propose a time period of several hours in which you will be abl...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

Hi Kev, The only real way to possibly discover what is causing the problem is to check how each item of equipment is functioning, disregard the ones...

3 years ago
Reply
RE: 12kw Samsung gen 6. Short cycling

Has the indoor air temperature changed, and are both water pumps running continuously?

3 years ago