Buffers, hot water and cooling
Posted by: @prunusDT according to the ASHP seems to be a constant 3C, either in heating or when chilling the DHW tank as a test (both with the secondary pump set to 1.1m3/h (=18l/min), I should try with it at max speed).
Thats presumably heat pump DT, what about radiator DT and, importantly, temp diff between flow from heat pump and flow to rads (ie temp diff across the buffer).
Posted by: @prunusInstaller's heat loss calculation came in at 8kW, and system has glycol in it.
Interesting, so why did he fit a 12kW heat pump?
Given that installers tend to overestimate the actual house loss may be perhaps 6kW. Does the system cycle a lot even when its pretty cold (say 4C or less?). 8kW can be achieved with single 22mm primaries by pushing the envelope a bit!
Posted by: @prunusI'm not seeing how I can get anywhere near the 15 l/min minimum flow without having a buffer?
15l/min is ~4m/s through a pipe with ID of 9mm. Thats, high but its either perfectly straight or at worst very smooth bends through the radiator, and its short. The water pump may be capable of doing this but 3 off 10mm dia pipes (ie 3 fancoils in circuit simultaneously) and you are well within range no question. If you get fancoils that don't shut off the water just modulate the fan (which may be the norm - I dont know), they will all be in circuit simultaneously anyway.
There is absolutely no point in having the ability to move heat (which is the only thing that min flow rate is about) unless there is somewhere for it to go/come from. Unless you have sufficient fancoils in circuit you wont dump enough heat into the water and so you will get cycling, possibly short cycling, whatever the flow rate. Not sure switching from volumiser for heating to buffer for cooling is going to help in reality because it doesn't change the load
Buffer or volumiser will both equally help with the short cycling, increasing the period but not changing the on/off ratio. However your 50l buffer may not be large enough to make a material difference; with a 12kW system you typically would have 200l+ system volume.
Given the (over) size of the heat pump, and your idea that you can run only a small number of fancoils, you do need to do some calculations, however back of the envelope, about minimum turn down in cooling, likely load in cooling, and the required system volume so that you get a reasonable cycle period for a reasonable hysteresis in the flow temperature. I am guessing it will work out quite a bit larger than 50l + the volume of a few fancoils, given the capacity of your heat pump.
Alternatively work above dew point and keep the rads in circuit so they increase the system volume.
This needs some basic thermodynamic and flow design else you risk having to experiment quite a lot. It may 'just work', but equally it may not.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Currently viewing this topic 1 guest.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 20 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
RE: Boiling Mad: Exposing Radiatorgate
Actually they do. My case is a prime example. Catalo...
By DREI , 3 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
Blunt answer? The 20-year-old gas system was f...
By DREI , 4 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
You can even go as low as 40c flow temp, if you want a ...
By DREI , 4 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 5 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 6 hours ago
-
RE: Midea ASHP – how to set weather compensation
I'm guessing these are the mcs defaults which are likel...
By JamesPa , 6 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 7 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 9 hours ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 10 hours ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 16 hours ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 16 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 1 day ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 1 day ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 1 day ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 2 days ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago
Members Online
No online members at the moment