@derek-m the 405 # settings. Probably 4052 to get my flow and return temps to have a larger difference or have I misunderstood the job of these settin...
@derek-m so would these actually make any difference to the difference in flow in and out temps if I adjusted them? I'm getting between 3 & 4 degr...
@mike-h I have one on the in and one on the out. I adjusted both. I haven't tried just one.
@derek-m I've found a setting under heat #40** #405* has an option #4052 that sets the inverter pump to run to adjust delta t. Is this a setting ...
@derek-m I have set the pump to speed 2 of 3 so medium speed. I now have a flow rate of 24 l/pm. From what I understand this is the minimum it should ...
@derek-m that is entirely possible. Would also explain the misuse of the description "indoor unit".
I'm on value 2 that says pump 1. I used this YouTube clip to get away from WC. There is probably an easier/better way but this way served it's p...
I was on what I believe is value #4. The one that says pump 3. This was giving the affect of short cycling. I'm listening by the UVC not the outside u...
@derek-m okay, I'll do that later today. Thanks
@derek-m yeah, I'd realised that. Unfortunately my bladder is strong enough to last through the night so I don't need to get up in the early hours yet...
@derek-m thanks again. I assume that is done with the button on the pump itself? I also assume that I should adjust both to the same?
@kev-m yeah, I don't have a programmable temp set back either but quiet mode runs at less power. I can't really find any information on it though othe...
- 26 Forums
- 2,118 Topics
- 46.6 K Posts
- 115 Online
- 4,523 Members
Join Us!
Latest Posts
-
Where can I get these new frb lock shield valves?
Watched the latest homeowners qa and they mentioned som...
By AdamK , 23 minutes ago
-
-
With their balancing process Im pretty sure all rads co...
By JamesPa , 2 hours ago
-
The sad end of my ECO4 installation.
This afternoon I was advised by a charity that was help...
By Dwynwen , 4 hours ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@davidalgarve It should just be recovered by both servi...
By dgclimatecontrol , 8 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 8 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 11 hours ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 12 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
I agree with @morgan. You can turn down the target t...
By JamesPa , 14 hours ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 1 day ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 2 days ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 2 days ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 3 days ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 3 days ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 3 days ago
-
RE: Is this just haze or something more?
@majordennisbloodnok I was giving a talk to primary sch...
By Toodles , 3 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
We had our Tesla Powerwall 3 (and Gateway) installed ea...
By Old_Scientist , 3 days ago
-
Indeed. With a battery its presumably the battery con...
By JamesPa , 4 days ago