@transparent thanks - sounds like generally its working correctly. I think the main thing I now need to see is how much we produce with direct sun.
It remains puzzling why last year production was around 40% less than previous years even though it seemed to me above average sunshine in main months.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
I depends somewhat on where you live @tim441 but most of the UK will have sunshine this next weekend.
That gives you just enough time to have an AC/DC clamp meter delivered.
Â
Posted by: @tim441It remains puzzling why last year production was around 40% less than previous years
Two possibilities:
- system degradation, although 40% drop is unusual
- an overall cloud of gloom and despondency covering the UK during the energy crisis 🙄Â
Save energy... recycle electrons!
@transparent ah yes, your final thought seems very likely to be the case. Amazed in that case we produced anything at all!!
on the subject of clamps... it seems the clamp part is AC only in the one you linked? I have found a similar one (that is virtually unused since purchase!). But that's also AC clamp only
Is there any benefit in checking the AC via clamp? in case the meter has gone faulty (unlikely?).
For the DC side I guess i could check the production using the test leads? or find another test meter that can test DC via clamp/jaws....
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441it seems the clamp part is AC only in the one you linked?
Apologies; I'd followed the CPC menu system to find that item, but forgot to check that it had indeed arrived at a suitable clamp meter.
The equivalent one, which does indeed allow measurement of both AC and DC current is this one at £48.
Â
The one I use is made by Aneng, and bought directly from the manufacturer in China using AliExpress for about £23:50 incl carr & VAT:
Save energy... recycle electrons!
@transparent no apologies necessary - I very much appreciate the help and guidance. Its all a learning curve for me!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
That Aneng ST209 is also now available on ebay for about £26-£28, and supplied from UK stock. 🙂Â
I'm still trying to get into the habit of using my clamp meter.
I made a mistake a couple of weeks ago and placed my 'ordinary' multimeter in circuit.
It was correctly connected to the 10A DC Amps range, but I'd forgotten to allow for the inrush-current on the DC-DC converter which was to be switched into circuit.
Here's the result:
Yes, the 10A fuse blew. You can see the glass cracked beneath the circuit board.
However, the fuse only succeeded in breaking the circuit after three tracks on the board had been vapourised.
Save energy... recycle electrons!
Posted by: @transparentThose figures for a (light) cloudy day sound about right to me.
I generally assume that such conditions will decrease panel output to around one-seventh of that obtained under full sun.Not having monitoring equipment is an issue which regularly crops up on this Forum.
It applies to almost every type of technology being installed by 'professionals'. 😒ÂNot only does it make life difficult for those, like you, who are now trying to report whether you may (or may not) have a problem
... but it also reduces the knowledge-pool on energy matters within the wider population.It seems odd to me that MCS fail to make adequate monitoring a mandatory part of installations by their accredited members.
There is a simple answer, monitoring costs money, and has to be installed and commissioned by someone who knows what they are doing, which I feel may be almost impossible. 🙄Â
Â
Posted by: @transparentHere's the result:
Yes, the 10A fuse blew. You can see the glass cracked beneath the circuit board.
However, the fuse only succeeded in breaking the circuit after three tracks on the board had been vapourised.
ouch! 😱 🤬 😬 Â
Â
Â
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@derek-m I am pretty sure it is with optimisers on all panels. However its not entirely clear from paperwork.Â
There is a small amount of early morning shade from a chimney to East and significant shade from (say) mid-afternoon from neighbour trees to west. So I'm pretty sure optimisers were required.
For the number of strings would we be able to tell from the number of DC cables entering inverter? There are 2.
Â
If you have two cables it could mean that you have two strings. The reason I asked is that your annual output is approximately 60% of expected, which could equate to energy being received from four panels in full sunlight, whilst the energy from the three sunny panels plus one shaded panel has been lost. How technical are you?
Â
Posted by: @derek-mIf you have two cables it could mean that you have two strings.
For that size of array, I strongly suspect that each 'cable' is in fact a single 4mm^2 wire.
Two wires equals one string.
Â
Save energy... recycle electrons!
@derek-m understood... I guess its possible .... but lets see the output on a sunny day as that should help as well.Â
I'm not an electrician! But have a moderate understanding I would say through experience etc. Did you have a specific thought on a further test?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
-
Plug and play solar. Thoughts?
2 weeks ago
-
Cleaning solar PV panels? to increase output
3 years ago
-
PV without battery storage?
4 years ago
-
Solar PV quotes - 4.9 kW system but 3.6 kW inverter?
4 years ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 576 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
@petch Same with me, I had to insist and taking a le...
By MK4 , 12 minutes ago
-
RE: Tell us about your Solar (PV) setup
Since you seem to quite thoroughly investigate every st...
By MK4 , 1 hour ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
Well I've had an interesting few days and would like to...
By giganto , 13 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Yes, here's mine. From the service manual parts numbers...
By bobflux , 17 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
Thanks for sharing your observations, both of you. From...
By Jonatan , 17 hours ago
-
Had to learn the hard way 🤣 now I'm sharing T...
By bobflux , 17 hours ago
-
RE: Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Im assuming from your original post that hysterisis ref...
By JamesPa , 18 hours ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 20 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 21 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 1 day ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 1 day ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 2 days ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 2 days ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 2 days ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 3 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 3 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 3 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 4 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 4 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 4 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 4 days ago