PV inverters seem to interact
On 26th Jan I had my faulty loft PV inverter replaced. I opted for a Solis 1.5KW as it's the same as I installed myself on a garden array 2 years back. The next day, about 8:30am the mains tripped on earth leakage. I reset it and everything was ok. Next day, the same again, and the penny dropped. I examined my weatherstation logs for solar intensity and sure enough the trip was just at the point the inverter started to export.
For 10 days now I've been trying different combinations of isolating supply loops to home in on the problem.
I'm now 99% sure that the problem is some sort of interaction between the two inverters. If I unplug the garden inverter from the mains there is no morning trip. Connect it and there's a trip. And when it trips, if I reset it straight away it usually trips again 5 minutes later when the loft inverter starts exporting again. If I reset it a second time it stays reset. The garden PV array has quite a lot of side shade so almost certainly starts to export later than the roof PV.
The fact that the inverter is fine on the second trip reset implies it's not a high residual earth leakage issue. To be sure, I've isolated the garden cable run (underground armoured) and unplugged everything and checked E-L and E-N resistance - no obvious issue.
Does anyone have any bright ideas?
Thanks
I suspect @transparent might 😀
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Thanks for raising this issue @geo3geo
I've been investigating tripping issues with a set of inverters by Growatt for several months.
We are not alone. There is a similar report over here on the well-respected DIY Solar Power Forum, which is useful because the responder is from the UK and refers to the different types of trip we have available.
We have
- MCBs (Miniature Circuit Breakers) for over-current protection
- RCDs (Residual Current Disconnector) for earth-leakage protection
- RCBO (Residual Current Breaker with Overcurrent) which combines both of the above features in one unit
I'm going to insert here a table showing the different categories of RCD which are presently recognised/approved for UK use,
because we're likely to need it shortly:
Posted by: @geo3geoThe fact that the inverter is fine on the second trip reset implies it's not a high residual earth leakage issue.
I don't think we can conclude that... especially this early in the discussion!
In my case I'm presently using 3x Growatt SPF5000ES (off-grid) inverters fed from a an RCBO rated at 40A, curve-C, and 30mA leakage trip level.
Adjacent to this is an RCBO at 32A, curve-C, 30mA leakage, and supplying a Growatt (grid tied) MIN3600TL-XE inverter
My inverters are all within a 2m cable-run of those trips in the consumer-unit.
Please note the level of detail I'm giving: It matters!
And note also that the SPF5000 inverters use internal transformers,
whilst the "TL" in the model number of the grid-tied inverter stands for "TransformerLess".
Can you please share a similar level of detail on your hardware?
Save energy... recycle electrons!
My inverters are Solis 1.5kW Mini S6 Single Tracker and in the specification is states
Topography - transformerless
The roof inverter is some 10m from the consumer unit, the garden one is about 50m. I've been in this house for 30 years and the consumer unit and earth leakage trip is at least that old. It's ident is Crabtree 63A, 30mA, 2 pole, BS5293
Let me know if you need any more info.
Here is this morning's log for interest:
Mon 12th Feb, garden loop MCB closed, Garden PV isolator closed, garden inverter connected - Earth leakage tripped at 8am. Immediately opened garden loop MCB and reset the RCD. Then closed garden loop MCB, no trip.
Is that Crabtree RCD protecting a number of circuits @geo3geo ?
When it trips out, what else gets affected?
Ignoring the legal aspects, how competent are you on wiring issues?
That would help me to understand the level of detail I can refer to.
Save energy... recycle electrons!
The RCD is protecting the whole house. So when the RCD trips everything goes. The attached image will explain. Solar MCB is for the roof PV, garden PV on the garden spur.
Re. competence I'm not an electrician, not that familiar with regs, but do have a degree in Elec Eng.
An electrical engineering degree is more than adequate for this discussion @geo3geo 🙂
Is this perhaps the moment to consider a new consumer unit?
It looks like the left-hand three MCBs have no earth-leakage protection.
So a faulty cooker would kill you before the trip contacts opened. 😖
Consumer Units are surprisingly cheap....
... and especially so if you buy them pre-populated with a number of different trips.
Have a look at the website for TLC - a trade supplier who also sells to end-users and will deliver direct to you.
To give you space to experiment with the connections to your inverters, what about asking Sparks to place those trips into a separate enclosure with its own DIN-rail.
That could in turn be supplied from a 'standard' 32A MCB in the main consumer unit.
You can then have that secondary enclosure isolated whenever you want to try a different combination of RCD and MCB to link to the two inverters independently.
Save energy... recycle electrons!
@transparent The unit you highlight is certainly cheap. Thanks for the lead. I see the RCB is type A which isn't transient resistant. Could it be that all I need is a transient resistant RCD? I think it's safe to assume is the present Crabtree RCD isn't transient resistant.
I read somewhere that the RCDs age (whatever that means) and should be replaced anyway at some point. Do you know if there's substance to this?
And maybe I need to make proper provision for my EV 13A outside charge socket, which is currently a spur off the downstairs sockets loop. The spur is fed via a 2 pole 16A RCBO. From what I read, EVs ideally need a type EV RCD, to cope with DC and transients.
And I'm still looking, medium term, at the possibility of an ASHP with battery storage to get lower running costs. The battery would have its own inverter, the prospect of adding a 3rd inverter given what I'm experiencing with two does not fill me with confidence.
Anyway I'm learning a lot, so much appreciate your feedback.
I am just wondering if because of the lengthy underground cable, that when the inverter starts to generate there is either a power surge or reflection pulse which is inducing a momentary voltage in the earth conductor, which thereby trips the RCD.
Posted by: @geo3geomaybe I need to make proper provision for my EV 13A outside charge socket, which is currently a spur off the downstairs sockets loop. The spur is fed via a 2 pole 16A RCBO. From what I read, EVs ideally need a type EV RCD, to cope with DC and transients.
Yes.
You're right to bring this up at the same time.
However it needs to go into a separate topic where others can find it at a later date.
Have a look at what I've written about EV charger supplies previously.
Then add to that topic if you'd like further information.
Posted by: @geo3geoI'm still looking, medium term, at the possibility of an ASHP with battery storage to get lower running costs. The battery would have its own inverter, the prospect of adding a 3rd inverter given what I'm experiencing with two does not fill me with confidence.
Ditto.
That question is better in a topic where battery storage for heat-pumps is already being discussed.
You've already been posting there!
I'll comeback to the question about 'transient resistant RCDs' another time.
At the moment I'm preparing for a meeting this evening!
Yes, you'd be better off with Transient Suppressors.... but that won't resolve the problem we're discussing here.
And I need to draw a diagram to explain that. 🤔
Save energy... recycle electrons!
@transparent You are right of course the two extra topics I introduced don't belong here and could confuse the main issue behind this thread. What I was getting at was that if I'm going to replace the consumer unit I need to take a step back and plan properly to sort out/make provision for, these other issues at the same time.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 270 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 52 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 1 hour ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 3 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 3 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 5 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 7 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 19 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 21 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 24 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago