Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Thanks for the additional information.
As I say 2 hours to get up to temperature after a long shut off is not totally surprising (albeit that the LLH may well be contributing - we may circle back to that later). However I would initially focus on performance when defrost is occurring which, as I understand it, is when your house is not warming sufficiently (please correct me if I have misunderstood your problem).
Looking at the plot most recently posted, it seems that the system keeps up initially (I can be certain about this because I dont know the target flow temperature, but it stabilises so I presume this is at or around the target), but then there are again extended periods when the compressor frequency is zero and the flow temperature thereafter is a bit all over the place. Why are there extended periods when the FT is zero and what is happening to the room temperature (which I think is the problem) in this period and the OAT.
Im basically trying to find the evidence in the plots of the problem you refer to. If you hadn't said there was a problem the plots appear fairly normal except for the unexplained periods when the compressor is off for an extended time.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi,
I'm saying this from my experience, not as a heating expert:
Your compressor is turned off for too long periods. You may think the UFH is at temp, but low down its cooling. and when its OAT is cold, needs constant flow going through it. I would turn down the flow temp and run it constantly. DT 10 the unit straining like mad to heat the screed. I too though my unit was undersized, but after I turned to flow down and ran it constant, I could keep the house topped up with heat for 8kw an hour produced at freezing (heat loss 11) and the pump had lots more in the tank.
My graphs looked just lie yours when was aiming for a temp that the screed could not get to.
In mild weather, I tend to batch heat a bit more until I get a weather comp that I'm happy with
at DT10, your little unit is putting in over 10-11kw of energy, then is idle or just ticking over for large parts in the day. You need to even this out more
I did think about trying that this year just need to convince my financial voice to try it, as it will be significantly more expensive, it will pull 25% less energy but at 4 times the price
I get where you’re coming from. But I don’t think you’re undersized . You’re trying to cram in all the heat your house needs into certain periods of the day. This is a perfectly reasonable thing to do, but with the nature of heat pumps, you’ll defrost a lot.
Posted by: @davidnolan22Hi,
I'm saying this from my experience, not as a heating expert:
Your compressor is turned off for too long periods. You may think the UFH is at temp, but low down its cooling. and when its OAT is cold, needs constant flow going through it. I would turn down the flow temp and run it constantly. DT 10 the unit straining like mad to heat the screed. I too though my unit was undersized, but after I turned to flow down and ran it constant, I could keep the house topped up with heat for 8kw an hour produced at freezing (heat loss 11) and the pump had lots more in the tank.
My graphs looked just lie yours when was aiming for a temp that the screed could not get to.
In mild weather, I tend to batch heat a bit more until I get a weather comp that I'm happy with
at DT10, your little unit is putting in over 10-11kw of energy, then is idle or just ticking over for large parts in the day. You need to even this out more
Can I just say that this is what I think too, but I was waiting for @gary to answer the questions before being certain about the conclusion.
Heat pumps need to be on 24*7 during the height of the heating season, assuming that they have been correctly sized. The FT needs to be turned down as low as possible (to be done with thermostats, TRVs etc set well above desired temperature). In the shoulder season, or with a well oversized heat pump, batch heating may be possible and may work out cheaper, although there is no guarantee.
Operated this way its reasonable to expect the running cost to be similar to gas or oil, or a little cheaper. If you qualify for OvOs 15p tariff then definitely much cheaper, particularly if you have UFH and so can operate at a max FT of 35C or below.
As a concrete example I am operating with radiators and a max temp of 42C, the heat pump is working out ~12% cheaper than gas. Im buying electricity for it at an average of 19p by using EON Next Drive which gives 7hrs cheap rate at night in return for a 10% daytime price hike. I operate 24*7 without setback or set forward, so I'm not exploiting the overnight cheap rate to any great extent.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @garyhe issue is that the heat pump cannot get to the set flow temperature during the coldest periods
Hello, I confused about why this is a problem for you. Is your house not getting warm enough?
Thanks Bob
Correct it’s designed to 45 at -2C and can’t get to 45C house isn’t cold but 20 rather than 21C
@gary mine was “designed” to 45, bit system can’t get above 36. That bit was nonsense.
from looking at your graphs of one day: you’ve got loads of scope to get more energy into your house, if you want/need to, by changing your control strategy.
Yes the examples I gave weren’t when it was at its coldest that week when it didn’t get above zero and dropped to -4 overnight I don’t have data for then but it was running 24/7
@gary some the trends you've posted show the LWT is at the setpoint. They also show the setpoint is changing and they show the compressor frequency at zero (not running). This makes me think you're running with a control scheme that's changing the LWT to meet a room temperature demand and then switching off when the demand is met. Do you have an EcoDan installed with room temperature auto adapt?
Bob
No not auto adapt running hotter at cheaper times cooler at expensive times. Off is when demand is met on milder days. System won’t run below 32c without cycling
Not sure if you have the defrost cycle and what happens correct. The heat pump reverses the refrigeration cycle not the heating water. The circulation pump runs as normal. Hot and cold refrigerator gases swop roles at the condenser only. So instead of being in heat mode it moves to cooling mode.
So cold water from defrost does not enter the return it enters the flow side. But a big volume of water on the flow side will allow some mixing and less very cold water will hit the radiator. Just slightly cooled water.
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 386 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles If I ever catch myself feeling hubristic I ...
By Papahuhu , 2 hours ago
-
Why? Factor in 85% efficiency for that oil boiler and...
By Old_Scientist , 3 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
I've been watching this with interest as I would like s...
By JohnnyB , 4 hours ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
What the hell. There is exactly one reason to use a h...
By bobflux , 4 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Thanks for such a comprehensive response!!! ...
By errmm , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 9 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 15 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 16 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 1 day ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 2 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 2 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 2 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 3 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 3 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago